Tue, Jan 1, 13 at 8:52
| The breaker box has a 50 amp breaker installed. The replacement double ovens require either a 30 or 40 amp breaker depending on the one I choose. My question is do I need to change the breaker in the box to match the requirement of the double oven I choose? |
Follow-Up Postings:
|
- Posted by petey_racer (My Page) on Tue, Jan 1, 13 at 9:15
| It seems this question is self-answering. The existing 50 is meaningless. It just happens to be there. If you need a 30 or 40 you need a 30 or 40. |
|
| thanks, really don't know why the builder put in the 50 since the present oven requires a 40 amp. |
|
- Posted by petey_racer Upstate, NY (My Page) on Tue, Jan 1, 13 at 10:59
| He may have been planning for a full range and put the 50 in just in case. At least you know the wire is big enough. Better too big than too small in this case. |
This post was edited by petey_racer on Tue, Jan 1, 13 at 15:54
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Electrical Wiring Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.