| If pulling new/replacement THWN (90C) conductors through an existing (old work) conduit, containing old 60C (TW) conductors, are the old wires "grandfathered", or is there some mandate to upgrade all conductors in that "raceway"?
I'm "a-guessin'" that the 60C wires can be left in place, but all conductors in that conduit have to be de-rated per 60C tables... yes/no/elaborate/please enlighten the ig-nernt? Thanks in advance... assiduously rectifying jury-rigged wiring that would make even Pharkus go... Mr. Bill! =:O |
Follow-Up Postings:
|
| Unless you can find equipment to land the 90C wires on that is rated 90C you will be limited to 60C anyway (or whatever the equipment the wire lands on). |