No pipe to ground to

Padraic482
12 years ago

I'm planning to wire my detached garage. There are no water pipes around it. My Black & Decker Home Wiring book says I'll need to ground the panel to BOTH a grounding rod AND an underground water pipe. Obviously, I can't do the latter. In a case like that, will the inspector let me get away with just a grounding rod?

Comments (23)

  • kalining
    12 years ago

    No offence but why don't you ask the inspector ? He is the one that will know. If i'm doing a job i'll ask the inspector
    what he wants. Ever inspector has a different idea of what
    HE or SHE wants.

  • jkjk
    12 years ago

    Subpanels can not be grounded. There is one ground in the system and that's at the main panel.

    As the previous poster said, ask the inspector:

    http://ths.gardenweb.com/forums/load/wiring/msg1115444822420.html

  • brickeyee
    12 years ago

    "Subpanels can not be grounded. There is one ground in the system and that's at the main panel. "

    Not correct if the panel is in a detached structure.

    If you do not have a water pipe, use two grounding rods.

    You can use a single rod if it is less than 25 ohms to earth ground.
    To make the measurement you need to drive another rod.
    Since you are only required to add one additional rod if the original is over 25 ohms, and no one want to remove a rod, just drive two rods from the start and skip the measurement.

  • jkjk
    12 years ago

    It's more complicated than that as the post I linked to suggests.

  • normel
    12 years ago

    It's more complicated than that as the post I linked to suggests.
    If is detached, the ground and neutral are separate and you require a ground rod (or two). Nothing complicated about that.
    Rules were changes in 2008.

  • jkjk
    12 years ago

    "Nothing complicated about that."

    It's not complicated if you look for the following:

    Form the cited post:

    "The requirement for no other metallic connections is very important. No phone line, cable tv lines, metal water lines. NO connection.
    This is to prevent the return of any currents on a secondary ground connection.
    If the conenction was made, the return currents would divide based on circuit impedance and a phone line would likely be quickly destroyed."

  • Ron Natalie
    12 years ago

    Sorry jk jk, but you are still dangerously wrong.

    If a structure has more than one circuit, it must have a grounding system. That means a primary ground system (two ground rods will do although there are other ways) plus you have to bond any water piping, structural metal, etc...
    This is the way it has been for decades.

    Prior to 2008, the no metallic connection exception allows you to avoid running a grounding conductor between the buildings. That exemption NO LONGER EXISTS and it was never a particularly good idea to begin with.

  • brickeyee
    12 years ago

    "Subpanels can not be grounded."

    You are confusing bonding of neutral (groundED conductor) and earth grounding of the panel.

    As a sub-panel the neutral is not bonded to earth ground in the separate building.
    As a separate building grounding electrodes are required.

  • westom
    12 years ago

    National Electrical Code defines five types of electrodes (building frame, concrete encased, ground ring, rod, or plate) acceptable for earthing. Any one of those electrodes is sufficient. Only earth electrode that is insufficient and therefore must be supplemented is an underground water pipe.

    Any metal water pipe must be bonded to the breaker box ground so that a wire fault to any pipe causes a circuit breaker to trip. Connecting to water pipes is bonding for human safety. And is earthing that is insufficient.

    This is only about what electrode is sufficient. Whether that sub-panel must be earthed is another and different topic.

  • jkjk
    12 years ago

    "This is only about what electrode is sufficient. Whether that sub-panel must be earthed is another and different topic."

    Thanks. I was misreading the question. That's the problem with me and the small phone screens. I apologize.

  • Padraic482
    Original Author
    12 years ago

    Hey guys,

    Thanks for all the responses. In my case, and given that I'm a total newbie at this, I think "ask the inspector" was probably the best advice.

    But just to clear up my situation: I have a detached garage. Currently (no pun intended) I have a single 110V circuit running out to it from the house via an underground conduit that powers a couple of lights and receptacles.

    However, I'm planning to move my woodworking shop out there and two of my machines run off of 220V. Since the basement is finished now, reworking the circuit that runs from the house to the garage would be very difficult and disruptive.

    But it would be relatively easy to bring entirely new, separate service in from the overhead street wires that run right in front of garage, and that's what I'm planning to do. So it wouldn't be a sub panel... it would be a brand new main panel with its own meter.

    I'm just wondering though... would it be possible to use the existing underground conduit in lieu of a water pipe? My only concern is that the panel would probably have to be mounted in the corner diagonally opposite where the conduit comes into the garage. So a ground from that panel would have to run around 30' of walls to get to the conduit.

    I'm going to ask the local Building Dept. anyway, but feel free to comment.

  • lbpod
    12 years ago

    You realize that this separate service is going to
    have it's own metering charges, (a monthly fee you
    pay, even if you use no power at all)? Also, it
    will be considered a 'commercial service', since
    it is obviously not 'residential', unless someone
    actually lives in the garage. Commercial services
    usually are a higher cost per KWH.

  • petey_racer
    12 years ago

    "No offence but why don't you ask the inspector ? He is the one that will know. If i'm doing a job i'll ask the inspector
    what he wants. Ever inspector has a different idea of what
    HE or SHE wants.

    No offense, but you are supposed to know what you are doing BEFORE you do a job.
    An inspector is NOT there to tell you what to do. He/she is there to (hopefully) catch the mistakes you might make.
    Also, it's absolutely NOT up to what he or she "wants". It is up to them to interpret and enforce the codes in place in your area.

  • brickeyee
    12 years ago

    "I think "ask the inspector" was probably the best advice."

    And any AHj should tell you to learn how to do re job.

    They are not here to give advice, and that is what you are asking.
    They do answer code questions that are asked many times, but rarely are wiling to lay out how to do a job.

    "would it be possible to use the existing underground conduit in lieu of a water pipe? My only concern is that the panel would probably have to be mounted in the corner diagonally opposite where the conduit comes into the garage. So a ground from that panel would have to run around 30' of walls to get to the conduit."

    The long distance is not a good idea, and will decrease the performance of the grounding electrode system. It will also be sort of pricey given the size of the grounding electrode conductor required (and that depends on te service ampacity).

    Listed electrodes are not all that expensive, and you would likely meet some resistance from the AHJ trying to re-purpose a section of conduit as a grounding electrode, if they would allow it at all.
    At the very least they would be well within their rights to want it exposed for examination.

    Just count on driving two rods at least 6 feet apart.
    Services are not a really good idea for a beginner.

    There are many details (including dealing with the local POCO) that all must be done correctly.
    Some of the rules you need to follow are not even in the NEC, since it technically does not apply to the distribution line from the POCO.
    The NEC has some rules for overhead lines, clearances, masts, etc. but the POCO still has the final say, not even the AHJ.

  • kalining
    12 years ago

    Sorry but you guys have no clue of what happens. I've had as many as 5 inspectors and non of them could agree on
    the way the job should be done. Yes i agree. We do know what we are doing but the inspectors have the last word. They are a bunch of kids that can't make it in the work aday world. Can't do the job and flunked out of everything they tried so they made them an inspector. They'er idiots. No offence to a real inspector. we had an inspector that was 200 percent wrong and an ass hole. He accidentally almost fell off the roof. But what can you do. Do it their way. Even if it is wrong but remember it's job security when you have to go back and fix it every week.

  • petey_racer
    12 years ago

    Yeah, no clue. That's what it is.

    How about you get your facts in order and arm yourself with knowledge against uninformed inspectors.

    They ONLY have the last word on things IF they are correct in their code interpretations. They CANNOT just make shi* up.

  • brickeyee
    12 years ago

    "Even if it is wrong but remember it's job security when you have to go back and fix it every week. "

    And job insecurity when something goes wrong and you can no longer get insurance.

  • kalining
    12 years ago

    Sorry guys. It doesn't work like that up here. If the inspector signs it off and you know damn well it's wrong you have no choice. We don't worry about insurance. The inspector is " god " . He or she is the one that goes down.
    Not us. Dictate to the inspectors up here and they can actually ban you from a job site they work on. My licence is insured. The department of labour backs us up in court because we are qualified. We live in a different world.
    Your electrical codes are similar to ours but not up to date. I've seen this site where the home owner can pull his
    or her own hydro meter to shut the power off and do work.
    Pull that off up here and you can be fined and or have your
    hydro shut off. You have to break a seal to do that. Their
    seal. They can actually charge you with trespassing and
    tampering with their property. Believe me, it's been done.
    2 ground rods in the same property ? Not allowed here.
    I'm sure you know why.

  • brickeyee
    12 years ago

    "2 ground rods in the same property ? Not allowed here. "

    The NEC called for a single grounding electrode for many years, and it could even be a metal water line with 10 feet i in earth contact.

    This was changed after it was simply found inadequate in some soil condition.

    A rod was than added along with the water line is usable.

    If no water line is available you must show the rod is 25 ohms or less to earth.
    Making this measurement requires a second rod to measure against.
    No one want to bother removing the second rod, and even if the first rod is more than 25 ohms, only one additional rod is required.
    In most cases it is just not worth the hassle, so two rods are driven.
    The NEC also requires the bonding of all electrodes, even from other systems (phone, cable TV, TV & radio antennas, etc.) to form a single grounding electrode system.

    There is not any great risk in this.

    In the USA we have way over 50 authorities, all using whatever code they have adopted (often the NEC as a basis, but with local alterations).

    The federal labor department has no say over things like state and local licensing, and licenses are issued with all sorts of limits (one city, one county, one state) but there are NO nationwide licenses.

    The USA is a republic, made up of 50 sovereign states.

    We hold individuals responsible for their actions, and saying 'the inspector made me do it' is not going to hold up well in a civil action (though it may protect you from criminal action).

    Once you lose a major civil action you will find your errors and omissions insurance painfully expensive (and in many places it is required to be in business).

    Probbaly time to find another profession.

  • Ron Natalie
    12 years ago

    The funky british spelling and the fact that he refers to the power company as hydro is a dead giveaway that the Kalining is a Canadian.

  • kalining
    12 years ago

    Of course i'm a Canadian. What was your first clue ? That is why our electric codes keep us alive. Yours ????? we have what is called an interprovincial licence. We have to take another course and another licence to be able to work in the entire country of canada. Interprovincial. If you don't have that you cannot work outside of your area. That holds true for the automotive trade and all construction trades. As i said before. It's a different world. Hopefully you will catch up to us. No offence to anyone.

  • Ron Natalie
    12 years ago

    Well in the past the big clue was most Canadians were polite and helpful, but I guess there are exceptions to all rules.

    The reason I brought it up is because it does not good for brick to argue NEC procedures to the Canadians nor you to argue CEC rules to those south of the border.

    Since the original questioner was from the US, I would recommend he followed us who gave the correct, legal, and safe rules that apply in the US.

  • brickeyee
    12 years ago

    "That holds true for the automotive trade and all construction trades. As i said before. It's a different world. Hopefully you will catch up to us. No offence to anyone."

    Just keep your socialist utopia on your side of the border.

    There is no reason to even try to "catch up" with such a scheme.