| We are clearing a lot for a home and need to run a water supply line from the meter to the house. The approximate distance is 1000 feet. There is good water preassure in the area thanks to a water tower close by. I am going to use PVC, and was thinking 1" would be ok, but was told by a friend to use 1 1/4". Whats the best way to do this? It is a 2 bathroom 2400 square foot home, nothing major for usage, just normal appliances and bathroom uses. There is not much elevation change, maybe a rise of 4' at the most from the meter to the house. We are in South Carolina and i am not sure where the frost line is, but i am sure i can find out locally before hand. Thanks for any help. |
Follow-Up Postings:
|
| Use flexible line that has no joints of whatever type the AHJ will allow. |
|
| I agree with Brickeyee on the flexible line. You might be able to get it in 500' rolls. There will probably be a choice on stregnth of the line and I would spring for the heaviest. And you should find the frost line and what the local code is on burial depth so that you don't get a freeze up. |
|
- Posted by lazypup (lazypup@yahoo.com) on Wed, Sep 28, 11 at 1:03
| For single family residential service code requires that the water supply line must be sized to supply 100% total fixture load, where the fixture load is determined by the code table for individual fixture demands. Individual fixture demands per code table: BATH = WC 3, tub/shwr 4 & lav 2 = 9gpm x2 = 18gpm Kitchen- Sink 2.5 & DW 2.75 = 5.25gpm Laundry 4gpm Hose Bibb 5gpm TOTAL 32.25gpm ( round to 30gpm) In a 1" plastic pipe the friction head loss is 0.2869psi/ft and the run is 1000ft for a total friction head loss of 286psi loss. at 1-1/4 the friction head loss is 0.0702psi/ft x 1000ft = 70psi loss. At 1-1/2 the friction head loss is 0.0322psi/ft x 1000ft = 32psi loss. For a 1000ft run the preferred size would be 2" pipe which would yield a friction head loss of 0.92psi/ft x 1000ft = a loss of 9psi below the static head pressure at the meter. (Loss based up using PE plastic pipe) |
|
- Posted by weedmeister (My Page) on Thu, Sep 29, 11 at 15:25
| Have you thought about yard watering? Would you ever want to put in a sprinkler system? |
|
- Posted by bus_driver (My Page) on Thu, Sep 29, 11 at 21:32
| The pressure losses shown by lazypup are at the calculated flow of 32.25 gpm. At lower flow rates, the pressure loss is lower. I suspect that the flow rate of 32.25 gpm will be seen very rarely in your situation. |
|
- Posted by lazypup (lazypup@yahoo.com) on Fri, Sep 30, 11 at 0:08
| It doesn't matter if it never sees that peak load, code requires the line to be sized to max and in most jurisdictions you can not even pull a permit until you do the math. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Plumbing Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.