| Hi--I have a Polaris 180 that is driven by a booster pump switched by an old-school Intermatic timer. Power failures in my area have sometimes caused the booster to run when the IntelliFlo filter pump is off.
What I would like to do is have the booster pump switch on when the IntelliFlo begins a high-flow-rate feature. Is there any simple off-the-shelf pressure-switch or flowmeter-switch devices that would "sense" the increased flow rate/pressure and just switch the booster pump on/off? I *don't* want to add another controller to the system--the IntelliFlo pump seems very capable by itself. |
Follow-Up Postings:
|
| It woudln't be that hard to do. First get one of these.... http://www.amazon.com/Tecmark-Universal-Pressure-Switch-Fittings/dp/B0 03BGLD8I Then, run the power to the booster pump through a 24vac relay. Run power from a 24vac transformer through the pressure switch, to the relay. Set the pressure switch at 8+ psi so that it makes sure that the pump is running before it allows the booster on. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Pools & Spas Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.