| I will be buying a very inexpensive house, and had it professionally inspected. The inspector noted that the GFCI receptacles are not properly grounded, as well as the other receptacles (even though they are 3 pronged.)
My question is whether or not I have a totally unsafe situation, and if so, what would I need to do to properly rectify the situation. As for the still safe but possibly negative aspects, I understand that improper grounding could cause problems with an HDTV set and perhaps other appliances? I will also have a room with pinball machines (which are all supposed to be 3 pronged, but some of them have been modified to 2 prong - something i plan to take care of), and I'd like to have at least the receptacle for that be properly grounded. I would think that the GFCI's should be grounded as well, but my real estate agent says that the GFCI catches the surge, so it is not completely necessary, although obviously better. As for rectifying the situation, my inspector says that all I would need to do is to simply drop a grounding wire down to the ground, which should be be so difficult since the house is raised on piers, and the circuits are all very near walls. My real estate agent says that that would be improper, and that the only real way to fix the situation is to properly rewire the circuits to the breaker box (an expensive proposition.) As for putting money into the house, I don't plan to spend much time there both in total year, and portion of the years, and would only want to do work that would be an absolute necessity, or that I could justify as being a cost that I could recover when I sell. As for the entire situation of buying a home, I am in a very difficult situation as I need to buy a very inexpensive house (which by default is going to have issues), and must do so very quickly before filing for Chapter 7, so I need to buy this house no matter what! |
Follow-Up Postings:
|
| A professional home inspector is required to know very little about electrical systems. Your problem could be as simple as a loose ground wire somewhere or might require the entire house to be rewired to properly ground everything. Of course, people lived without ground wires for years. They are a safety device. Some electronic devices will require a ground to work properly. You might consider selling your pinball machines and HDTV to pay off some of your debts instead of worrying about that though. |
|
| GFCI receptacles work fine without a ground, and they are an acceptable replacement for 2-prong receptacles when no gruond is present. You cannot just "my inspector says that all I would need to do is to simply drop a grounding wire down to the ground." The grounds are required to run with the circuit conductors. It ends up being as much work to run another wire with the branch circuit conductors as pulling in new cable with ground. It IS a hazard to have 3-prong receptacles when no ground is present, unless they are fed by an upstream GFCI device. You could use GFCI breakers and leave the 3-prong receptacles in place. You need tp affix stickers that say ‘No equipment ground’ and ‘GFCI protected’ to the 3-prong receptacles fed this way as a warning to users. Surge protection devices require ground to provide full protection. There can be problems with electronics when no grounds are present. Usually it is not a problem but it can cause 60 Hz hum to appear. |
|
| OK, so if I plug in a 3 prong appliance into a GFCI, I will still be protected from shock, although I would get the surge protection. It sounds like all I need to do is just replace all the receptacles with GFCI's, and I'll be safe - OR alternatively, replace all the breakers with GFCI breakers. What would be the cost to do either (i.e., per receptacle or breaker)? I figure I could do the receptacle change myself, but would I need an electrician to do the breaker? I suppose I could ask the electrician to check to see if there is a loose ground wire first. I think that rewiring everything would be prohibitively expensive. Contrary to the first replier, I am NOT going to sell any of my possessions. |
|
| GFCI receptacles do not provide surge protection unless it is an added 'feature' by a particular manufacturer. A GFCI works be making sure the hot and neutral current match within ~0.005 amps (5 milliamps). It protects against the current going anyplace besides between the hot and neutral. It is pretty rare to get yourself across the hot and neutral perfectly with no other path for the current to take. Breakers are not hard to replace, but you need to be aware that even with the main off, the lines coming into the main breaker from the meter are still hot. You do not need to replace every receptacle. GFCI receptacles have line screws for the input, and load screws that can feed regular receptacles down stream and provide the same protection. It can be a chore to figure out the order receptacles are fed from the breaker panel and then hooked up. |
|
| Your inspector should know this. First (as brickeyee noted), the GFCI does zero surge protection. Second, GFCI only provides human safety. Third, a GFCI is the only way of installing three prong plugs on two wire circuits. Code then says that GFCI must have this wording glued to that receptacle: No Equipment Ground. Everyone should know that receptacle does not have safety ground. Fourth, the only connection to earth ground must be at the breaker box. A receptacle grounded to earth is a code violation. It must be grounded to a bus bar inside that breaker box. Fifth, the critical earth ground for human safety and for transistor safety must be from breaker box to some dedicated earth electrode. Water pipe is insufficient. Code lists the five electrodes that might be used, in Article 250.52. That is earth ground. Which is something completely different from safety (equipment) ground in a receptacle. |
|
| "the critical earth ground for human safety and for transistor safety must be from breaker box to some dedicated earth electrode. Water pipe is insufficient." The actual grounding electrode system is not so much for human safety but lightning and leakage current on pole transformers. If a metallic water pipe with 10 feet in earth contact is present it MUST be used as the primary electrode. If no metallic water pipe with adequate earth contact is present, a single made electrode can be used, but it must be tested to ensure it is 25 ohms or less to earth. |
|
| > The actual grounding electrode system is not so much for human safety > but lightning and leakage current on pole transformers. First Energy, the company that also created that famous NE blackout (NY, Ontario, OH, MI) stopped fixing earth ground to cut costs and increase profits. Therefore people were being shocked in their jacuzzis and swimming pools. The problem was not solved until local governments passed ordinances. $thousands in fines every day someone was shocked. Suddenly First Energy started fixing those transformer ground. Suddenly people were not long being shocked. Firstmost - those grounds exist for human safety. |
|
| This thread has taken quite a turn from the OP's question. The first thing you need to do is determine if the house is wired with grounds. Just open up any electrical socket and count the wires. You should see black, white, and green/copper. If you only see 2 wires, then you have no ground. That would mean you have to rewire the entire place to bring it up to modern standards. You can install GFCI's for an added measure of safety, but they are not a replacement for missing grounds. If you see 3 wires, then the place is wired with a ground, but something is connected improperly. It could be the physical ground to the earth, but it would be much more likely that some wire just came loose. If it is the whole house, then start looking at the panel. If it is just one room, then look at that branch circuit. Re your possessions - I'm sure you have justified keeping all your toys while you default on your debts, but it is an immoral position. If you don't have money to pay your bills, then you don't have money for a pinball collection. Sometimes life is tough, but you have to suck it up and do the right thing. |
|
| "First Energy, the company that also created that famous NE blackout (NY, Ontario, OH, MI) stopped fixing earth ground to cut costs and increase profits. Therefore people were being shocked in their jacuzzis and swimming pools. " At 120 V the earth is a very poor conductor. At the lowest distribution voltage (7,200 volts) it is decent. If the POCO has not tied the center tap of the transformers down to earth the leakage will appear on the secondary on the grounded conductor. The main purpose of earth grounding the already grounded conductor is to provide a path for this leakage. In a correctly installed and operating system that is the purpose. An incorrectly installed and operated system can easily create hazards, but the hazard is from the incorrect installation and operation. The only major blackouts I am aware of in the northeast had far more of the genesis in solar storms creating voltage shifts in the earth itself. It could even be argued that NOT tying the ends of the transmission lines to earth might have actually prevented the problem. Over long distances especially at higher latitudes the actual earth potential can be rather from from zero if a geomagnetic storm is present causing changes in the earth's magnetic field.
|
|
| That First Energy example demonstrates a human safety problem when the local distribution (when First Energy cut costs) was improperly maintained. Once the earth grounds were restored, that human safety problem was eliminated. BTW, if you do not know the NE blackout - that literally took out electricity in NY, Ontario, Michigan, Ohio, etc, then you do not have any news sources. First Energy created that blackout by doing so many things wrong - all simultaneously. Read the NERC report that describes First Energy doing failure after failure all day to create a 4 PM blackout across all those states. Of course, this is not about grounds. Solar flares had nothing to do with this famous event. Then entire blackout was create by an electric company dominated by business school types who only understood cost controls and knew virtually nothing about electricity. Who would do anything – including run a nuclear reactor with a hole in its containment dome and a potential ‘Three Mile Island’ problem – because only profits mattered. You disappoint me if you do not know the so many flagrant failures all directly traceable to management in First Energy - including people being shocked in swimming poles because First Energy stopped fixing transformer ground - that are essential to human safety. |
|
| You disappoint me if you do not know there have been multiple blackouts in the NE from power system failures. The most recent one (1980s?) was from a geomagnetic storm when hydro Quebec lost a major transmission line. What is the date of the one you are referring to? |
|
| Swamp, I suggest you consider the financial advice offered here a free bonus on top of the free electrical advice, and do with it what you will. <grin> If your house is groundless, for example wired with old ungrounded NM or even knob and tube, a fairly cheap and easy code-legal fix is to replace all the 3-pin receptacles with 2-pin types. IIRC they cost maybe a buck and a half each at the big box stores (somewhat more than the cheap 3-pin as they sell in smaller numbers). Donate the removed 3-pin receptacles to your local thrift store or sell them at a garage sale. For improved safety I would fit GFIs instead in the kitchen, bath, garage, and cellar. Outdoors too, if you have such. Decent GFI recepts run $10 or so at the big box stores. As mentioned above, mark them "no equipment ground." Of course you shut off the power before changing receptacles. When wrapping the wires round the recepts' terminal screws be sure to wrap them clockwise - so that when you tighten the screw the wire is pulled into a tighter circle, not spread out. Tighten firmly. |
|
- Posted by ronnatalie (My Page) on Thu, Feb 18, 10 at 8:35
| Note that while you are allowed to plug your HDTV into a non-grounded outlet (either 2-prong or 3-prong with GFCI protection), there are certain other restrictions. You can't legally use the GFCI dodge on certain appliances and power tools with grounded cords. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.