wiring a 220v oven

Posted by carny55 (My Page) on
Tue, Jan 2, 07 at 23:44

My electrician asked me for the amperage on a new electric oven. He wanted to know what wire gauge to use. The manufacturer's info showed that the device used 3.6 KW on a 120/240v line. (And also showed 2.7 KW on a 208Y/120v line).

Well, that confused us all. As I understand Watt's law, that would imply a 15 amp circuit for 240V (3600w/240v=15a). We called the home improvement store (Lowe's) and they said 30 amp circuit. And use 10 gauge wire.

So my question is which is correct? Should it be 30 amp since the 240v is made of 2 120v wires and that amperage would be 30 amp (for 3.6 KW).

And finally why is it called 220v if it's really 240v?

And what is 208Y/120 ???

Thanks,

Electrically confused

p.s. we are using 10-3 gauge wire, and a 30 amp circuit. Are we right?


Follow-Up Postings:

 o
RE: wiring a 220v oven

That confused you all? I would sincerely hope it did not confuse your electrician.

Your new oven draws 3600 watts at FULL load @ 120/240v. A watt is a watt. At that point amperage is determined by the voltage. At full load this is a nominal 15 amps. This is NOT a 15 amp circuit.

Why did you call Lowes about this? All they did was sell you the thing. They are most often clueless about these matters and often give anywhere from erroneous to downright dangerous advice.

Unless the instructions SPECIFICALLY state so, all you need is a 120/240v-20 amp circuit for this appliance. Since this unit requires 120 & 240 volts you must run a 4-wire cable in the XX/3 variety. Such as 12/3 (with ground) NM cable.
IF the unit required a 30 amp circuit then 10/3 would have been appropriate.



"And finally why is it called 220v if it's really 240v?
Who calls it 220v? Not me.
That is a generic term adopted by the masses.
Actually your oven is 120/240v, NOT simply 240v. There IS a difference.


 o
RE: wiring a 220v oven

Many code revsions ago the nominal voltages were added to the code. The nominal residential voltages are 120 V and 240 V. Both are RMS so the peak is higher by sqrt(2) = ~1.4
208 is most often seen as part of a 3 phase system, along with some other non-residential type voltage (high leg stingers, etc.)


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here