Thu, Feb 23, 12 at 19:42
| I am adding an additional fluorescent light (two 48" T8 bulbs) in my garage and will need to run about eight feet of wire from an existing light to supply power. There are two lights in a series connected by 14 guage wire. I have some left over 12 guage romex and wonder if it is okay to use it instead of 14 guage. Otherwise, I will buy some more 14 guage. Basically, is it safe to go from smaller guage to larger in this application? Thanks for any help. |
Follow-Up Postings:
|
- Posted by bus_driver (My Page) on Fri, Feb 24, 12 at 7:13
| No prohibition on using the #12 as you describe. |
|
| bus_driver, I was under the impression one must maintain consistent wire gauge throughout a given NM branch such that a over-current event would always occur at an accessible junction point or at the breaker (not along a length of wire). Granted going up a step as johns08 describes would be very unlikely to fall into this category, but is it the "right" way to do it? Dan |
|
- Posted by bus_driver (My Page) on Mon, Feb 27, 12 at 15:39
| Why would a #12 conductor, which is permitted to be protected from overcurrent at 20 amperes for ordinary residential circuits, pose an additional hazard when used on circuits protected at 15 amperes? |
|
| "I was under the impression one must maintain consistent wire gauge throughout a given NM branch such that a over-current event would always occur at an accessible junction point or at the breaker (not along a length of wire)." What? Any current flows in the entire circuit. Using a larger conductor is acceptable, though it can lead to confusion later on if someone tries to increase the circuit ampacity without checking every section of the circuit. The OP said nothing about changing conductors outside a JB. |
|
| My point is that IF you have an over-current condition, the spot with the most resistance would heat faster (i.e. why you don't put in a section of 14g wire in a 20A circuit). The comment was hypothetical and I wasn't suggesting the OP's method was in any way unsafe, but that it might, as you say, "lead to confusion later". Dan |
|
| "My point is that IF you have an over-current condition, the spot with the most resistance would heat faster" The only heat that matters is the breaker or fuse. That is the device that is going to open the circuit. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.