My electrician is finishing the 'rough-in' work for our kitchen renovation and I was surprized to see the lighting setup.
Thanks! |
Follow-Up Postings:
|
- Posted by terribletom (My Page) on Thu, Feb 10, 11 at 11:48
| "However at the first junction box it is split into 12/2 cable feeding some outlets and 14/2 cable feeding the lights. Is this a problem?" Yes, if you have correctly described the situation, it IS a problem. There are some very narrowly defined circumstances in which a short length of #14 wire might conceivably be used for as a fixture whip on a 20-amp circuit, but at first glance, your description does not appear to fit those circumstances. Another issue that could be in play has to do with whether the "outlets" fed by the 12/2 cables are small appliance receptacles (e.g., along the kitchen counter, a work island or dining room). If that's the case, regardless of wire size, receptacles and lighting cannot be on the same circuit. |
|
| If there is ANY #14 wire in the circuit the WHOLE CIRCUIT must be derated to 15 amps. |
|
| It would be an issue if it were in my house. |
|
- Posted by terribletom (My Page) on Thu, Feb 10, 11 at 12:29
| Nor mine. It's all quite academic, but... I think that if you wend your way through the tortured cross-referenced paths running through 210.19(A)(4) Exception No.1 (b), 410.117, and 210.20(B) you'll conclude that there's a narrow exception applying to luminaire whips of conforming lengths and wiring methods whereunder the presence of a #14 tap does not require derating of the circuit to 15 amps. But, like I said, it does not appear to apply here. In any case, I consider Brick's comment, as phrased, to be correct because the whip is not considered part of the branch circuit -- it's a fixture connector. |
|
| "In any case, I consider Brick's comment, as phrased, to be correct because the whip is not considered part of the branch circuit -- it's a fixture connector." Since the #14 run is "14/2 cable feeding the lights" it is not being used as a whip to a single fixture and the 'whip' exception does not apply. |
|
- Posted by terribletom (My Page) on Fri, Feb 11, 11 at 10:42
| 1. "your description does not appear to fit those circumstances." 2. "But, like I said, it does not appear to apply here." Meh, but it's important who gets the last word, sooo... "the 'whip' exception does not apply." You win. TYVM. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.