proper pitch for drain pipe under floor?

Posted by Ruddydog52 (My Page) on
Thu, Nov 17, 11 at 19:53

Hello, I will be installing a washer and dryer in my upstairs closet that backs up to a bathroom. I need to run the drainage pipe from the washer under the floor (7 feet) to the stack. I don't no the formula for figuring the right amount of pitch for the pipe per foot.
Does anyone know how I figure this out? Also I want to use those new flexible water lines instead of copper does anyone have any pro or cons on them? They would be a lot easier to snake through the walls.

Thanks for reading my post
Ruddy


Follow-Up Postings:

 o
RE: proper pitch for drain pipe under floor?

The washer drain must be 2" trade size minimum. Pitch for the "horizontal" portion is 1/4" per foot minimum. For 7', it is 1 3/4".


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here