Current water heater installed before current code, now what?

TxMarti
11 years ago

The water heater is in the middle of the house. Slab foundation and water heater on floor. Current code requires it be off the floor, in a pan, with pipe to drain or outside. There is nothing wrong with our water heater, but we are replacing the tile and I thought it would be good to replace the water heater at the same time since it has to be removed from the closet it is in. But if we did, we have to bring it up to code. How on earth would we get it piped outside?

Comments (7)

  • lazypup
    11 years ago

    Need more information...

    Is it in a bathroom or a utility room?

    Gas or Electric?

  • TxMarti
    Original Author
    11 years ago

    Gas, it's in it's own little closet off the kitchen.

  • brickeyee
    11 years ago

    If you do not alter it grandfathering applies.

  • TxMarti
    Original Author
    11 years ago

    The water heater is 9 years old and the 2nd one we've replaced in the last 15 years. Our water used to be really hard and was notorious for killing appliances, but they switched from well to lake water about 8 years ago and our co-op built a new treatment plant a few years ago so I assume it's just like any other foul smelling water now.

    I don't know how long a water heater is supposed to last. I didn't even know we were supposed to drain it every year until the man at Lowe's told me. He's also the one who told me everything had to be brought up to code if we replaced it.

    If that is true, now would be the time to do it if it requires tearing off sheetrock to run a pipe outside. Easier for us than a neighbor who doesn't have a straight line of walls leading to an outside wall, but still a pain.

    I'm even wondering if it would be better to put in tankless if we have to make a lot of changes.

  • ionized_gw
    11 years ago

    Be sure to install a good quality valve on the new tank. The ones that are included are a pain if you flush them like you should.

    This is a good site if you want to learn about water heaters:

    http://www.waterheaterrescue.com

  • TxMarti
    Original Author
    11 years ago

    Oh & I decided against tankless. I need it to work even when the electricity is off.

  • lazypup
    11 years ago

    The next question is what kind of tile? If the water heater is installed in an attic or over a wood floor you are required to have a pan with a 3/4" diameter drain line to an approved indirect waste receptor or outdoors in a conspicuous place.

    If it is installed over a floor that is not subject to water damage, such as concrete or ceramic tile it does not require a pan.

    All water heaters are also required to have a TPRV (Temperature & pressure relief valve) with a full bore drain line to an approved indirect waste receptor or outdoors EXCEPT: in instances where a gravity flow drain line cannot be achieved, such as below grade in a basement, the TPRV may be removed and if it is a gas water heater a "Watts 210 gas valve" is installed, then the gas supply line is run to the Waats 210 gas valve, then to the water heater gas control. In this manner if the temperature in the tank exceeds 210degF or if the pressure exceeds 150psi the Watts 210 gas valve closes and shuts off the gas supply to the burner.

    When a Watts 210 gas valve is installed you must also go to any convenient location in the structure and install a Pressure Relief Valve on the hot water system where the Pressure Relief Valve can be drained to an approved indirect waste receptor or outdoors.

    In the case of an electric water heater you only need the pressure relief valve because the upper thermostat in an electric water heater has the required thermal shutdown function.