Covered Patio GFI requirement

Posted by lwim (My Page) on
Mon, Mar 28, 11 at 15:06

Two questions:

1) We're in the final stages of adding a large 15x32 covered patio attached to our house. We have two 20 Amp circuits, one serving 2 outlets and the other 3 outlets, all located in the ceiling, about 12 feet off the floor. Their purpose is to be used for electric heaters. Nothing else are on the circuits. Do these require GFI protection? My electrician says they don't because they're not in a reachable location. Is this correct?

2) We have another cicuit that serves three fans with lights, rope lights and 8 can lights. There are no outlets on this circuit. Does it require a GFI breaker since it's outside?

Cheers,
Larry


Follow-Up Postings:

 o
RE: Covered Patio GFI requirement

1. If you're subject to the National Electrical Code he's wrong.
The code only permits the "not readily accessible" outdoor receptacles to be exempted from the requirement when they are to there to feed certain loads of which space heaters aren't one of them (the permitted rules are for snow melt/deice, and pipe/vessel heaters).

2. Receptacles must be protected. If the rope lights are plugged into a receptacle, then those need to be protected. Lighting and fans do not need GFCI protection unless the manufacturer requires it in the specifications. Some wet location units do have that requirement.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here