| I'm planning to wire my detached garage. There are no water pipes around it. My Black & Decker Home Wiring book says I'll need to ground the panel to BOTH a grounding rod AND an underground water pipe. Obviously, I can't do the latter. In a case like that, will the inspector let me get away with just a grounding rod? |
Follow-Up Postings:
|
| No offence but why don't you ask the inspector ? He is the one that will know. If i'm doing a job i'll ask the inspector what he wants. Ever inspector has a different idea of what HE or SHE wants. |
|
| Subpanels can not be grounded. There is one ground in the system and that's at the main panel. As the previous poster said, ask the inspector: http://ths.gardenweb.com/forums/load/wiring/msg1115444822420.html |
|
| "Subpanels can not be grounded. There is one ground in the system and that's at the main panel. " Not correct if the panel is in a detached structure. If you do not have a water pipe, use two grounding rods. You can use a single rod if it is less than 25 ohms to earth ground. |
|
| It's more complicated than that as the post I linked to suggests. |
|
| It's more complicated than that as the post I linked to suggests. If is detached, the ground and neutral are separate and you require a ground rod (or two). Nothing complicated about that. Rules were changes in 2008. |
|
| "Nothing complicated about that." It's not complicated if you look for the following: Form the cited post: "The requirement for no other metallic connections is very important. No phone line, cable tv lines, metal water lines. NO connection. |
|
- Posted by ronnatalie (My Page) on Fri, Jan 20, 12 at 17:29
| Sorry jk jk, but you are still dangerously wrong. If a structure has more than one circuit, it must have a grounding system. That means a primary ground system (two ground rods will do although there are other ways) plus you have to bond any water piping, structural metal, etc... Prior to 2008, the no metallic connection exception allows you to avoid running a grounding conductor between the buildings. That exemption NO LONGER EXISTS and it was never a particularly good idea to begin with. |
|
| "Subpanels can not be grounded." You are confusing bonding of neutral (groundED conductor) and earth grounding of the panel. As a sub-panel the neutral is not bonded to earth ground in the separate building. |
|
| National Electrical Code defines five types of electrodes (building frame, concrete encased, ground ring, rod, or plate) acceptable for earthing. Any one of those electrodes is sufficient. Only earth electrode that is insufficient and therefore must be supplemented is an underground water pipe. Any metal water pipe must be bonded to the breaker box ground so that a wire fault to any pipe causes a circuit breaker to trip. Connecting to water pipes is bonding for human safety. And is earthing that is insufficient. This is only about what electrode is sufficient. Whether that sub-panel must be earthed is another and different topic. |
|
| "This is only about what electrode is sufficient. Whether that sub-panel must be earthed is another and different topic." Thanks. I was misreading the question. That's the problem with me and the small phone screens. I apologize. |
|
- Posted by Padraic482 (My Page) on Sat, Jan 21, 12 at 11:36
| Hey guys, Thanks for all the responses. In my case, and given that I'm a total newbie at this, I think "ask the inspector" was probably the best advice. But just to clear up my situation: I have a detached garage. Currently (no pun intended) I have a single 110V circuit running out to it from the house via an underground conduit that powers a couple of lights and receptacles. However, I'm planning to move my woodworking shop out there and two of my machines run off of 220V. Since the basement is finished now, reworking the circuit that runs from the house to the garage would be very difficult and disruptive. But it would be relatively easy to bring entirely new, separate service in from the overhead street wires that run right in front of garage, and that's what I'm planning to do. So it wouldn't be a sub panel... it would be a brand new main panel with its own meter. I'm just wondering though... would it be possible to use the existing underground conduit in lieu of a water pipe? My only concern is that the panel would probably have to be mounted in the corner diagonally opposite where the conduit comes into the garage. So a ground from that panel would have to run around 30' of walls to get to the conduit. I'm going to ask the local Building Dept. anyway, but feel free to comment. |
|
| You realize that this separate service is going to have it's own metering charges, (a monthly fee you pay, even if you use no power at all)? Also, it will be considered a 'commercial service', since it is obviously not 'residential', unless someone actually lives in the garage. Commercial services usually are a higher cost per KWH. |
|
- Posted by petey_racer (My Page) on Sat, Jan 21, 12 at 13:23
| "No offence but why don't you ask the inspector ? He is the one that will know. If i'm doing a job i'll ask the inspector what he wants. Ever inspector has a different idea of what HE or SHE wants. No offense, but you are supposed to know what you are doing BEFORE you do a job. |
|
| "I think "ask the inspector" was probably the best advice." And any AHj should tell you to learn how to do re job. They are not here to give advice, and that is what you are asking. "would it be possible to use the existing underground conduit in lieu of a water pipe? My only concern is that the panel would probably have to be mounted in the corner diagonally opposite where the conduit comes into the garage. So a ground from that panel would have to run around 30' of walls to get to the conduit." The long distance is not a good idea, and will decrease the performance of the grounding electrode system. It will also be sort of pricey given the size of the grounding electrode conductor required (and that depends on te service ampacity). Listed electrodes are not all that expensive, and you would likely meet some resistance from the AHJ trying to re-purpose a section of conduit as a grounding electrode, if they would allow it at all. Just count on driving two rods at least 6 feet apart. There are many details (including dealing with the local POCO) that all must be done correctly.
|
|
| Sorry but you guys have no clue of what happens. I've had as many as 5 inspectors and non of them could agree on the way the job should be done. Yes i agree. We do know what we are doing but the inspectors have the last word. They are a bunch of kids that can't make it in the work aday world. Can't do the job and flunked out of everything they tried so they made them an inspector. They'er idiots. No offence to a real inspector. we had an inspector that was 200 percent wrong and an ass hole. He accidentally almost fell off the roof. But what can you do. Do it their way. Even if it is wrong but remember it's job security when you have to go back and fix it every week. |
|
- Posted by petey_racer (My Page) on Sat, Jan 28, 12 at 10:45
| Yeah, no clue. That's what it is. How about you get your facts in order and arm yourself with knowledge against uninformed inspectors. They ONLY have the last word on things IF they are correct in their code interpretations. They CANNOT just make shi* up. |
|
| "Even if it is wrong but remember it's job security when you have to go back and fix it every week. " And job insecurity when something goes wrong and you can no longer get insurance. |
|
| Sorry guys. It doesn't work like that up here. If the inspector signs it off and you know damn well it's wrong you have no choice. We don't worry about insurance. The inspector is " god " . He or she is the one that goes down. Not us. Dictate to the inspectors up here and they can actually ban you from a job site they work on. My licence is insured. The department of labour backs us up in court because we are qualified. We live in a different world. Your electrical codes are similar to ours but not up to date. I've seen this site where the home owner can pull his or her own hydro meter to shut the power off and do work. Pull that off up here and you can be fined and or have your hydro shut off. You have to break a seal to do that. Their seal. They can actually charge you with trespassing and tampering with their property. Believe me, it's been done. 2 ground rods in the same property ? Not allowed here. I'm sure you know why. |
|
| "2 ground rods in the same property ? Not allowed here. " The NEC called for a single grounding electrode for many years, and it could even be a metal water line with 10 feet i in earth contact. This was changed after it was simply found inadequate in some soil condition. A rod was than added along with the water line is usable. If no water line is available you must show the rod is 25 ohms or less to earth. There is not any great risk in this. In the USA we have way over 50 authorities, all using whatever code they have adopted (often the NEC as a basis, but with local alterations). The federal labor department has no say over things like state and local licensing, and licenses are issued with all sorts of limits (one city, one county, one state) but there are NO nationwide licenses. The USA is a republic, made up of 50 sovereign states. We hold individuals responsible for their actions, and saying 'the inspector made me do it' is not going to hold up well in a civil action (though it may protect you from criminal action). Once you lose a major civil action you will find your errors and omissions insurance painfully expensive (and in many places it is required to be in business). Probbaly time to find another profession.
|
|
- Posted by ronnatalie (My Page) on Mon, Jan 30, 12 at 10:38
| The funky british spelling and the fact that he refers to the power company as hydro is a dead giveaway that the Kalining is a Canadian. |
|
| Of course i'm a Canadian. What was your first clue ? That is why our electric codes keep us alive. Yours ????? we have what is called an interprovincial licence. We have to take another course and another licence to be able to work in the entire country of canada. Interprovincial. If you don't have that you cannot work outside of your area. That holds true for the automotive trade and all construction trades. As i said before. It's a different world. Hopefully you will catch up to us. No offence to anyone. |
|
- Posted by ronnatalie (My Page) on Mon, Jan 30, 12 at 19:41
| Well in the past the big clue was most Canadians were polite and helpful, but I guess there are exceptions to all rules. The reason I brought it up is because it does not good for brick to argue NEC procedures to the Canadians nor you to argue CEC rules to those south of the border. Since the original questioner was from the US, I would recommend he followed us who gave the correct, legal, and safe rules that apply in the US. |
|
| "That holds true for the automotive trade and all construction trades. As i said before. It's a different world. Hopefully you will catch up to us. No offence to anyone." Just keep your socialist utopia on your side of the border. There is no reason to even try to "catch up" with such a scheme. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.