Minimizing hot water wait time - PEX home run or trunk and branch

Posted by stitz_crew (My Page) on
Sun, Nov 25, 12 at 17:10

I have a few quesitons on a new build using Pex.

Is there a reason to run an HR system for cold lines if there is no concern on waiting for hot water? My thoughts are that a trunk and branch system seems the most practical.

I planned on using an HR system for hot supply using 1/2" for most areas. One area that I am concerned with is the master bath that will require roughly 50' of piping runs to most fixtures. From reading it seems that a 1/2" pex line will hold around .46 gallons at 50'. This seems that it would still take a decent amount of time to clear the cold water. Although this is not as wastefull as a 3/4" trunk line it is more of a concern on wait time.

Here is what I thought as a solution to this problem of waiting on hot water. I was looking at having a 2nd 10-20 gallon electric water heater in my closet (not wifes) adjacent to the shower. I would have it drained under the bench seat in shower (out of sight). If I run a 3/4" hot supply into the cold end of WH the room temp water in the line is mixed into the 2nd WH which is set slightly hotter than main to adjust for room temp water. The hot end of WH would then run to a manifold where 1/2" pex lines are run to each fixture in master bath. This would cut the runs to ~6'-15' compared to 50'. The 2nd WH would not use as much electricity b/c it is always fed by a hot line (room temp at worse). I feel this is a better solution than a re-circ system b/c the master bath is the only place where hot water use is most important.

The rest of the homes hot water supply would be run on 1/2" HR where lengths are considerbly less than master bath. I was thinking of a 66 gal main WH with a 20 gal 2nd giving plenty of hot water for us and guests.

So it seems that my thoughts are using Trunk and Branch for cold supply, HR for most hot supply and remote manifold (off 2nd WH for master bath).

Hopefully some of you can make sense of this and provide some input in a kind manner. I attached picture if that helps of master bath. Thanks


Follow-Up Postings:

 o
RE: Minimizing hot water wait time - PEX home run or trunk and br

Since your closet is right there on the exterior, why not put in a direct vent gas tankless? You can have endless hot water fairly rapidly and takes up half the space. Yes, it's more money than what you propose, but you needn't worry about a tank having a leak in your closet, nor ever running out of hot water for your tub or shower. I have a friend with a long ranch house, and there's a small BTU tankless at the kitchen end, and a larger BTU one at the bath end. It works very well.


 o
RE: Minimizing hot water wait time - PEX home run or trunk and br

I doubt very seriously if your plumbing inspector will allow you to discharge the water heater TPRV into the shower pan. If someone happened to be in the shower when the valve opened their feet would be scalded.

That water heater is on an outside wall. The preferred method would be to discharge both the TPRV & the pan outdoors through the wall.

Also, you are just arbitrarially assuming 1/2" is the correct size of the PEX lines, that is not correct.

I strongly suggest you download the free PDF Zurn PEX Installation guide.

http://0323c7c.netsolhost.com/docs/PEXDesApplGuide.pdf


 o
RE: Minimizing hot water wait time - PEX home run or trunk and br

Makes sense on the drain line. Draining to the exterior would be better. I was also was looking at doing a remote manifold at the vanity wall and attaching a Recirc pump with a seperate return line to free up closet space and just upsize main WH. I would rather have to fastest hot water response to the vanity faucets for washing hands. I would run the proper pex sizing as required by fixture. Thanks for the help.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here