C/B Tripping Only For A Certain Amount Of Time

Posted by marshh (My Page) on
Tue, Mar 13, 12 at 7:54

Gday,
A circuit breaker keeps tripping at home only after some heavy rainfall, though after an hour or two I am able to reset the breaker and it works fine again. Any ideas as to what the problem might be? Thanks


Follow-Up Postings:

 o
RE: C/B Tripping Only For A Certain Amount Of Time

Wet conductors somewhere.

Once they dry out the breaker can be reset.

Check outside outlets (receptacles and lighting).

Water is not an especially good conductor, but if enough ionic material is present in the water it can conduct.
A short path (or a large area) can be enough to trip 15 and even 20 A breakers.


 o
RE: C/B Tripping Only For A Certain Amount Of Time

Do you have a pump anywhere?


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here