code question on Microwave electrical supply

Posted by stash-hdy (My Page) on
Sun, Jan 24, 10 at 11:15

Want to add a builtin Microwave over the oven, there is not a plug in the space. There is a range hood next to it with a plug. Question can I tap into the range hood plug and run a plug for the Microwave?


Follow-Up Postings:

 o
RE: code question on Microwave electrical supply

Not unless the hood is on a dedicated circuit, which is HIGHLY unlikely.

You need to run a new circuit for it.


 o
RE: code question on Microwave electrical supply

thanks, that's why I asked. The microwave draws 13.9 amps is a 15 amp circuit sufficient?


 o
RE: code question on Microwave electrical supply

No, install a 20A.


 o
RE: code question on Microwave electrical supply

thanks, looking at my panel the slots are all filled. Can I use a double circuit breaker in a 20 Amp circuit that is already there? Are there any other considerations I need to be aware of using a double circuit breaker?


 o
RE: code question on Microwave electrical supply

thanks, looking at my panel the slots are all filled. Can I use a double circuit breaker in a 20 Amp circuit that is already there? Are there any other considerations I need to be aware of using a double circuit breaker?

You need to make sure your panel will accept tandem or half-size breakers.


 o
RE: code question on Microwave electrical supply

If you don't know about your box, check for the model number. It will have something like "letters" 2, 2 digit numbers "letters and numbers" on it. The first number is the total slots in the box. The second is the total allowed unit. In 1624, you would have 16 slots and 8 of them could be used for tandem or half-size breakers. Generally, if only some of the slots accept tandem breakers, it will be the bottom slots. The panel should have a wiring diagram on it for you to confirm.


 o
RE: code question on Microwave electrical supply

Where should the outlet be installed for the microwave? How High? In the cabinet above it? plug in or hard wired?
Mike


 o
RE: code question on Microwave electrical supply

In the cabinet above the micro; to the right side; typically low as opposed to high up; plug-in...NEVER hard wired.


 o
RE: code question on Microwave electrical supply

Thanks


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here