 o
old dryer 2-#6 & 1-#8 cable

Posted by Rick4343 (My Page) on
Thu, Mar 21, 13 at 11:23

What do I need to run a outlet for a dryer with the above listed cable ? cable type? breakers? outlet type? Thank you for any help. Rick Please note I have the dryer but I have no outlet. Nothing. Starting from the breaker box is there any way to get power to this dryer ? Thanks again. Rick

This post was edited by Rick4343 on Fri, Mar 22, 13 at 11:57


Follow-Up Postings:

 o
RE: old dryer 2-#6 & 1-#8 cable

You are not allowed to make any changes to an old 3-wire dryer circuit.

t must be replaced with anew 4-wire circuit.
Some AHJs will allow simple changes like moving or replacing the dryer receptacle, or even moving it a few inches a long as the old cable reaches the new location.

Others require the upgrade for ANY alteration


 o
RE: old dryer 2-#6 & 1-#8 cable

New dryers are allowed to use the old (in place) 3-wire circuit, generally.


 o
RE: old dryer 2-#6 & 1-#8 cable

"New dryers are allowed to use the old (in place) 3-wire circuit, generally."

But you are not allowed to modify the old circuit.

Limits set by local AHJ.


 o
RE: old dryer 2-#6 & 1-#8 cable

He's not even modifying a circuit it sounds like. He wants to know if he can use some 6-2 cable he found to wire up a new dryer, and the answer is an unequivocal NO.


 o
RE: old dryer 2-#6 & 1-#8 cable

I don't think it's really clear what he's asking. One of his questions is "what cable?". If he wanted to use the cable he has, why would he ask what cable?

And I don't think we'll ever hear back from him, so there's probably no point in debating what he's trying to do.

Edit: Oops, I just noticed that he changed his original post earlier today. So maybe he will stick around to answer questions and provide more info.

This post was edited by greg_2010 on Fri, Mar 22, 13 at 14:36


 o
RE: old dryer 2-#6 & 1-#8 cable

yes, looking at the original, I thought the circuit was already in place and he was dealing with a new 4-wire dryer with a 3-wire circuit.

With no circuit in place, that 6/2 wire cannot be used. He needs 6/3. He'll also need a new 4-prong outlet (somebody can list the nomenclature), and a standard 2-pole breaker of the appropriate size. And the appropriate style clamp at the breaker box and perhaps the outlet box.


 o
RE: old dryer 2-#6 & 1-#8 cable

No, he needs 10/3. 6/3 is WAY overkill for a dryer.


 o
RE: old dryer 2-#6 & 1-#8 cable

Nice catch, petey.


 o
RE: old dryer 2-#6 & 1-#8 cable

I am sorry if my question was unclear. So here we go, my gas dryer died and I have been given an older, but working electric dryer. There is no plate on the back listing its specs. It has a 3 prong plug, but it does not fit a "standard" dryer outlet. The only info I can glean is the printing on the "cable" of the dryer its self. Which is [ Type SR Range Cable 2 - #6 & 1 - #8 ] So with that information my questions are. Can I still get an outlet for this type of plug, or can I change the plug? What type of cable do I need to run from the breaker box? What kind of breaker(s) do I need? Or do I need to make another trip to the scrap yard? Again sorry for any mix up and thank you for your time. Rick


 o
RE: old dryer 2-#6 & 1-#8 cable

P.S. its still in the garage so at least I dont have to hall it back out of the basement. Rick


 o
RE: old dryer 2-#6 & 1-#8 cable

The plate specs for mine are located inside the door. You might look there.

Otherwise, if you intend to stay within the code, the 10/3 cabling should be fine. You will probably need a 30-amp breaker. You will need a 4-prong outlet and box for the wall. You should be able to replace the cord on the dryer with a 4-prong cord.

Things get a little tricky with replacing a 3-prong cord with a 4-prong cord at the dryer. I'll let others talk about this.


 o
RE: old dryer 2-#6 & 1-#8 cable

Most dryers made in the past twenty years have four terminals where the cord attaches with a jumper or bonding screw that bonds the case to the neutral for three wire connections.


 o
RE: old dryer 2-#6 & 1-#8 cable

You can change the cord to match your receptacle, but changing the receptacle to match the cord may invoke the 'no alteration rule' in the NEC.

What size breaker is feeding the present receptacle?

That old cord sounds oversize.

Many cords use smaller conductors since they are exposed and use higher temperature insulation.

This post was edited by brickeyee on Tue, Mar 26, 13 at 12:46


 o
RE: old dryer 2-#6 & 1-#8 cable

What size breaker is feeding the present receptacle?

There is no present receptacle. He's doing everything from scratch. See his update on "Mon, Mar 25, 13 at 15:04" where he explains the situation.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here