Exterior lighting and recep rough in

Posted by attemptedgardener (My Page) on
Tue, Jan 5, 10 at 8:16

I was wondering what the standard practice is for wiring entrance lighting and exterior receptacles. Do you typically cut the sheeting and install a box or just stub out the wire? Also, I know the receps need to be GFI protected, but do the lights need to be on the GFI circuit or can they go on another lighting circuit?

Thank you,
Chris


Follow-Up Postings:

 o
RE: Exterior lighting and recep rough in

What circuits things go on is independent of GFCI protection. You can put your exterior receptacles and lighting outlets on any circuit not otherwise restricted.

Only the 120V 15/20A receptacles in the designated locations (outdoors is one) are required to be protected in general (discounting special equipment like pools/spas). Unless the manufacturer recomnmends/requires GFCI for the particular lighting fixture, I wouldn't bother.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Instructions

  • You must be a registered member and logged in to post messages on our forums.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • It is illegal to post copyrighted material without the owner's consent.
  • HTML codes are allowed in the message field only.
  • No advertising is allowed in any of the forums.
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.



 
Click here to learn more about in-text links on this page.