GFCI Breaker Tripping Spa Light

Posted by tbird355 (My Page) on
Sun, Aug 8, 10 at 20:19

I have a problem with GFCI breaker tripping on a Spa (hot tub) light. Here's the details.

This is a built-in spa (not premanufactured) built 20 years ago. There is a underwater Sta Rite (Pentair) enclosure built into the gunite wall. Installed in that niche is a Sta Rite 120 volt 250 watt fixture. The fixture is fed by a 16/3 captive cable that runs in a conduit from the niche to the equipment room on the other side of the wall. The 16/3 cable is connected via wire nuts in a jbox to 3 14 gauge stranded cables (black, white, green) in a conduit from the subpanel. The fixture is alone on a 20 amp GFCI breaker in the spa subpanel. The GFCI breaker trips as soon as it is set. Until recently, the light had been working fine. I swapped in a new breaker with the same results. Given that the fixture is 20 years old, I installed a new Sta Rite fixture. It also trips the breaker immediately.

I have tried a number of things to try and locate the problem but with no success. I took the new fixture and captive cable out of the spa and conduit and connected it directly to the breaker. That worked fine. With the fixture and cable back in place, I disconnected the ground wire in the jbox. The strange thing is that, with the ground wire disconnected, the breaker did not trip as long as the fixture was out of the water and not in its niche. As soon as the metal housing of the fixture touches the water, even slightly, the breaker trips. With the light fully installed back in the niche, one by one I disconnected the 3 wires in the jbox. With the ground wire and hot lead connected but the neutral disconnected, the breaker did not trip. The neutral connected by itself or the neutral and the ground connected caused the breaker to trip even without the light on. That tells me the fault is coming from the neutral. The problem is I can't imagine how the fault is occuring. It's a new fixture. The captive cable is new. There is nothing else on the circuit.

Any ideas?

Thanks.
Tom.


Follow-Up Postings:

 o
RE: GFCI Breaker Tripping Spa Light

What about the conduit feeding the J-box underground. Is it corroded? This could possibly cause it to ground out and trip the GFCI.


 o
RE: GFCI Breaker Tripping Spa Light

You replaced the GFCI breaker. Neutral from light feeds through this breaker. Verify that is correct.
You replaced the fixture.
Only thing left is the wiring from the J-box to the subpanel.


 o
RE: GFCI Breaker Tripping Spa Light

Here's an update on this. Pentair sent a replacement fixture and it works properly. The breaker does not trip.

Bottom line was that the original fixture was slightly leaking water and therefore creating a current path to ground tripping the breaker. The new fixture we purchased had defective electronics in the overload circuitry causing it also to trip the breaker. The replacement fixture from Pentair replacing the new one under warranty worked properly.


 o
RE: GFCI Breaker Tripping Spa Light

I hate problems like this, because the last thing that you would assume wrong is that the new fixture is bad.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Pools & Spas Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here