Fire Blocks in a wall

plumeriavine
14 years ago

When a partition wall is built, is a fire block included?

If so, what would it look like?

Are there different variations?

Comments (30)

  • brickeyee
    14 years ago

    It depends on what code is being used.

    The national codes only require blocking if the cavity is more than 10 feet tall, but many localities use a shorter height.

  • User
    14 years ago

    Interior walls have sheet rock as fire block. Walls between habitable areas and garages/storage areas might require more than sheet rock for fire blocking. Fire blocking is required when making a hole in interior to garage areas.

    Depends on local codes. Call your local codes or building inspection office.

  • sombreuil_mongrel
    14 years ago

    In our locality, we have to put them in if the wall is higher than 8 feet. They don't care where though, just as long as it cuts the distance to less than 8.
    Now, generically, sometimes people say fire-blocking when they mean fire-stopping, which isn't necessarily wood blocks, but could be; it's also permissible to be metal or rock wool, or a special fire-stopping foam insulation.
    Just wanted to cover all the bases.
    Casey

  • snoonyb
    14 years ago

    Old school;
    3 from a corner or doorway, 2 from a window interior or exterior.
    If I'm in the grove and the rhythm feels right, I'll continuos block.

  • plumeriavine
    Original Author
    14 years ago

    What is strategic blocking of interior walls for cabinetry?

    Reinforcing the wall for the cabinetry?

  • brickeyee
    14 years ago

    Blocking for cabinets, towel bars, toilet paper holders, etc.
    is not normally placed to block the stud cavity.

    The width of the wood is against the inside of the wall to provide as large a target as possible for fasteners.

    Sometimes even 1x lumber is used.

  • sombreuil_mongrel
    14 years ago

    Plumaria:
    It means that there is a continuous row of blocks, with the flat side out (to present a broad face) at the height of the tops and bottoms of the cabinet boxes (and countertop height if you want the Rolls Royce treatment) so that the cabinets can be hung without searching (sometimes in vain) for studs. It lets you put the screws inconspicuously right near the corners. It eliminates a second hole where the installer missed the stud on the first try. One disadvantage: the bottom wall cabinet line is where a lot of wires have to be for U/C lighting, plugmold, etc., and those wires have to be drilled through those blocks; you have to know exactly where you want the wires, and it's harder to relocate them later.
    Casey

  • macv
    14 years ago

    Most codes (including the IRC) require partitions to have vertical fireblocking at the ceiling and floor levels (usually provided by the top and bottom plates), and horizontal fireblocking not more than 10 ft along the wall (usually provided by the studs or mineral wool/fiberglass insulation).

    There are other fireblocking requirements for soffits, dropped ceilings, cove ceilings, chimneys, stairs, etc.

  • macv
    14 years ago

    Firestopping vs Fireblocking

    Before the members of CABO changed the organization's name to ICC and published the IRC, the 1995 CABO 1 & 2 Family Dwelling Code (section 602.7 "Firestopping required") contained the same requirements as the 2000 IRC (section R602.8 "Fireblocking required") except that the term "fireblocking" was substituted for "firestopping" throughout the section.

    I don't know why this change was made but it might have been a concession to SBCCI since it appears to be the only member organization that preferred the term "firestopping".

    Fireblocking requirements are independent of the requirements for construction of fire partitions, fire separation walls, and fire walls. They are also independent of the structural requirements for bearing walls and partitions.

  • plumeriavine
    Original Author
    14 years ago

    Related issue: is insulation mandated in partition walls?

    Sorting this out, sheet rock is a fire block for partition walls? Sheet rock means drywall?

    Which types of code books might have these types of details? You know, like NEC for Electrical, UPC for Plumbing.

  • macv
    14 years ago

    A partition is an interior wall so insulation is not mandated (I assume you mean by code) but you might add it for a small amount of sound isolation in walls without door openings.

    Sheetrock is USG's trade name for gypsum wall board, aka drywall. Drywall is not a "fireblock". You may be confusing the term fireblocking with a "fire separation wall" but that would only be required between separate dwelling units. The wall separating an attached garage from a single-family dwelling does not really have a name or a fire-resistance rating so it is effectively a smoke partition.

    This information should be contained in whatever building code is used in your community. Ask the local building department for the proper codes and then buy them online.

    Where is the project?

  • macv
    14 years ago

    A wall separating a dwelling from an unheated or partially heated garage would need to be insulated.

  • snoonyb
    14 years ago

    "The wall separating an attached garage from a single-family dwelling does not really have a name or a fire-resistance rating"
    Oh but they do. They are effectively an occupancy seperation and in some cases not only require a single layer of 5/8 drywall, where beneath a 2nd story deck or causeway designated as egress, 2 layers of 5/8th's on both walls and ceiling.

    The kicker is that a doorway has a 20min door on a self-c;osing device.

  • macv
    14 years ago

    All parts of a single-family dwelling, including a private attached garage, are considered the same occupancy so there are no occupancy separations. If the drywall is not fire-resistant (type X or type C) and is not required to be on both sides of the studs, the assembly cannot pass the ASTM test that establishes a fire resistance rating.

    I don't know why you mention decks and causeways, the OP was asking about partitions. I know of no code that requires a double layer of drywall at a garage. What code are you using? The IRC requires drywall on the garage side to be 1/2" non-rated gypsum wall board.

    As for doors in a shared garage wall, the IRC requires a solid wood door, a steel clad door, or a 20 minute fire-rated door but there is no requirement for the frame or an automatic closer so the assembly cannot meet the requirements for a fire-rated door.

  • macv
    14 years ago

    Until the OP tells us where the project is located or what code applies, it is pointless to answer code questions.

  • plumeriavine
    Original Author
    14 years ago

    thank you for helping to clarify. I've been trying to track down the governing codes. Sorry to not respond faster. It was not through a lack of trying.

    I fall under the 2007 California Building and Fire Codes.

    I've been wading my way through what I can so far find of the code book.

    I haven't found anything as specific as "fire resistant X or C on both sides of the studs." There's got to be something like that that applies.

    Anyone have any more clues?

  • plumeriavine
    Original Author
    14 years ago

    I am still working on this - - one partition wall has a washer/dryer on one side and the kitchen on the other.

    Should the wall behind the washer/dryer be considered a high humidity area and need cementboard instead of drywall?

    Maybe not - - just a question.

    There are numerous penetrations that haven't been filled in. Looking at firestops on Wikipedia, there seem to be standards for mending drywall and floors/ceilings that have had cables punched through. Any pointers as to if or when firestops are required for penetrations?

  • brickeyee
    14 years ago

    "Should the wall behind the washer/dryer be considered a high humidity area and need cementboard instead of drywall? "

    Humidity is not what requires anything extra, water does.

    In most houses only the walls around a shower or tub require a moisture barrier.

    Some places allow even tubs without a shower head to slide.

    The other bathroom walls can be regular drywall, along with kitchen back splashes, laundry areas, etc.

    It is the repeated soaking with water that creates the requirement.

  • macv
    14 years ago

    The 2007 California Building Code (CBC) is a modified version of the 2006 International Building Code (IBC) and both are published by the International Code Council (ICC). You can order a copy of the 2 volume set online from the ICC for $600 or from other code bookstores. Ordering it through a member of the ICC will save $120. There might be a set available at your local library; ask the local building inspector.

    Most other states have also adopted the International Residential Code (IRC) for one & two family dwellings 3 stories or less in height which is the code that I quoted earlier but California has not adopted it so it is necessary to find the requirements for occupancy group R-3, 1&2 family dwellings, and occupancy group U, garages.

    However, the requirements for private garage separation is the same in the IRC, IBC and the CBC except that the IBC and CBC also require a door closer.

    2007 California Building Code:
    "406.1.4 Separation. Separations shall comply with the following:
    1. The private garage shall be separated from the dwelling
    unit and its attic area by means of a minimum 1/2-inch gypsum board applied to the garage
    side. Garages beneath habitable rooms shall be
    separated from all habitable rooms above by not less
    than a 5/8-inch Type X gypsum board or equivalent.
    Door openings between a private garage and the
    dwelling unit shall be equipped with either solid wood
    doors or solid or honeycomb core steel doors not less
    than 1 3/8-inches thick, or doors in compliance
    with Section 715.4.3. Openings from a private
    garage directly into a room used for sleeping purposes
    shall not be permitted. Doors shall be self-closing and
    self-latching."

    The above referenced Section 715.4.3 allows doors with a 20 minute fire protection rating to be used in a "smoke-barrier wall" which is effectively what the garage separation wall is rather than a fire separation wall. In the CBC an attached private garage is considered an accessory occupancy use to the residential occupancy use so there is no occupancy fire separation required.

    Anywhere that hot gasses could rise from one floor to the floor above it (excluding floor openings for stairways, etc) must be fireblocked/firestopped. That is accomplished by the top and bottom plates of normal walls that don't have soffits, dropped ceilings, etc. Holes and spaces around pipes and wiring that penetrate the plates are normally sealed with a special fire-resistant foam. The building code describes what can be used and where.

    The wall behind a washing machine doesn't need any special treatment unless you are going to be hosing things down but you might want to provide an additional layer of drywall for sound separation.

    I am curious why you are asking these construction questions. Are you planning to build or repair a house yourself?

  • snoonyb
    14 years ago

    Interesting!
    1st this " macv (My Page) on Sat, Mar 6, 10 at 22:17
    All parts of a single-family dwelling, including a private attached garage, are considered the same occupancy so there are no occupancy separations.
    I don't know why you mention decks and causeways,"

    It was general information based upon 35+ yrs. of working on single, multiple occupancies including high rise commercial as and for contractors archetects, endineers and as an inspecter.

    "I know of no code that requires a double layer of drywall at a garage. What code are you using? The IRC requires drywall on the garage side to be 1/2" non-rated gypsum wall board."

    Would you like a list of the communities that i presently accomplish repairs for, which have this as an application?

    "As for doors in a shared garage wall, the IRC requires a solid wood door, a steel clad door, or a 20 minute fire-rated door but there is no requirement for the frame or an automatic closer so the assembly cannot meet the requirements for a fire-rated door."

    And now this;

    "However, the requirements for private garage separation is the same in the IRC, IBC and the CBC except that the IBC and CBC also require a door closer.

    2007 California Building Code:
    "406.1.4 Separation. Separations shall comply with the following:
    1. The private garage shall be separated from the dwelling
    unit and its attic area by means of a minimum 1/2-inch gypsum board applied to the garage
    side. Garages beneath habitable rooms shall be
    separated from all habitable rooms above by not less
    than a 5/8-inch Type X gypsum board or equivalent.
    Door openings between a private garage and the
    dwelling unit shall be equipped with either solid wood
    doors or solid or honeycomb core steel doors not less
    than 1 3/8-inches thick, or doors in compliance
    with Section 715.4.3. Openings from a private
    garage directly into a room used for sleeping purposes
    shall not be permitted. Doors shall be self-closing and
    self-latching."

    All of these are based upon the UBC and can be ammended to more closley reflect local applications.

    "IRC, IBC and the CBC except that the IBC and CBC "

    Certainly glad to have expanded your horizons.

  • plumeriavine
    Original Author
    14 years ago

    Thank you all for your detailed answers.

    If there is a tankless water heater in a basement, does that mean fireblocking/firestopping would be needed between the basement and the first story? I am thinking about the comment about the hot gasses.

    Additionally, if we vent a dryer from the first floor through the basement to the exterior wall, would this also be considered hot gasses?

    Does anyone have a picture of what top and bottom plates of normal walls look like?

    Does anyone have a code reference for the use of fire resistant foam in penetrations?

  • macv
    14 years ago

    I quoted the IRC because of it's almost universal adoption in the US and the lack of information from the OP regarding the applicable code. Then you contradicted me by quoting local ordinances or assuming the building is multi-family... for a homeowner on a home forum? Why would you feel the need to do that and how would it help the OP?

    I don't know why you have quoted what I said in the previous posts. Now that the OP has identified the building code I quoted the requirements from it. It all comes from the 2007 California Building Code which is taken verbatim from the 2006 IBC.

    The 1997 UBC required a 1-hour rated wall on the garage side but that code hasn't been the building code in California for 3 years.

    The UBC term "on the garage side" has always seemed odd since fire rating test standards require an interior partition to be able to be exposed to fire on either side of the wall so there can be no rating that applies one side of a partition and not the other. In fact, the original definition of Type X drywall is that thickness of the material that can achieve a 1-hour fire rating with an equal thickness on each side of the wall. That happened to be 5/8" thick at the time. 5/8" Type X on one side of a a partition and 1/2" regular drywall on the other is not a 1-hour rated partition. Three years ago, a local local building official might have accepted 2 layers of type X on the garage side as an equivalent or alternative to a 1-hour rated wall for a renovation project but it would not be allowed in new construction.

    If you are concerned about local ordinances modifying the 2007 CBC to require additional protection on the garage side, you should ask the OP where the project is located and find out if that municipality has enacted modifications rather than wasting your time harassing me.

  • snoonyb
    14 years ago

    "The 1997 UBC required a 1-hour rated wall on the garage side but that code hasn't been the building code in California for 3 years."

    This, again, is not necessesarily true. As I said, Its up to the interests and application of the juridictional authority. They can adopt it as written or make it more stringent, BUT NEVER LESS.
    That is why, here on the truely left coast, there is a State code and in some cases a county and or versions of the code adopted by the individual municipalitys.

    "If you are concerned about local ordinances modifying the 2007 CBC to require additional protection on the garage side,"

    Again, general information, which I am becoming convinced, you are immune to the concept of.

    "rather than wasting your time harassing me."

    You mean, of course, broadening your horizons.

  • snoonyb
    14 years ago

    "If there is a tankless water heater in a basement, does that mean fireblocking/firestopping would be needed between the basement and the first story? I am thinking about the comment about the hot gasses.

    Additionally, if we vent a dryer from the first floor through the basement to the exterior wall, would this also be considered hot gasses?"

    These two would be best addressed in the plumbing forum.

    "Does anyone have a picture of what top and bottom plates of normal walls look like?"

    Here is a very good site: http://www.awc.org/pdf/WCD1-300.pdf

  • macv
    14 years ago

    "Old school;
    3 from a corner or doorway, 2 from a window interior or exterior.
    If I'm in the grove and the rhythm feels right, I'll continuos block."

    That's all you could contribute?

    Can you be so ignorant about building code fire protection requirements that you don't know what hot gasses are or what fireblocking is?

    I don't think so; I think you are an internet troll pretending to be stupid in order to disrupt the discussion and you have succeeded because everyone is now gone so you can talk to yourself; I'm gone too.

  • sierraeast
    14 years ago

    "If I'm in the grove and the rhythm feels right, I'll continuos block."

    Taken as if you aren't in the groove, you dont solid block? Typical attitude of a racetrack tradesperson! I solid block whethwer Im feeling great, on a roll, or if I left the house after being bit by the dog. It's the project that's the consideration, not all about you!

  • snoonyb
    14 years ago

    sierraeast

    Sorry to hear that your having so much dificulty getting off the front porch.

  • sierraeast
    14 years ago

    It's called old age dude! The only thing to look forward to in this business is a bad back and a bad attitude! :-)

  • snoonyb
    14 years ago

    Really!

    I'm 68 and wear the bags every day.
    I guess the attitude is something to look forward too.