I have a gfi that has never worked. When replacing the bad? one I found out the load side was hot too. Since both sides are hot, could I just wire them together with a pigtail and connect the gfi plug?
RE: GFI wiring
Just a follow up, when I turn the breaker off for that gfi, both sides are dead. I'm assuming that since they are on the same circuit, it would be ok to connect the two and connect with a pigtail to the new gfi plug.
RE: GFI wiring
Hi Mr / Ms Orgnova,
One thing to check before you wire the two hot's together is to make sure that they are on the same phase. Is the breaker a single or double breaker? If it is a double breaker there is a chance that the two "HOT" wire are on a different phase. If that is the case then you cannot wire them together.
I am guessing that the GFCI will only be protecting that one plug position. So I would take one of the hots and put a wire nut on it and tape it up. I.E. just put it out of the way. You will not have a "LOAD" side connected up to the GFCI. I would then connect up the remaining Ground, Hot and Neutral wire to your GFCI.
Not the GFCI will then only protect that one outlet because you have no downstream LOAD outlets.
Warmest regards, Mike.
RE: GFI wiring
Hi! When you say that both line and load are hot, do you mean they're hot even with the GFI out of the circuit and not connected together?
If not, are you sure the line and load connexions were not reversed on the GFI? Some newer GFI's are designed not to work if it's the case.
RE: GFI wiring
"Some newer GFI's are designed not to work if it's the case."
ALL new GFCIs now detect if the power is applied to the LOAD terminals in error (instead of the LINE terminals).
What are you using to check the voltages?
RE: GFI wiring
If that GFI was wired that way, shouldn't you be worried about some other possible safety issues with the wiring in the entire house? I'd have it checked out.
RE: GFI wiring
Where is this GFI installed, what is its purpose, and who installed it?