Plumbing softener drain line to sewer clean out

bigsmooth469
14 years ago

Hi All,

Just curious is this is an acceptable practice? I have a plumber who wants to run a drain line out of my garage into the sewer clean out, says it will require a new P-trap. Is it better to go directly to the drain or will the clean out be just fine? I figure since the clean out is hooked up to the sewer, it's the same thing, right?

Thoughts or comments would be appreciated.

Comments (10)

  • lazypup
    14 years ago

    You cannot hamper the function of the clean out, however you may install a Sanitary Tee and put the clean out cap on the top of the Tee, then connect your new drain line into the side opening of the Tee.

    Also, you cannot directly connect the water softener drain line to the DWV system. The water softener drain line requires an "indirect waste" connection, which means you could either install a sink with a trap that connects to that tee, then discharge the water softener drain into the sink, or you can install a standpipe with a trap in the same manner as a washing machine standpipe and discharge the water softener drain into the standpipe.

  • bigsmooth469
    Original Author
    14 years ago

    lazypup, understand your first statement which is he can tie into the clean out by going undeneath the exposed area...he would dig and T into the white pipe coming up from the ground and not alter the cap.

    Don't understand the second paragraph though, the clean out goes to the drain, if he plumbs the p-trap into the bottom part of the clean out, it would empty into the sewer right?

    Sorry, I'm obviously not up on my plumbing lingo! :)

  • manhattan42
    14 years ago

    You can drain the softener to the cleanout provided:

    1. The softener drains to a trap
    2. The softener drains to the trap by way of an "air gap"
    3. The trap is connected so that the connection can still be used as a 'cleanout'.

  • bigsmooth469
    Original Author
    14 years ago

    Well, the work is done, now that I saw what they did and how they did it I kind of wish I would have tried it myself but it would have likely taken me twice as long, so oh well, live and learn.

    They did exactly what's described by manhattan42, works great.

  • User
    9 years ago

    That is not according to code. If that standpipe backs up there will be cross contamination between the sewer line and the softener. In many locales softener installs must be done by a licensed plumber. Is you installer a licensed plumber? I ask because he obviously does not know what an air gap to drain is

    The softener drain line must have an air gap to the drain. The way it is configured, If he had simply run the drain line up a couple inches then 90's it and 90'd it again so the line was in fee air above the standpipe he'd have had an air gap.

    Call him back and make him do it according to code or make him buy a nifty air gap from www.airgap.com.

  • kuomatt
    9 years ago

    Thanks, justalurker. The installer is from one of the big water softener companies. I will ask them to correct it.

  • User
    9 years ago

    If they give you the rope-a-dope and say "that's how we do it all the time" tell them you'll call the plumbing inspectors and have them take a look. Then they'll correct it cause the plumbing inspectors will look to see if they pulled a permit and they didn't cause there was no inspection.

  • cntl4userguy
    9 years ago

    The other problem with that install is that you have eliminated the cleanout port.

  • cntl4userguy
    9 years ago

    is that a 3/4 against a 2in? If so, OK.