4 wires for 240v appliance

Rocky865
12 years ago

Why are four wires used for a 240v dryer or range. I know one is the neutral and one is the ground, but they are both attached to the same ground panel in the breaker box. The transformer to house cable has only 3 wires. If the wire gauge is sufficient, it seems to me that the circuit is the same. Why not connected together inside the appliance? I am not trying to be an electrician but I am curious. I don't need to know "it is the code". Thanks

Comments (8)

  • dkenny
    12 years ago

    first you have to understand the function of the wires.

    the 2 hots are easy.. they carry the 240 volt currents

    now it gets a little more complicated
    the neutral..this wire carry current for 120 volt circutis
    even a dryer has 120 volt circuits..and currents..so some current flow on the neutral wire..yes even in a 240v dryer..the mechanical timer..most likely is 120v..

    the ground...you know the wire that ties to the neutral at the panel?
    this wire..well it doesn't carry current unless there is a fault..hence its a safety ground..

    got it?
    the center tap of the transformer is tied to earth ground as a safety measure..a local ground reference..a place for fault currents to flow..

  • ionized_gw
    12 years ago

    In fact, in olden days, the dryer circuits were 3-wire. A dedicated ground requirement was added in more recent electrical codes. You may need a neutral wire for 120V loads on the dryer, light and controls, probably. You have 120V across either of the hot conductors and the neutral. The 240V is across both hot conductors. The independent ground is for safety.

  • bus_driver
    12 years ago

    With 3 conductors or with the neutral and ground connected together within the dryer, if the ground/neutral combined is broken and the "hot" wires remain intact, turning on the dryer will place 120 volt potential onto all the metal parts of the dryer. The neutral carries current for the motor in the dryer, the lighting and the timer. With ground and neutral combined and broken within the cord or earlier within the circuit, the neutral current has no place to go and the dryer will not work. But the housing will be energized at 120 volts- waiting to bite a person. With 4 conductors and the ground and neutral separate within the dryer, if a break/cut or failure of the ground and neutral occur, the dryer will not work. But no hazard arises because no current carrying conductors are bonded to the dryer housing.

  • brickeyee
    12 years ago

    "A dedicated ground requirement was added in more recent electrical codes."

    dryers and rangs ad a special exception that allowed -wire ciruits.

    Sonce the timers and often the drum morot are often 120 V loads the dryer was really a 120/240 V combination load that would require a 4-wire circuit.

    The exception allowed 9and still grandfathers) 3-wire circuits for ONLY dryers and ranges.

    All other 120/240 V loads have required 4-wres for a very long time.

    The circuit used to power houses and large residential loads is an Edison circuit.

    It has the advantage of having 240 V available for larger loads, while not having any voltage greater than 120 V to ground (or neutral) present.

  • Rocky865
    Original Author
    12 years ago

    Thanks. I still can't understand the difference in where the wires are connected at the appliance or the entrance box. The circuit is still the same, if wire gauge is large enough to carry the current without resistance. I can understand the safety of having 2 wires to ground at the box in case one gets disconnected. I am not being argumentive. At my level of knowledge on the subject it is just difficult. Thanks again to each of you.

  • Rocky865
    Original Author
    12 years ago

    I also found info at mikeholt.com More complicated, but all of the info from every source is appreciated. I had seen a wiring diagram and it just seemed redundant.

  • bus_driver
    12 years ago

    If the neutral becomes broken or disconnected anywhere between the panel and the load when the load is energized by the hot, the broken end of the neutral nearest the load becomes energized at 120 volts.
    Are we together on that?
    Would you want a conductor that is energized at 120 volts attached to the outer body of an appliance?

  • brickeyee
    12 years ago

    "The circuit is still the same, if wire gauge is large enough to carry the current without resistance."

    There is ALWAYS a voltage drop in a wire carrying current, no matter how large the wire is.

    The grounding conductor (AKA 'safety ground') is NOT intended to be part of the circuit in normal operation.

    It is there to keep the chassis at zero volts to earth, and provide a path for fault currents to trip breakers (or fuses) if the chassis should become electrically hot from a fault in the equipment.
    If the ground was not present the chassis could be at 120 V until another path to ground occurs, like through a person touching the chassis and a ground.

    Very old radios without a polarized plug could have the chassis at 120 V.
    Touch a metal knob or the chassis and ground and you competed the circuit.

    Since no current is flowing in the grounding conductor (safety ground) it is reliably at zero volts to earth.

    The neutral (AKA grounded conductor) is NOT at zero volts since it is part of the circuit, carries current, and the current creates a voltage drop (it may be very small, but it is not zero).

    A typical US house uses an Edison circuit, created by grounding the center tap of the secondary winding on the pole transformer.

    This limits the voltages to 120 V to earth, while providing 240 V leg-to-leg for larger loads.
    Since transformers always have leakage from the primary side to the secondary side (through inter-winding capacitance) and the lowest distribution voltage is 7,200 volts the secondary will charge to this value if it is not connected to the primary somehow to create a return path for the leakage current.
    This is normally done by using a 3-phase Y to distribute power, with the center of the Y connected to earth and used as a neutral to return any imbalance in the three phase loads.
    One side of each phase transformer is thus tied to earth and neutral.
    Any leakage from the primary side can then return through the earth connection from the house main panel to the pole primary earth connection.
    While the earth is a poor conductor at 120 V, it works well at 7,200 V (and higher) most of the time.
    In some areas (sandy dry soil) a neutral is run on the poles to ensure it is available for current even when the earth resistance is excessive.

    One of the hazards that was created by using metal water pipes as a grounding electrode is that water line workers can be injured or killed.
    If they cut a water line and then touch each side of the cut pipe there can be enough voltage and current to kill.

    Arguably the current might still be there if the pipe was NOT used as a grounding electrode though.
    The pipe would likely still be a lower impedance path, and current would preferentially flow in it over a higher impedance earth only path.