How to seal underground splices

Posted by supersport396 (My Page) on
Wed, Feb 27, 08 at 13:04

I had 6/3 put in 1.5in conduit, had to make two splices and made them in 4x4x4" sealed junction boxes, the tops are sealed good but the pipes running into the boxes isn't completly watertight,to me atleast. Connections were made with split nuts, wrapped tightly with rubber tape, then regular electrical tape.

Still..I would like some other way of sealing these connections from water and shorting..is there some kind of tar or grease I can put around the splices before I close the boxes and finish covering it up.

Thanks

Michael


Follow-Up Postings:

 o
RE: How to seal underground splices

Underground splice kit.
Underground conduit is NEVER dry. Consensation will make them wet even if completely sealed.


 o
RE: How to seal underground splices

The boxes WILL fill with water. They are also supposed to be accessable without excavating any material (except gravel, sand or landscaping mulch/similar - and only then if there is a permanant marker to locate the box)

Underground splice kits are a must here but the reality is the box probably isn't big enough to contain them. A material like Scotchkote might do a reasonable job of sealing the splice but they will need several coats and you won't know for sure it worked or not till you have a failure.

The best way to do an installation like this is to use pullboxes similar to the boxes used for underground sprinkler valves. The conduit enters the open bottom of the box through 90s and the splice is made in the empty space between the box lid and the fill in the bottom of the box using underground splice kits. The fill is sand or gravel and it will drain away standing water so the splices don't sit in water all the time.

I'd really suggest you do something different even if it's install larger boxes than you have so UG splices can be used. If you have aluminum wire and it gets wet you're gonna have paste where the wire was real soon. If it's copper you might wind up with some exhorbitant electric bills and not know why as well as voltage issues on the load end.


 o
RE: How to seal underground splices

please don't say it is 6/3 NM Romex cable. If it is, it will be shot in a year


 o
RE: How to seal underground splices

It just regular 6/3, non underground cable from lowes.. heavy vinyl type outer insulation. It is in 1.5 conduit...


 o
RE: How to seal underground splices

6/3 nm in a conduit full of water is dangerous and won't last long.


 o
RE: How to seal underground splices

It just regular 6/3, non underground cable from lowes.. heavy vinyl type outer insulation. It is in 1.5 conduit...


Might as well pull it out now and start over. Use individual #6 THWN conductors this time with no splices.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here