Alright, so I've got some lights I need to link up to a circuit with low-voltage contact outputs. I've also got a 4-zone ZCR sitting here.

The lights are 150W incandescents, one per "channel".


From a technical standpoint, if the relays are capable of handling motor/pump loads, they darn well shouldn't have a problem with lamps. Nobody is going to convince me this is UNSAFE.

That said, I do want to know, am I officially allowed to do this?


Follow-Up Postings:

 o
RE: Using 'zone control relay' for non-heating application...

Relays have contact ratings.

Find out what the rating of the one you have is.


 o
RE: Using 'zone control relay' for non-heating application...

Info online: "15A max combined load".

Label from one of the four relays itself: "250VAC 15A".


I know it's electrically fine, I'm just wondering about code/legality.


 o
RE: Using 'zone control relay' for non-heating application...

Most relays serve multiple functions, not just the duty they perform in a particular piece of equipment. As brickeyee suggested, make sure you are within the rated range of the contacts.


 o
RE: Using 'zone control relay' for non-heating application...

Can someone PLEASE just tell me if I'm violating the NEC by using this product for an application the manufacturer did not intend? You know, since both of my posts so far have stated that I already knew what I was later told anyway?

I'm not just talking about a plain-jane standalone relay from Radio Shack, or a contactor. This is a "Zone Control Relay": a Taco SR504-2, intended for controlling circulator pumps for heating.

I know I am within the ratings. I'm not asking if I am nor whether or not it will work, or be safe. As I stated in both of my posts, I only want to know if it is LEGAL. That's IT.


 o
RE: Using 'zone control relay' for non-heating application...

"Can someone PLEASE just tell me if I'm violating the NEC by using this product for an application the manufacturer did not intend? You know, since both of my posts so far have stated that I already knew what I was later told anyway?"

How do you know what the manufacturer intended the part for?

If you do use the part consistent with any UL listing it has you are fine.

The NEC does not really cover the internal wiring and components of equipment, that is NEMA.


 o
RE: Using 'zone control relay' for non-heating application...

If it's not part of it's intended use then it is not UL listed for that application and that is in fact a violation of code. You need to follow the manufacturers instructions and specifications on all parts you use. Not sure if that answers your question


 o
Code article

It'll def. be in the building code


 o
RE: Using 'zone control relay' for non-heating application...

"If it's not part of it's intended use then it is not UL listed for that application and that is in fact a violation of code."

UL listings for discrete parts like relays do not normally define an "intended use."

They define the loads that a relay can control in terms of resistive, inductive, horsepower, etc.

What load you control is not defined as long as it falls within the ratings of the relay.


 o
RE: Using 'zone control relay' for non-heating application...

That's the problem, brickeyee. I'm not sure that what I'm talking about constitutes a discrete part.

I know I can buy components at Radio Shack and build things. Then I am obviously following the manufacturer's instructions, because I am the manufacturer.

I am not talking about just a "relay". I am talking about a preassembled circuit board containing a transformer, four relays, and some screw terminals. It is INTENDED to control circulator pumps on zoned heating systems.

I am not controlling pumps on a boiler. I am controlling lights.


Frankly it's too late, I needed this answer two days ago, and I've already installed the darn thing. I KNOW it is electrically safe, I was just hoping (for my own sake - as there is no inspection process here) to find out ahead of time if what I was trying to do was 100% officially legal.


 o
RE: Using 'zone control relay' for non-heating application...

If installed a suitable enclosure, just use it and move on to other things.


 o
RE: Using 'zone control relay' for non-heating application...

I can't find the exact one I have (used/salvage stuff) but here's a similar one that is currently available:


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here