Thu, Feb 25, 10 at 19:12
| Spoke to the building inspector today on the phone. He said he is fine with my high voltage lamp cord in the wall with no visible markings being converted into a low voltage lamp cord in the wall.
Is there anything in the NEC that prohibits low voltage lamp cord in the wall. or is it strictly a locally decided issue? Would you feel comfortable with this situation? |
Follow-Up Postings:
|
- Posted by ronnatalie (My Page) on Fri, Feb 26, 10 at 5:35
| Yes, the NEC PROHIBITS putting cords in walls. Period. Doesn't matter if it's for 12V or 1200V. Article 400.8 USES NOT PERMITTED. The NEC isn't some national law however, it only has meaning when adopted by your state/local as the (or part of the) electrical code. No I am *NOT* comfortable with it. It's banned by the NEC for good reason. |
|
- Posted by plumeriavine (My Page) on Fri, Feb 26, 10 at 16:48
| Thank you. NEC is cited as the governing rule book for our area. 400.8. Got it. |
|
| Your AHJ is an idiot. |
|
- Posted by azlighting (My Page) on Sun, Feb 28, 10 at 0:03
| Should be fired... NEC is the MINIMUM safety requirement... |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.