C/Bs and multiwire curcuits

Posted by tom418 (My Page) on
Sat, Mar 3, 12 at 13:43

I'm installing two duplex recepticles in a two gang box. I'm feeding this from a home run to my GE breaker box. I'm using 14-3, multiwire curcuit.

From what I've learned, the newer NEC now requires a two pole C/B with the handle tie feature, even if each phase feeds one yoke? I've been looking for a GE THQP215, and could not easily find one. Home Despot didn't carry them where I am.

Note: Each duplex outlet will be fed from one leg, with pigtailed neutrals

Is the reason for the code change to ensure that each pole is fed from a different phase, or is it to protect someone working in the box?


Follow-Up Postings:

 o
RE: C/Bs and multiwire curcuits

Lots of two-pole breakers have just one handle, common-trip. The SqD QO series is one example. Since two circuits on opposite poles share a neutral, shutting off just one of those circuits leaves the other circuit energized. If the energized one is actually supplying some load and the neutral is opened at certain points, as one might do if working on the other circuit and believing that is not live, the open end of the neutral nearest the load of the still-energized circuit will then be energized at 120 volts. Nasty surprise- or worse. The common-trip or tied handles solves that problem.
Your store can order the breaker. Will they? Ask them.

Here is a link that might be useful: Breaker


 o
RE: C/Bs and multiwire curcuits

Thanks for the link, Bus_Driver, but the Home depot stores near me don't sell the item (Enfield, CT, Wallingford, CT, West Springfield, MA, and a few others). Looks like I'll have to order through Amazon.com, for a few bucks more.

I had no trouble finding the same breaker a few years ago, when I put in a well pump (240V, didn't have a choice about the trip handle then...)


 o
RE: C/Bs and multiwire curcuits

It used to be that the handle tie was only require if you fed the same yoke with both sides, now it's required in all cases. The GE 215 breaker isn't that hard to find...You can order it online and have it in a couple of days if you can't find it.


 o
RE: C/Bs and multiwire curcuits

Approved handle ties are still allowed and are a less expensive solution. Since you're having trouble finding a common 2 pole breaker, then you'll probably not find a handle tie at the big box store. I'm guessing that part of the problem is that this breaker might be one of the 1/2 size GE breakers.

You can always call some electrical supply houses in your area, surely there is a stocking GE distributor nearby.


 o
RE: C/Bs and multiwire curcuits

tom_o :

Yes, it is a half size breaker. Are these becoming obsoleteted/ phased [no pun intended] out by GE?


 o
RE: C/Bs and multiwire curcuits

No, they're still available and in common use. Can't account for why your homecenter doesn't have them, but they are available online as I stated.

Alternatively you can move some of your single pole full size stuff from higher up in the panel down to single pole skinnies and put a full size double pole up top.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here