| I need to design plumbing that will go behind cabinets for a plumbed steam oven, which I dot not have yet and will nto have during cabinets' installation (I hope to purchase the combi oven from Miele that is suppose to come to US market next year so I have no instructions for it yet). I looked into the instructions from UK and the ones for Gaggenau combi oven, but I have the following questions:
Do I need to have a P-trap on the waste line or may I use a waterless trap ? Can I simply drain it into my basement laundry sink similarly as my washing machine drains into it? If so, what is the longest run such drainage arangement can have (I need ~ 20 feet to get to the sink). I am in Connecticut. |
Here is a link that might be useful: waterless trap
Follow-Up Postings:
|
- Posted by lazypup (lazypup@yahoo.com) on Sun, Dec 4, 11 at 8:57
| The discharge line from a steam oven MAY NOT be directly connected to the DWV piping. The oven is required to have an Indirect Waste, which means the line must drain into a sink or floor drain, and the lowest portion of the drain line from the oven Must Be a minumum of 2" above the flood level rim of the recepter. And there shall be no trap on the discharge line from the oven. |
|
| thank you- is there a limit on the length of the pipe that runs from the oven before the airgap? The waste line from the oven itself is 10 feet, but I need >20 feet to drain straight to laundry sink in the basement. |
|
- Posted by lazypup (lazypup@yahoo.com) on Sun, Dec 4, 11 at 17:52
| I am not aware of any limit, providing that all the horizontal run is pitched with a 1/4" per ft pitch however, you will have to use copper or iron pipe to make the line because the discharge temp of the water from the oven exceeds the maximum temperature rating for PVC or ABS |
|
| thank you so much.... |
|
| "Do I need to have a P-trap on the waste line or may I use a waterless trap ? " Items listed for use in "RV's and boats" are not typically allowed in houses under the plumbing code. Valve type devices have a nasty habit of failing to close when debris builds up on them, even soap scum. Use in foreign countries is not a good indicator. |
|
| Will iron be less expensive than copper? I was told copper only, but I am guessing it may cost me a fortune to run 24 ft copper at 1.5 inch drain. Any idea what is the cost I am looking at? |
|
| I have gotten more info (once I looked up pricing for copper pipes I got desperate and called Miele in Germany). The water will be discharged at 70 Celsius, (which is 158 F)- can this go into a plastic drain pipe? If yes, which one exactly: ABS or PVC? The more detailed manual I finally gotten today states: Water hose data When laying the water pipes in ducting, we recommend a Connecting the drainage hose: Am I reading this correctly that I need a 2 inch plastic drain pipe to connect to a waste hose of the appliance? US code stipulates indirect drain for steam oven, which I can accomplish, but 24 ft of copper? Do I really need copper? |
|
- Posted by jakethewonderdog (My Page) on Tue, Dec 13, 11 at 8:16
| The max temp for PVC is 140 F. The max temp for CPVC is 200 F - but CPVC isn't normally used for DWV applications. Lazypup, what would code say about using CPVC for a drain in this application? Are there CPVC DWV fittings available? |
|
| as a side question: my cloth washing machine uses water at ~158F (70 C) when I run sanitary cycle (with the heater from the washer additionally heating the "hot" water suppplied) - would that be problematic with the black drains that I have installed in the laundry room as well? |
|
- Posted by lazypup (lazypup@yahoo.com) on Tue, Dec 13, 11 at 9:49
| CPVC is not approved for DWV and the maximum working temp for PVC is 73degF |
|
- Posted by jakethewonderdog (My Page) on Tue, Dec 13, 11 at 10:49
| I should know better than to question Lazypup... but it looks to me that the rating for PVC is at 73 deg F while the max service temp is 140. Anything above 73 deg and the pipe has to be de-rated for pressure and spans between supports. efs, I think the answer to your question is this: If it's unlikely to be thoroughly inspected, do it in PVC. It's going to work fine, but if the inspector really digs into the job, he could raise a red flag. CPVC is sometimes used in lab drains to handle corrosive chemicals. There are DWV fittings available, but are very limited in supply and are hard to get. Even so, an inspector probably wouldn't approve it. |
|
- Posted by lazypup (lazypup@yahoo.com) on Tue, Dec 13, 11 at 11:39
| I will agree that 2" types K,L or even M copper could prove rather expensive, but if you use thinwall DWV grade copper it should prove affordable. I doubt that you will find thinwall DWV copper in a homesupply such as Lowes or HD, but if you contact a commercial plumbing supply or if you talk to the proprietor at your local ACE or True Value hardware stores they can get if for you, and although it is more than PVC, it is still affordable. |
|
| thanks. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Plumbing Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.