GFCI wiring

Posted by jim912 (My Page) on
Sat, Mar 22, 14 at 10:35

GFCI receptacle in my kitchen is not working after reset. I checked power to receptacle - reads 120V between LIne and GROUND (coming from main panel). Then I checked power directly into the outlet slots and it measures 0 voltage. Replaced GFCI with same results. There are 2 downstream outlets the also have no power. Used stab connections on back of outlet. Unsure what my next step should be - other than calling an electrician.


Follow-Up Postings:

 o
RE: GFCI wiring

Chances are you have a fault. If it never resets, it's almost assuredly a ground-to-neutral fault somewhere. First step is to disconnect the downstream outlets and see if the GFCI resets. If so the fault is downstream. You can reconnect it and then go and disconnect the third outlet at the second, etc... to isolate the problem. Once you've found it look carefully for the bare ground touching the neutral screws or the neutral wire touching something (the box or one of the ground wires).


 o
RE: GFCI wiring

OK. I disconnected the black & white wires on the LOAD side of the GFCI and got the same results - 120V across the LINE/GROUND wires but nothing in the GFCI slots. The wiring into the GFCI appears to be tight.


 o
RE: GFCI wiring

What about LINE-NEUTRAL?


 o
RE: GFCI wiring

Across the hot and neutral it's measuring 5.6V.


 o
RE: GFCI wiring

Something's wrong with your feed. You should get 120V HOT-NEUTRAL.


 o
RE: GFCI wiring

I thought the GFI outlet was first in that circuit. Is it possible there's something else before it or is just it bad wiring between the panel and the outlet? Nothing's ever been changed - it just happened.


 o
RE: GFCI wiring

If you have power from hot to ground but you are reading nothing or very low voltage from hot to neutral then you have a lost neutral somewhere. Look for a j-box or maybe the panel it comes from, worse case scenario you need to run a new wire and abandon the old one.


 o
RE: GFCI wiring

I concur with nick on this one. Obviously the hot and most likely the ground are intact. The neutral isn't. As far as your meter is concerned, neutral and ground should be synonymous.


 o
RE: GFCI wiring

Thanks guys, you've given me something to research. If I can't find anything, I'll call in a professional.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here