Is 6 awg wire enough for 130' to a hot tub

bojah
13 years ago

I am running wire for a future hot tub and was wondering if 6 awg is enough? The hot tub calls for 4 wire, 240 volt, 50 amp. The run is 130' (110' indoor and 20' outdoor) using 1" liquid tight conduit.

Comments (15)

  • bojah
    Original Author
    13 years ago

    Thanks a ton Kurto. I have been getting many opinions and didn't feel that anything thicker that 6 guage was needed.

  • bojah
    Original Author
    13 years ago

    Question: Is it a code violation to use single colored wires?

  • Ron Natalie
    13 years ago

    For #6 and smaller wires, you must use white and green insulation for the neutral (if present) or ground, respectively.

    You're free to use any color but white and green for the hot legs (and there's no requirement that different legs be different colors).

  • kudzu9
    13 years ago

    ronnatalie-
    In a situation like this, can you use a white wire for a hot leg if you wrap it at each end with colored electrical tape to "change" the color, or must the entire jacket be colored?

  • Ron Natalie
    13 years ago

    You can mark a white wire black at the termination and all other points of access if you use it for a hot leg.

    You can not remark a wire white to use it for the neutral.
    You can not remark a wire green to use it for the ground.
    You can not use a bare ground for the hot tub installed outdoors.

  • Ron Natalie
    13 years ago

    You can't remark a green wire either.

  • normel
    13 years ago

    And you can only remark wire if it is part of a cable assembly and is to be used for switch loops, NOT individual conductors.

  • Ron Natalie
    13 years ago

    Actually it doesn't have to be part of a switch loop (it does have to be part of a cable). The code says *IF* you use it for a switch loop, it can only be for the supply *TO* the switch not for the return to the outlet.

    Older code versions let you use white for the switch loop feed without even bothering to remark it.

  • brickeyee
    13 years ago

    "And you can only remark wire if it is part of a cable assembly and is to be used for switch loops, NOT individual conductors."

    Not true at all, especially for larger wires.

    Wires pulled into conduit are routinely re-marked to indicate phases, neutrals, etc.

    Very large conductors are often available in ONE color --- BLACK.

  • Ron Natalie
    13 years ago

    That only applies for larger than #6.

  • Ron Natalie
    13 years ago

    Nope actually brick, you can't EVER remark a white wire other than inside a cable. DOesn't matter if it's 0000.

    Greater than #6 you can remark the non-white, non-green wires to another color.

  • brickeyee
    13 years ago

    That is not was was stated.

    While the cases for remarking a white or green are limited, the remarking of larger wires to indicate they are a neutral or ground is allowed outside of cables and for larger wire sizes, many of which only come in black.

    When I wanted bare 1500 MCM for a lightning down wire system luckily I needed enough to purchase an entire spool (the 4 foot wooden variety) because I had to get it made that way.

    It blended into the brick on the face of the building nicely, instead of being an ugly black line.
    We had to get a well drilling company to make a hole large and deep enough for the grounding rods.

  • PRO
    Blue Mountain Electric
    7 years ago

    Voltage drop does not occur in a run less than 1000' Wire size is required based on the size of the breaker being called for. Voltage drop is factored in as required by NEC for anything this size. The rule about distances between bends is the only thing to look out for. You can never have more than 360° of bends before you reach a junction or termination point.

  • Ron Natalie
    7 years ago

    Voltage drop does not occur in a run less than 1000'

    Nonsense. Even at 200' a 16A on 20guage current will have over 8% voltage drop.

    Wire size is required based on the size of the breaker being called for.

    Thanks for showing up five years after the fact with the wrong answer.