Venting for range hood

Posted by rhoda_dendron (My Page) on
Sun, Jun 30, 13 at 20:51

Is this the right venting for a range hood. It doesnt look smooth to me, and i think te range hood should be more powerful. I think it s around 400 cfm.
Thanks fir any help!


Follow-Up Postings:

 o
RE: Venting for range hood

If that's 8", or even 6", ducting, I can't tell from the picture, it may be adequate. What does the range hood call for?
Personally, I'd prefer a roof mounted fan which draws the exhaust out, rather than a standard range hood fan trying to push the exhaust up to the roof. It's also quieter in the kitchen.
JMHO


 o
RE: Venting for range hood

No, flex duct is against code. Rigid metal only. And it only looks like 4" which will barely carry 250 CFM. You will need to redo this all the way through the roof with larger rigid ducting..


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Home Repair Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here