Posted by bojah (My Page) on
Wed, Jan 26, 11 at 23:10

I am running wire for a future hot tub and was wondering if 6 awg is enough? The hot tub calls for 4 wire, 240 volt, 50 amp. The run is 130' (110' indoor and 20' outdoor) using 1" liquid tight conduit.


Follow-Up Postings:

 o
RE: Is 6 awg wire enough for 130' to a hot tub

According to my calculations, at 130', you'll see a 2.5% voltage drop using 6 gauge copper wire with a 50A load. That should be just fine. I use http://www.nooutage.com/vdrop.htm as a calculator, so you can check my work.

Here is a link that might be useful: www.nooutage.com


 o
RE: Is 6 awg wire enough for 130' to a hot tub

Thanks a ton Kurto. I have been getting many opinions and didn't feel that anything thicker that 6 guage was needed.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

Question: Is it a code violation to use single colored wires?


 o
RE: Is 6 awg wire enough for 130' to a hot tub

For #6 and smaller wires, you must use white and green insulation for the neutral (if present) or ground, respectively.

You're free to use any color but white and green for the hot legs (and there's no requirement that different legs be different colors).


 o
RE: Is 6 awg wire enough for 130' to a hot tub

ronnatalie-
In a situation like this, can you use a white wire for a hot leg if you wrap it at each end with colored electrical tape to "change" the color, or must the entire jacket be colored?


 o
RE: Is 6 awg wire enough for 130' to a hot tub

You can mark a white wire black at the termination and all other points of access if you use it for a hot leg.

You can not remark a wire white to use it for the neutral.
You can not remark a wire green to use it for the ground.
You can not use a bare ground for the hot tub installed outdoors.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

You can't remark a green wire either.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

And you can only remark wire if it is part of a cable assembly and is to be used for switch loops, NOT individual conductors.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

Actually it doesn't have to be part of a switch loop (it does have to be part of a cable). The code says *IF* you use it for a switch loop, it can only be for the supply *TO* the switch not for the return to the outlet.

Older code versions let you use white for the switch loop feed without even bothering to remark it.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

"And you can only remark wire if it is part of a cable assembly and is to be used for switch loops, NOT individual conductors."

Not true at all, especially for larger wires.

Wires pulled into conduit are routinely re-marked to indicate phases, neutrals, etc.

Very large conductors are often available in ONE color --- BLACK.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

That only applies for larger than #6.


 o
nope

Nope actually brick, you can't EVER remark a white wire other than inside a cable. DOesn't matter if it's 0000.

Greater than #6 you can remark the non-white, non-green wires to another color.


 o
RE: Is 6 awg wire enough for 130' to a hot tub

That is not was was stated.

While the cases for remarking a white or green are limited, the remarking of larger wires to indicate they are a neutral or ground is allowed outside of cables and for larger wire sizes, many of which only come in black.

When I wanted bare 1500 MCM for a lightning down wire system luckily I needed enough to purchase an entire spool (the 4 foot wooden variety) because I had to get it made that way.

It blended into the brick on the face of the building nicely, instead of being an ugly black line.
We had to get a well drilling company to make a hole large and deep enough for the grounding rods.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here