Dryer Receptacle

Posted by remington351 (My Page) on
Thu, Jan 14, 10 at 1:45

Hello Everyone,
I need some help with the wiring on my existing clothes dryer receptacle. The receptacle is a three prong type with 6ga aluminum type SE cable feeding it. The receptacle is currently nailed directly to my poured concrete basement wall. I want to finish the laundry area with 2x4 studs and drywall and will need to remount the receptacle to the new wall.

There is a bare copper wire that runs from the center post of the receptacle to one of the mounting nails that holds the receptacle to the cement wall. What is the purpose of the copper wire that is attached to the nail? Is this some type of grounding wire? Will I disrupt the ground path if I mount the receptacle to 2x4/drywall instead of directly to the concrete?

Thanks!


Follow-Up Postings:

 o
RE: Dryer Receptacle

I can't imagine *ANY* purpose to connecting a ground wire to a nail. If the box is metal, there should be a wire connecting to some fitting on the box (typically a SCREW used solely for that purpose tapped into the box, or other fitting). A nail would not suffice.

You should be extremely wary of any copper-to-aluminum connections and whether the receptacle is approved for aluminum wiring. Is there a separate ground in the SE cable? Is that connected to the receptacle (i.e., is it four pins). Your local authority may consider this enough of a renovation to mandate bringing that up to code, if not.


 o
RE: Dryer Receptacle

Thanks for the reply. I've tried to upload some pictures to show exactly what I'm talking about. Hopefully the links will work.

Here is a link that might be useful: Receptacle photo


 o
RE: Dryer Receptacle photo2

Here's another pic.

Here is a link that might be useful: Another photo


 o
RE: Dryer Receptacle

Pics are not very good quality. A copper wire running to a nail embedded in concrete is NOT a proper ground. Move the receptacle and ground it properly.


 o
RE: Dryer Receptacle

Looks like the nail was used as a grounding point for the receptacle box. The copper and aluminum together is a bad idea. A box is not allowed to be grounded through use of a nail either, has to be a threaded screw. Anyway there is no reason to leave this feed as it is if you are doing so much as putting Sheetrock up. You have to run new 10/3 with ground to your service panel, install a double gang nail on box to the stud for the wall. After sheet rock is up, install a 4 wire receptacle and change the cord on the dryer to a 4 wire cord/ plug. A lot of work but the only time to do it is now. Make sure the washer has a 20 amp dedicated circuit that is grounded as well since now is the time to bring up to code (required too).


 o
RE: Dryer Receptacle

Thanks for the responses. I was hoping to postpone upgrading to the 4 prong, but you guys have convinced me it's prudent to take care of it now. Thanks again.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Electrical Wiring Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here