welder on 200' run

Posted by tagunny (My Page) on
Fri, Feb 21, 14 at 22:12

I was wondering if i can run a tig welder on 60amp service @ 200' from panel thhn copper #4 the welder will is phase 1 250a@40% and 200a @60% duty cycle thaks for any help


Follow-Up Postings:

 o
RE: welder on 200' run

First off you'll have to tell me what kind of conductors you are using. Even with the allowances for welder #4 copper (at any rating) isn't big enough. Depending on what you are using you will need something along the lines of 1/0 or 2/0 for that size welder.

The other issue is voltage drop, but 2/0 wouldn't be a bad idea.


 o
RE: welder on 200' run

The supply conductors for a dedicated welder circuit are sized using the rated AC input amps and the duty cycle for the maximum rated welding amps. So first we need to know the input amps off the name plate, next we need to know what the duty cycle is at the maximum rated output (welding amps). (The actual welding amps that you gave us are not used for sizing the circuit).

This post was edited by joefixit2 on Sat, Feb 22, 14 at 11:12


 o
RE: welder on 200' run

Gack JoeFixit is right. My mind was elsewhere. You need to know what the AC input rating is. Many of the smaller ones can run on either 120 or 240, so you get by with lower required amps and less voltage drop on 240.


 o
RE: welder on 200' run

The output rating of the welder is irrelevant. What is the input rating?


 o
RE: welder on 200' run

This is a welder i was looking at buying (miller syncrowave 250dx tig runner)what i found out is that input v@220 -77amp- Min. Conductor #6- Max.lenght 119' - min. ground #6 so i dont think i can use this welder in this location were i have 60amp 2/#4 and 2/#6 @ 210' I guess ill have to go with a smaller machine


 o
RE: welder on 200' run

#6 would be acceptable except for the very long run. #4 would have a reasonable voltage drop at 77 Amps.


 o
RE: welder on 200' run

Just a thought. I run a Miller Dialarc AC/DC 250A. It can be wired for 220v or 440v. I run it off a 220v 50A circuit.

Technically it is capable of drawing something like 90A input, but I've never needed near that much current. Hell I'm not welding 2" plate steel with it. Most of what I weld is 1/4" or 3/8". For that, a 50A input is plenty. I can crank it up so hot to melt welding electrodes and never blown the breaker.

I weld with a heavy duty industrial welder not because I need all the amps, but because it's continuous duty with 1/8" rod and welds much more smoothly than a typical buzz box.

I'm sure there are people who will point out my circuit is sized too small but there is just no need for such a heavy duty circuit unless you are welding some serious heavy duty plate.

If anyone can point out a significant safety concern with my setup, I'll stand corrected.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here