oven/cooktop wiring

Posted by bhoublon (My Page) on
Wed, Jan 5, 11 at 9:13

I have a range fed by 6/2 al wire on a 50 amp breaker. I want to replace the range with a cooktop plus wall oven. They are rated at 5.8 and 7.2 kW.
If I add up and apply the demand factor I get 35amps.
Can I replace the wire with 8/3 copper and put it on a 40 amp breaker? The run is 50 feet.

Thanks
B


Follow-Up Postings:

 o
RE: oven/cooktop wiring

At least part of the answer will depend on what the installation instructions for the separate pieces say.

Sharing of a larger than required branch circuit can result in wiring being to small to sustain adequate fault current to trip the protection on the circuit.

This can leave equipment wiring to act as a fuse in the circuit if a fault occurs.

.


 o
RE: oven/cooktop wiring

The installation says 30 amp for the oven and 40 amp for the cooktop.


 o
RE: oven/cooktop wiring

The multiple unit demand factor?

It does not apply inside a single unit.


 o
RE: oven/cooktop wiring

It is a separate cooktop and single wall oven, installed in the same countertop space.


 o
RE: oven/cooktop wiring

The demand factors do not apply to equipment in the same space.


 o
RE: oven/cooktop wiring

Is that part of 220.55? I as assuming that I can handle one cooktop and up to two wall ovens on the same circuit as a range and apply the demand factor. I could not find a reference about the placement of the units.

Thanks


 o
RE: oven/cooktop wiring space

All I can find is: "The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens, all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range."
A range would have everything in the same space, too...


 o
RE: oven/cooktop wiring

I would go ahead and use 6/3 NM for the wiring. That would allow for future upgrading of the cooktop or oven. Your plan for installation is correct.


 o
RE: oven/cooktop wiring

"...adding the nameplate rating of the individual appliances and treating this total as equivalent to one range."

That means you just add them up, no demand factor.

I would still be inclined to run separate branch circuits to avoid dealing with larger conductors.


 o
RE: oven/cooktop wiring

Since you plan on runnng a new cable, why not use the old cable for the oven and run a new cable for the cook top.


 o
RE: oven/cooktop wiring

There is no space in the panel left for another 240V two-slot breaker. The current 50amp breaker has two additional 20amps on each side. I want to replace it with a normal 40amp two slot breaker, and add 2 double pole breakers in place of standard breakers to make up for the 20amp slots.
They are dishwasher and garbage disposal,so no worry of need to balance the load.
The cable is Al, I thought I would be safer with cu.

How could I connect the #6 and two #8 or one #8 and one #10 in the box and avoid a wire nut?

Thanks


 o
RE: oven/cooktop wiring

The garbage disposal and dishwasher do not need their own 20 amp breakers.


 o
RE: oven/cooktop wiring

Panel is full. Add a sub panel.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here