Thu, Jan 14, 10 at 14:25
| Ok... Boat CFR's and NEC guidelines are not the same as housing.
Installing an older model stove - 3-wire vintage (it was free). Have run 6/3 to a 50A Breaker. 1) Would like the proper way to connect the neutral white wire and ground in the outlet and then in the sub-panel (can neut wht and grnd go together if I keep white and ground together in the breaker box? thanks. |
Follow-Up Postings:
|
| 1) Don't. Wire up the outlet for four wires hot,hot,neutral,ground and change the pigtail on the stove to a four prong to match the outlet. As long as you have the correct wiring you might as well do this correctly all the way. |
|
| I was not sure I could change the stove 3-wire config to a 4-wire. Than makes outlet and breaker box easy, however, I am not sure what to do with the white neutral and ground on the stove. |
|
| I don't know all the stoves but basically there will be a terminal block for 2 hots and the neutral. There should be a jumper from the chassis to the neutral connection, remove this and fasten the ground to the chassis. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.