Pipe size for inground pool
Hi
I'm in the process of contracting a pool that is 20x48 with an average depth of 5.75. The pool will include an 8 ft deep end and an 3.5 ft shallow. The shallow end will be 24 ft in length and the other half will be the deep end.
The contractor states using a 1.5 HP Hayward Super Pump, Hayward 240t filter and 1.5 inch pipe will be sufficient to keep the pool clean in a 10 - 12 hour turnover cycle.
My question is this. If a 1.5 inch PVC pipe can only take 42 GPM shouldn't the pool require a 2 inch pipe? They continually state that the pool will be fine with 1.5 inch pipe and state the following reasons for discouraging me away from 2 inch pipe.
1. more surface area in the pipe makes the pressure flow into the pool less, thus less pressure means less movement of water and more time for water to get back to the skimmers.
2. Any automatic cleaner you use will run slower and may stop and go and will need an upsize adapter to 2"
3. all inlets and outlets in the pool wall and floor are factory cut for 1 ½ " so an extra $600 will be added to the price to up size these openings.
I want to ensure 1.5 inch pipe is ok to use for a 20x48 pool because from what i have read a 42 GPM flow rate is the maximum for this size pipe. Please help me. I'm not writing a contract until I get this issue resolved.
Comments (47)
robindigo
16 years agoSounds like your builder needs some education. Encourage him to sign up for the construction school put on by the Genesis 3 Design Group in Atlanta in October.
West Hollywood Swimming Pool Builders · Arlington Landscape Architects & Landscape Designers · New Bedford Landscape Architects & Landscape Designers · Chattanooga Landscape Contractors · Deerfield Landscape Contractors · Fruit Heights Landscape Contractors · Golden Gate Landscape Contractors · Pacifica Landscape Contractors · Thonotosassa Landscape Contractors · Chicago Ridge Landscape Contractors · Shenandoah Landscape Contractors · Brentwood Decks, Patios & Outdoor Enclosures · Canton Decks, Patios & Outdoor Enclosures · Crystal Lake Decks, Patios & Outdoor Enclosures · Redmond Decks, Patios & Outdoor Enclosurespoolmd
16 years agoyour builder is out of the mindset of the 60's. he must be oldschool with absolutely no time spent in the classroom to learn or understand hydrolics.He is doing you no favors by insisting on small pipe,and what you save now will cost you month after month after month after month...need I go on!!
tresw
16 years agoThat's a big pool (42,000 gallons). At 42 gpm it'll take 17 hours to turn the water over once. Maybe they're coming out of the pump with 2" and then splitting into 1-1/2" pipe for the runs?
gorilla_x
16 years agoDepending on the slope of the pool floor, you've got anywhere from a 34K-42K gallon pool.
If 34K, a turnover in 12 hours requires 47 GPM. If 42K, 59 GPM is needed. So you've just exceeded the max flow on 1.5" pipe unless you extend the filtering several more hours... assuming there is one suction and 1 return.
The reality is if you have multiple suction pipes, you approximately double the max flow rate. If the skimmer and drain are piped separately (i.e. you'll have two 1.5" pipues pulling water from the pool), your pool can flow about 84 GPM.
Will 1.5" work? Sure, but you'll introduce a lot extra pressure in the system, thus reducing overall efficiency, and increasing electric comsumption.
I'm with the others here... you need 2" plumbing. Your plumbing will be more efficient. High efficiency means a lower electric bill.
I'll address your PB's raeasoning:
Quote: "1. more surface area in the pipe makes the pressure flow into the pool less, thus less pressure means less movement of water and more time for water to get back to the skimmers."They put a nozzle on the return pipes inside the pool, that is why you get a high pressure stream back into the pool. Nozzle's, because they reduce flow, increase pressure. My last pool had 2" pipes and 1.5 HP pump. No issues.
Quote: "2. Any automatic cleaner you use will run slower and may stop and go and will need an upsize adapter to 2" "
My last pool had 2" pipe and 1.5 HP pump. Had a Hayward Navigator suction-type cleaner. Worked like a charm.
Quote: "3. all inlets and outlets in the pool wall and floor are factory cut for 1 ½ " so an extra $600 will be added to the price to up size these openings."
This just sounds like the company making the panels never upgraded, so they want to stick you for $600.
highlt
Original Author16 years agoGuys I appreciate the feedback. Not sure what to do about letting this person build my pool now. They have been buildings pools for 31 years but it's ashamed I have to do this kind of home work.
highlt
Original Author16 years agoBottom line question:
Does 1.5 inch PVC pipe only support 42 GPM? I believe 2 inch supports 62 GPM.
Thanks
TErryRack Etear
16 years agoYou can move 150 gpm through a 2" pipe, but it will take about 90 psi to do so,.
7 feet per second or less typically seems ideal, and 2" at 7fps is 80 gpm.
The returns on our pools are 1 1/2 ", but you have multiple returns to carry the load of the filtration system. So you would split a 2" or 2 1/2" then reduce to the 1 1/2" at the pool wall.
2" returns are very difficult to find eyeballs for, and the eyeballs end up being 1" anyways which brings you to where you were before w/ the 1" pipe.
Think about this also.2" pipe costs less than 20% more than 2" pipe. When we are talking about plumbing and entire pool the increase pipe size will costs less than $100 more
pauster
16 years agoI am paying $300 extra for my pool builder to upgrade from 2" to 2 1/2" pipes (for each individual run) on a 28K or so gallon pool. I expect to have a very short return on my investment due to the energy savings becasue of much lower resistance (2 1/2" has about a third of the dynamic head of 2" pipe in scenarios that apply to pools)
highlt
Original Author16 years agoGuys-
I'm still confused on exactly what can be run in 2 inch pipe. Is it possible for pump/filter, skimmers, inlets to use 2 inch pipe? Is there anything that can not use 2 inch. My builder is stating price will go up $600 for pipe and if I need 2 hp pump for 2 inch pipe and upsize filter too. Is it really worth all of this cost versus using the 1.5 inch?
Rack Etear
16 years agoYou can uss 2" pipe on a 1/2 hp pump. A 2hp pump should not use 2" pipe but 2 1/2" or 3" pipe.
There should be no "upcharge" for 2" pipe, as that is what every pool company should use on a pool over 5,000 gallons.
You can run a 1/2-1hp on 2" on 1.5-2.0 you either want multiple 2" pipes or upsized pipes.
comkow
16 years agoDon't mean to hijack, but
We will also be installing a 18x36 ig vinyl pool next month. No extra water features or spa..only solar heat.
What size pipe should the pb use if we have the intelliflo 4x160 variable pump (no exact hp per se). I have already told him we want 2in, and our pb also told us that would be an extra charge. Would we need 2 1/2"?
Rack Etear
16 years agohuh?
For the flow demands of your pool, and assuming they use 2-2" suctions 1 md 1 sk,
2" will be fine.
comkow
16 years agoAn Intelliflo 4x100?? Can't seem to find any pump like that. Do you have a link?? Is it still variable?? With the solar and a SWG, we will need to have the water constantly flowing and was trying to do it in the most energy efficient way.
Our pool will have 2 bottom drains that will be tee'd, 2 skimmers (1 shallow end, 1 deep end) and 4 returns (more returns if needed based on step-n-spa and width of steps)
2" pipe still sufficient??
poolexpert
16 years agoI stand corrected it's a starite but its owned by the same company.See the link. The problem the manufactures are running into is liability for entrapment especially if you sell someone a pump that is way to powerful for the existing plumbing. Its a pentairpool.com/pdfs/intellipro4x160m.pdf
Your solar installer should be able to dial in the most efficient flow rate for the solar by check incoming and outgoing temps.
If you go with the large 160 you need to follow the instruction in the pentair installation guide even though you can set the flow lower to accommodate the smaller pipe it probably would never be an issue with two skimmers and dual main drains but inspectors go by the letter of the law.Rack Etear
16 years ago" but inspectors go by the letter of the law."
Does anyone here have inspectors looking at pump curves and verifying pipe sized?
With 2 skimmers and dual main drains and 2 -2" pipes the water is moving at 7fps @ 160gpm.
highlt
This is scaring the hek out of me. My pool will have 2 returns and one drain. The builder insists that 1.5 inch pipe, with a Hayward 1.5 pump and and Hayward 244t filter will work fine.
I'm still confused at how to calculate the turnover rate. The pool builder states since there are two returns you can double the GPM.
They stated they will put in what I want but it will cost at least $600 more and they do not feel I will gain anything for my money.
Is there anyone, that can show me how to calculate the proper size pipe for this 20x40 pool? I'm lost on how the returns etc. affect this.
My builder is recommending the following:
1.5 inch Rigid pipe
244t Hayward Filter
2 returns
1 main drainThey have been building pools since 1977 and state they have never put anything larger than 1.5 inch pipe in. I'm afraid to tell them to use 2 inch pipe and have them screw up the plumbing or sizing the filter, pump properly. I'm ready to go but will not sign contract because of my fear of the pipe. I'd love to be able to see the calculations to determine exactly what I need. If I need to supply more information, please tell me and I will provide what's needed. I really appreciate the help.
highlt
I have post above with questions too but below is what I really need to understand.
If I use two inch pipe, does the filter, pump, inlets and returns need to accept 2 inch pipe or can 1.5 inch reducers be used? If reducers are used is there any advantage to using 2 inch pipe?
I'm asking this question because the inlets on pool are 1.5, the filter and pump are 1.5. I would have to upgrade my pump to 2 hp to get a Hayward super pump with 2 inch connector and the filter would have to go to Hayward 270t2. If I can run 2 inch pipe and use reducers, then the only cost impact would be the move to 2 inch pipe versus upgrading to more expensive pump, filter and having to have inlets that are 2 inch.
highlt
This pool dealer is reputable and all the customers I've contacted are happy. I just don't take anyone's word for anything and I'm trying to ensure the best plumbing system. My friend has same pool with there recommended setup with no issues for 1 year but I'd prefer to setup
the most efficient way.I have post above with questions too but below is what I really need to understand.
If I use two inch pipe, does the filter, pump, skimmers and returns need to accept 2 inch pipe or can 1.5 inch reducers be used? If reducers are used is there any advantage to using 2 inch pipe?
goodtimesnoodlesalad
16 years agoTwo returns? Is that enough? And to take the pump outlet up to 2" pipe then drop to 1 1/2" at the fittings going to the pool wall should'nt add much to the cost. Seems odd.
highlt
Original Author16 years agoYeager-
I live in the cincinnati/dayton ohio area. Maybe I'm anal but I trying to learn the best way to plumb this pool and the number of skimmers and returns.
Rack Etear
16 years agoHighlt
The math is easy,
20*48*5.5*7.5= 41,400 gallons.
To calculate the turnover you desire, I like 8-12 hours for a residential pool, let's use 12 for this equation as 12 is more prudent with a large pool such as yours.
41,400/12/60 = flow rate to achieve a 12 hour turnover.
In this case it is 57.50 GPM
Could we achieve this with 1 1/2" pipe? Sure but it will run 9.16 fps. 7 or less is what is desired on most swimming pool systems with 5 being ideal for suction lines.
I dont have any Hayward pump curves here nor do i care to, so I will use a whisperflo's curve for a baseline.
At 50' thd (head) a 1.5hp whisperflo will move 110 gpm. Now if we take this flow rate and put it through a 2" pipe we are looking at about 10fps at this flowrate. Which is over our 7fps. So we need either 2-2" pipes ~5fps, or 1 2 1/2" pipe which the water will move around ~7fps through.
It's impossible for me to calculate the tdh over the net and even that is a rough approximation.
Now getting to the filter. Typically the Maximum should be 20 Gpm per Sqft. The 244 is what I imaging you are getting is 3.14sqft that means that you can move a maximum of 62gpm through the filter which is far less that what we should expect from a 3/4hp pumps these days.
Long story short get a 1.0 hp full rate pump preferably a whisperflo. Add a 30" sand filter, and all 2" piping and you will be all right. Make sure that they have a individual pipe for the main drain and the skimmer. I would also suggest 4 returns on a pool that size. Just about every quality piece of equipment made these days has 2" or larger in and out.
My sizing is actually considered undersized as far as the piping goes for some builders, but anything bigger on a 1hp and the pump would more than likely cavitate and be a little bit louder than I would like. 80 gpm seems about right from a 1.0 hp pump it hits the pumps peak efficiency curve nicely.I cannot say their system doesnt work, however it give you no room to expand, and is very inefficient. I thought the people I worked with up here were dinosaurs when it comes to pipe sizing, but 1 1/2" pipe on a 45k gallon pool, most pools this size from the early 70's have 2" pipe.
highlt
Original Author16 years agoRacket-
I really appreciate your help. Another question. The builder stated:
"all inlets and outlets in the pool wall and floor are factory cut for 1 ½ " so an extra $600 will be added to the price to up size these openings."
Do the inlets and outlets on pool need to be enlarged to 2 inch or is it ok to use a reducer to fit the 1.5 opening on pool? Would the reducer defeat the purpose of having 2 inch pipe?
highlt
Original Author16 years agoWhat do you think of this for the pool plumbing versus there recommendation.
My Plumbing recommendations based on feedback
1. 2 drains (plumbed together with shutoff valve)
2. 4 returns (seperately plumbed with shutoff valves)
3. 2 skimmers (seperatley plumbed with shutoff valves)
4. 2 inch pipe for everything
5. s270t2(3.71) filter 2 inch
6. Hayward Super Pump II 1.5 HP 2 inch fitting
7. Hayward Heat Pump 1.5 fitting so have to use reducer to connect 2 inch pipe* I guess based on my prior question. I will ask is it a viable option to use 1.5 pipe for return lines since the pool has 1.5 inlets and outlets or stick with 2 inch all the way around and have them use reducers? I will also assume the skimmers have 2 inch fittings?
The pool company's plumbing recommendations
1. 1 drain
2. 2 returns (sperately plumbed with shutdoff valves)
4. 1.5 inch pipe for everything
5. s244(t3.14) filter 2 inch
6. Hayward Super Pump 1.5 HP 2 inch
7. Hayward Heat Pump 1.5 using 1.5 pipeRack Etear
16 years agoDo the inlets and outlets on pool need to be enlarged to 2 inch or is it ok to use a reducer to fit the 1.5 opening on pool? Would the reducer defeat the purpose of having 2 inch pipe?
No, the purpose of having 2" pipe is to reduce the velocity which in turn ruduces the energy used to move the water.
If you have more than one inlet, which you should, then there will be multiple lines that split off the larger trunk line.
1. ok
2. you only need 1 return line, balancing can be done if desired with different sized eyeballs. To Plumb and valve everything would be very expensive with little result.
3. 2 skimmers can run off of 1 2" pipe, you can run them independently, but its not needed.
4. 2" pipe is good, if you have to reduce its ok to do it at the appliance, or pool.
5. I would use a 30" tank for a pool this big, you will exceed the max flow rate on a 24 and have far more frequent backwash intervals.
6. I don't like superpump's I'd Suggest Pentair, or Jandy pumps as they seem to be the best built and supported.
7. I don't trust hayward to make a heater let alone a heatpump. I would look into Raypak, Pentair, or aquacal offerings.You will not get me or most people on this forum to approve hayward product, it is cheap macro builder equipment with horrible service and support. Even something as simple as a ball valve they seem to mess up. I am a Pentair backer but I also like Jandy, and Sta-rite's offerings.
I know talking to other people in your position that it can take an act of god to get people to derive from their standard equipment selections, but it's worth a shot because their warranty is more than likely one year, but I would imagine you are going to have to live with this for a very long time.
highlt
I really do appreciate all of your help. A couple of last questions in regards to your feedback.
"So your point is to have 1 single line ran but have 4 different returns plumbed in the same pipe?"
"Will I not gain more pressure if I run these independently?"
- 2" pipe is good, if you have to reduce its ok to do it at the appliance, or pool.
"As result, you are recommending to leave the 1.5 inlets/outlets on pool and save the $600 upcharge?"
The only reason I was thinking about plumbing returns and skimmers seperately is in the event of a pipe leak I could just shut off that line and not bust all the concrete out to fix it. Do you think it would make sense to do the follwoing for this pre-caution.
Put 4 skimmers in and have 2 on each independent line. Put 4 returns in and have 2 on each independent line.
In the event of a LEAK, I could shutdown the line for the skimmer or return with the LEAK and still have 2 skimmers or returns and not have to bust the concrete up. This is going over board but I would not ever want to bust it up with the price of concrete.- 2" pipe is good, if you have to reduce its ok to do it at the appliance, or pool.
Rack Etear
16 years agoYes,
You may, but the suggested flow rate over the weir in the skimmer is about 1/2 a 2" pipe would handle.
4 skimmers is overkill. If you have a leak, the extra piping would give you more options. After all it is your money so if you feel it is worth it I couldn't say the extra piping is detrimental in any way.
highlt
Final decision. I've narrowed this down to two options and would like some feedback on what people think is the best.
Option 1
1. 4 returns plumbed on seperate lines with ball valves on each line
2. 2 skimmers plumbed on seperate lines with ball valves on each skimmer
3. 2 drains on the same line tee'ed with a ball valve
4. Hayward S370T2 filter
5. Hayward Northstar 1.5 HP pump
6. Everything is plumbed in 2 inch pipeOption 2
Same as above except the underground pipes are 1.5 inch and all run into 2 inch manifold so all lines coming from 2 inch manifold go to 2 inch connectors on pump and filter.I'm considering option 2 because one of the pool builders is concerned I will not have enough suction for pool clearn if I use 2 inch underground. Any suggestions.
highlt
Original Author16 years agoDid you guys give up with the feedback? I'd really like a last opinion before signing my contract and deciding on best way to plumb it.
mnyzip
15 years agoI had a pool installed with 1.5hp pump with 1.5" lines. Contractually, I was suppose to get 2HP pump with 2" lines. The pool is backfilled and now my question is can I use the 2hp pump and leave the 1.5" lines? It is a 40 thousand gallon pool with 7 returns and 2 wide mouth skimmer one main drain and 2 side wall drains. Do I need 2" lines with 2 hp pump?
Walt Lange
8 years agoActually all of you calling the builder an idiot are morons. An in ground pool will have 2 skimmers and a main drain so that is 42 gallons per min x 3. That = 126 Gallons a min. for those of you that flunked math!!!! Those of you that have called the builder and idiot need to get a life when you have no idea what your talking about. Feet to pump head makes a difference also but, the nominal flow is between 50 to 70 gallons a min @ 60 feet away for a pool that size. That brings me to the pump. Most pumps 1.5 HP pump roughly 70 to 90 gallons a min so, 1.5 in plumbing is just fine. All code around the country is 1.5 residential and 2 inch for commercial! Building pools for 35 years makes me right and all of you wrong! Extreme Pools/ Gator's Pool Service Machesney Park Illinois! www.xpools.net
premier pool plumbing
8 years agoAs for someone calling a builder an idiot, not cool. I've only been pool and spa plumbing in AZ, NV, and CA for 22 years and have never used less than 2.5" suction 2" return since 98' on the pool. 3" suction 2.5" return spa. The last 2 yrs in AZ pipe size and sweep 90's has slowed us down too plumbing only a P+S per day from P+S & pool per day, only CA where we also plumb gas lines. 2 P+S per week. When the government demands variable speed plumbing will all change. I've plumbed over 3500 and ready to plumb in the woods PA, NY.
Aqua-Link Pools and Spas
8 years agolast modified: 8 years agoWalt. I agree the term idiot is inappropriate. Maybe uneducated should be a better term. Unfortunately you are giving out bad and dangerous advice yourself. Lets follow the minimal defensible standards that are set forth by the APSP of feet per second of water through SCH 40 PVC pipe. Copper and SCH 80 will have different values. The maximum FPS for suction is 6.5 and return is 8.0. Most 1.5hp pumps according to the pump charts at 50 feet of head will pull 120gpm. An example would be the Pentair Whisperflo. You can't just go by how many skimmers you have, you have to go by what is being pulled through that one pipe. At 120gpm that would mean you would need a 3" suction and 3" return to get to the APSP minimum standard. Most municipalities require a 1.5fps flow through the suction outlet. There would be no way you would get that rating with 1.5" or 2" pipe size. That's just a basic set up of plumbing hydraulics. It gets more detailed as you work your way down the pipe. Just because you have a 1.5hp pump does not mean you use a 1.5" pipe! Size the plumbing to what you want to achieve with the pool and then the pump to the plumbing.
8 years agoPremiere. I wasn't referring to you in the post but I'm not sure I understand what you wrote either.
Walt Lange
7 years agoFirst, I see a lot of people calling this builder an idiot and he is not. I been building pools for 35 years. The flow thru a 1.5 line is 42 gallons a min. It will decrease slightly after you get a ways a way. If you have 2 skimmers, 2 main drains that are tied together and you get to the manifold which I use 2" you can only get so much thru a 2 inch anyway. Max thru the pump per min re-guardless of pump size is 72 gallons per min with because you have 2 inch feed. A bigger pump just causes more head pressure and that is what you need to get good movement in the pool. At the filter lets say a Pentair 24" sand dollar it is 1.5" in to the filter and 1.5 out. So here you are again at 44 gallons per min. You can control the pressure and movement of the pool by using small return jets if you are further away causing a little more head pressure.
The standard for all residential pools is 1.5 inch pipe and best way is to run it all to a 2 inch manifold in to the pump. This will create good head pressure and the pool will be fine with a 1.5 horse power pump. The thing you need to do is make sure you have a good pump med. to high head. To the guy above,,,,there is no way to run 3 inch plumbing with a residential filter max size being 2 inch. You would need a commercial filter to achieve this. Like I said lots of these guys will take you to the bank these days making you believe you need bigger plumbing then you actually need. I build lots of ingrounds every year and always put the pumps and filters at the house and in some cases return lines are 150 feet away and all of these pools run fantastic with 1.5 inch plumbing as long as you run seperate return lines. The closer returns you use smaller eyeballs to make them all the same pressure! Just make sure you have a good high head pump!
www.SwimmingPoolSteve.com
7 years agoIt is important to differentiate what will work from what is a good idea. If the pool is built as per the specifications you have provided it will likely run OK and be clear most of the time. That certainly does not make it a good idea. There is absolutely no excuse for building such a large pool with such an undersized plumbing system. The efficiency from friction loss in the plumbing lines would be very high, and you will be very limited in terms of pump options since most new pumps need more flow than 1.5" pipes can supply. From a theory perspective the suction lines should be 3" or 4" in size for maximum efficiency...2" is really considered the new smallest size. Plumbing with 1.5" on anything not an above ground pool is just silly.
stein_eric
7 years agoHello
I need advice on pool plumbing. My pool is 56 years old. It was originally plumbed with 1 main drain and 1 skimmer and 1 return line. The main drain was decommissioned years before we bought the house.
We have been running this pool successfully for 14 years with one 1 1/2" skimmer inlet and 1 return line and a Navigator bottom cleaner. The long run plumbing is 2" and system worked fine. I re-plumbed the pump and filter area with a new Hayward 48' with Vaiflow valve with all 2" pipe in and out. So now all pipe is 2" out of ground through all appliances then back to 2" return line. The old system was 2" coming out of ground then 1 1/2" going into and out of pump with 1 1/2" coming out of filter to the simple back wash valve then back to 2" return. This worked just fine. Water was always clear.
However, after the all 2" set up was completed I have had air bubbles coming out of the return line. I inspected all fittings and there is no visible leaks anywhere. The pool will not clear up like it used to and I am thinking that the 1 1/2" step down into and out of the pump was there for a reason that I didn't realize.
When I hook up my Navigator bottom cleaner to the suction line in the skimmer it creates a lot more air bubbles in the return line
Any thoughts on this? Summary below:
Old system: worked great
1 Hp pump
48 sqft DE filter
1/12" skimmer inlet
2" pvc long run pipe
1 1/2" pipe into and out of pump
11/2" in/out filter
Simple back wash valve
New System: lots of air bubbles and pool wont clearSame 1 Hp pump
New 48 sqft Hayward filter
New Hayward Variflow valve
Same 1 1/2" skimmer inlet
Same 2' long run pipe
New 2" pipe into and out of pump
2" into and out of filter
Thank you!www.SwimmingPoolSteve.com
7 years agoEric - You have a leak in your system. Probably introduced when you did the plumbing work. Does the pump run clear (no air visible in the chamber)? If so the leak is past the pump somewhere. If the pump has air in the chamber then the leak is on the suction side of the pump.
HU-704438095
3 years agoI need help. I have a 18x36 pool with 5 returns (2 are step jets), 2 skimmers and 2 main drains and a waterfall. I have 1.5 inch lines and a 1.5hp pump. Is it safe for me to upgrade to a 2hp pump? Pump and filter are about 30 feet from the pool.
Mystic Pools, LLC
3 years agoIt's not so much a safety issue provided your drain covers are approved type, but a 1.5HP pump is oversized for the 1.5" plumbing and certainly a 2HP pump is WAY oversized for that size plumbing. You will NEVER get the full benefit of that 2HP pump's capability.
The illustration I've given to clients for years in a situation like this is, with an oversized pump, it's like sipping water through a cocktail straw. It draws more air than water as the pipe is too small and never gets the volume it's meant to handle. The pumps cavitate and are super noisy. Not too surprisingly, builders still use too small of pipe on new pools.Your best bet is a 3/4 HP pump.
Our suction lines on new builds or renovations are a 2.5" minimum. Often 3" and with spas sometimes 4" for spa jets.Elvir Mujahodzic
3 years agoHello . I couod
use your
professional help. The tool guys seems like a jerk .. I just bought a house with a inground 20x40 pool , it has a old Hayward sand filter , and a 3/4 hp pump . The pool is roughly about 35,000 gallons . the person I bought house from just out in a new liner , but before the pool
hasnt been used in 20 years from what the neighbors tell me . From what I can understand ( i am a plumber ) the pool has 2 skimmers , a main drain all seperate piping with 3 ball valves , and 3 jets where the water blows back into
the pool but 1 pipe ( 1.5 ) leaving the pump .. we had eveeything treated by the pool company and I even took the water sample into a pool
store . we could not get the water clear , it’s somewhat clear by the shallow end but the deep is is still
vwey cloudy . the pump runs for
12 hours a day . Reading thru a lot of things online i Am guessing the old sand filter might just need to be replaced , ( 20 years old ) from
what neighbors tell me . Will replacing the filter solve my issue ? Or
is the 1.5 piping with 1 Supply be my main issue ? What do you recommend . ? Tia
Mystic Pools, LLC
3 years agoI'm partial to diatomaceous earth filters or multi-cartridge filters. We have only a couple of clients with sand filters.
If a sand filter is to be used, glass media is a better choice instead of sand.
It sounds like your filter is just not performing properly and more than likely the sand is no longer trapping dirt and debris.But, you should be running the filter 24/7 to try to clear the water. Not 12 hours just yet.
If after a few days running continuously the pool is no better, than consider changing your filter.
Diatomaceous earth filters(DE) trap the most microns per square inch. Multi-cartridge filters are not far behind. Sand filters trap the least but if glass media is used, they work very well.
I would use the largest DE filter or the largest multi-cartridge filter. DE filters require more maintenance but provide the best clarity.
The 3/4 HP pump is ok. Don't go any bigger. The pool will run ok on 1.5" pipe but larger pipe is recommended. I have plenty of older pools with 1.5" pipe and have no issues.
Start with your filter first, running 24/7 and check the results before spending for a new filter.Ronaldo Lizardo
2 years agolast modified: 2 years agoThis guys is what I got for plumbing. all is 1.5“ the pump is VS FLOPRO™ 0.85 HP AND 1.65 HP.
the pool has 2 skimmers, 1 main drain all Independent lines. Then have 4 returns with 3 lines and 4 deck jets with one line.
I ask the pool builder to put 2” pipes from where all the lines come together to the pump to where it gets all connected to push water to the pool. He stated it was not necessary.
what you guys think, will this setup work for a 32-35k gallon pool?
Mystic Pools, LLC
2 years agoI this a new pool? Or equipment renovation?
So you have 2 pumps?
.85 and 1.65? What is 1.65 for?
For new construction, our skimmers are minimum 2.5" and the main drain is always 3".
I would have used 2" on everything coming up and all of the manifold.The 1.5" creates restriction and reduces flow on both suction and return.
The 3 suctions collectively running on an equivalent 3/4 HP pump will work ok. The moment a skimmer is isolated to manually vacuum, the pump will starve for water.
I would have arranged the equipment to reduce the 90's and bump size up to 2", especially coming into the suction, to reduce friction loss.I don't use ball valves a shown, as the actual ball opening inside is so small, which reduces flow.
Pet peeve for us. No blue glue at the equipment. We always use clear.
yeager