200 amp entry panel question

Posted by rbigg (My Page) on
Tue, Feb 25, 14 at 1:43

In your normal 200 amp entry panel, is the 240vac neutral connected to ground?


Follow-Up Postings:

 o
RE: 200 amp entry panel question

What is a "normal" panel?
There is no such things as a "240vac neutral".

Can you please be a bit more specific?


 o
RE: 200 amp entry panel question

At the service disconnect, the ground and neutral are bonded together. It has nothing strictly to do with panel capacities. Not all "main panels" are the service disconnect.


 o
RE: 200 amp entry panel question

ronnatalie: Thanks. I seem to remember in our 200 amp entry panel the ground and neutral were connected together.


 o
RE: 200 amp entry panel question

As they should be.
Is there a reason you are questioning this?


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here