I have a question on plumbing code - we live in California so I don't know if there are any unique requirements here. We are remodeling our kitchen and the sink has a 1 1/2" trap drain. In the plumbing of the trap drain, there are currently 2-45 deg turns between the trap and vent stack. By adding an one more 45 deg turn we can eliminate the need to go through the back of 2 cabinets. The plumber has said that it violates code to have 3-45 deg turns in a trap drain. I can't really find any code that mentions so I'd like to get any pointers here. Thanks,
|
Follow-Up Postings:
|
| Terms that may help you web search: "trap arm" "cumulative change in direction" "developed length" "fall of trap arm" By adding another bend, you will have lengthened the "trap arm". This is part of the problem. There is also a maximum "fall of trap arm" to consider. It may still be possible to have three 45-degree bends, but it will depend on all these factors. |
|
- Posted by lazypup (lazypup@yahoo.com) on Wed, Jun 9, 10 at 10:17
| There is another issue that you have not considered. The California plumbing code uses the same DWV line sizing as the UPC and under the UPC 1-1/2" line is limited to 1dfu while a kitchen sink is rated at 3dfu's. If you maintain the line in the exact same configuration as it was when the structure was built your work falls under the heading of "Maintenance" and you may continue to use 1-1/2", but if you alter the configuration in any manner it is defined as "New Work" and you would be required to meet the current code therefore the line would have to be increased from 1-1/2" to 2". |
|
| Uh-oh. 2 DFU 1 DFU If I'm right about this, then the post by lazypup above has two simple factual errors. I did a little web searching and found an IAPMO.org document comparing IPC and UPC. Here: The pipe size and DFU values are for both IPC and UPC type Plumbing Codes |
|
- Posted by lazypup (lazypup@yahoo.com) on Wed, Jun 9, 10 at 14:32
| Check your code again,,, Table UPC T7-5 1-1/2" pipe is rated t 2dfu on a vertical run but only 1 dfu on a horizontal run. There is also an exception on the vertical listing that says,,"no sinks, urinals or dishwashers- two lavs is okay)" |
|
| Millions of kitchens have 1.5" pipe up to the P trap. Millions more new kitchens too. We need at least one more plumber in this forum. Here we have in the above post a plumber implying that kitchens require 2" pipe everywhere. A sink strainer produces a 1.5" hole, which takes a 1.5" pipe, which goes into a 1.5" P trap. Pipe size increases to 2"after the Ptrap. |
|
| "Millions of kitchens have 1.5" pipe up to the P trap. Millions more new kitchens too. We need at least one more plumber in this forum. Here we have in the above post a plumber implying that kitchens require 2" pipe everywhere. " And millions of washing machine stand pipes are 1.5 inches. The code now requires 2 inch. The 1.5 inch lines had flow problems, and overflowed occasionally. The only thing we have to work against here is (for the most part) the present codes in effect. Yes, you can usually repair with 'like size' and continue on under the 'grandfather rules.' Everyone knows it would be impossible to tear up every house every time the code is changed. When you remodel the AHJ usually asserts their authority and requires you to alter things to the most recent code. A remodel is viewed as 'new work' by the AHJ, and he uses the code in effect when the remodel is performed, not the code in effect when the house was built or previously remodeled. |
|
| Online: UPC Table 7-3 lists the trap size for different fixtures 1.5" for kitchen sink UPC Table 7-5 lists the DFU capacity for horizontal/vertical DWV 1.5" has 1 DFU capacity horizontal and 2 DFU vertical UPC Table 7-5 excludes the trap arm (section from trap to vent). The trap arm is the same size as the p-trap (1.5" in this case). So, under UPC a kitchen sink can use 1.5" all the way to the vent. After the trap arm = not relevant to the OP's question. Typically, there is a santee and the flow goes downward at the point where the trap arm ends, so that could also be 1.5", under UPC, but my writing that out is not a recommendation to do this. But a kitchen sink is 2 DFU, not 3. -- Hope this helps. -- Did something change while I was away on vacation last month? |
|
- Posted by lazypup (lazypup@yahoo.com) on Thu, Jun 10, 10 at 18:01
| We need at least one more plumber in this forum. Here we have in the above post a plumber implying that kitchens require 2" pipe everywhere THAT STATEMENT IS A BALD FACED LIE PERPETRATED BY ONE WHO IS NOT A PLUMBER, YET WOULD LIKE US TO ACCEPT HIS EXPERTISE ON THE MATTER. Nowhere did I say that all kitchens sink waste arms have to be 2". My answer was in direct response to the original post in which they stated they were in California, and the California code is based on the UPC, which does require 2". Under the IRC it only requires 1-1/2" |
|
| No, sir. Plumbers can make mistakes. You can, just as I can. Don't say I'm lying. Plumbers can also disagree amongst themselves on how to implement, in spite of the fact that Code appears to be clear. Lazypup, you made mistakes, and now you have avoided dealing with them in your post above. Hmm. I've seen this before. You are good, in many ways. You avoid dealing with new information that contradicts your initial stance. This is not helpful to the OP. Check and re-check the information that I have looked up. |
|
- Posted by lazypup (lazypup@yahoo.com) on Thu, Jun 10, 10 at 19:40
| You keep implying that I made a mistake in my post above,,which is not true. |
|
- Posted by manhattan42 (My Page) on Thu, Jun 10, 10 at 21:38
| jsjames asked: 'We are remodeling our kitchen and the sink has a 1 1/2' trap drain. In the plumbing of the trap drain, there are currently 2-45 deg turns between the trap and vent stack. By adding an one more 45 deg turn we can eliminate the need to go through the back of 2 cabinets. The plumber has said that it violates code to have 3-45 deg turns in a trap drain. I can't really find any code that mentions so I'd like to get any pointers here.' I can find no specific code in the California UPC (see link below) that prohibits offsets in horizontal wastes or trap arms, but you do not mention what direction these 45s turn. Are they 45 degree horizontal offsets? (That is, side-to-side but still keeping the trap arm going in a generally horizontal manner.) Or are they 45 degree vertical offsets? (That is up-or-down causing the pipe to go in a generally downhill vertical manner.) It could make a BIG difference because if they are vertical offsets, you could be creating an 'S-Trap' of sorts, which would be prohibited under the California UPC and most any other plumbing code. |
Here is a link that might be useful: 2007 California UPC
|
| jsjames: I have read often that up to 135 degrees in total bends is OK. I gave you key words to search on instead of trying to answer the question directly. -- The second response you received said you needed to upsize to a 2" pipe. A trap arm can be 1.5" all the way to the vent.
Thank you to manhattan42 for posting California code: -- Table 7-3 says "Min. Size Trap and Trap Arm" in the column header The maximum length of a trap arm is not governed by this table 7-3. Table 7-5 says maximums I am disappointed that a serious contributor made a major mistake and then couldn't admit it. Every house has a kitchen. Many people will let the "main man" have his way... but I'm also disappointed in brickeyee for acting as a bully-follower (posting as if to confirm that 2" pipe is now required). We REALLY need to have more than one main person in this plumbing forum. hope this helps the forum and every one of its contributors. |
|
- Posted by lazypup (lazypup@yahoo.com) on Fri, Jun 11, 10 at 14:47
| You are absoutely correct, I made a mistake when i stated the kitchen sink was 3dfu instead of two, however under the UPC and 1-1/2" line is limited to a maximum of 1 (one) DFU. Correct me if I am wrong, but it is my understanding that 2 is greater than 1, therefore it would not matter if i had said 100, the fact remains that a kitchen sink exceeds the maximum allowable load on a 1-1/2" drain line under the current code restrictions. The point that I made in my original post was that if they maintain the drain in the exact same configuration as it was originally installed they could continue to use 1-1/2" BUT IF THEY ALTER THE CONFIGURATION that constitutes new work and they would then be required to install the drain under the code that is in effect at the time of the alteration. Davidro then argued that the UPC still permits 1-1/2" drain lines for a kitchen sink and he included a website that has a table comparing the IPC & UPC. He argued that the table lists the trap and tailpiece as 1-1/2", then he went on to say that the "tailpiece" includes all pipe from the trap to the vent, which is not correct. When using a tubular preformed trap the trap tailpiece is the short section of straight tubing on the downstream side of the trap weir which is an integral part of the trap fitting. The trap adapter is the official point of demarcation between the tubular trap fitting and the pipe drain line. A fixture arm or waste arm is any and all piping on the upstream side of the vent opening to the trap weir. That includes both the drain line and the trap tailpiece. (See attached drawing) He then posted a link to a website that compares the IPC to the UPC and he argued that is says the proper size of the drain for a kitchen sink is 1-1/2" Let us now examine precisely what his reference says: QUOTE: If you then read the next sentence under the table it says; 7-14. The IPC and UPC both require 1-1/2" minimum traps on kitchen sinks. The IPC permits a 1-1/2" branch drain. However, the UPC requires a 2" drain beyond the trap on any sink, as there may be food waste now or in the future. DOES IT NOT CLEARLY SAY THE UPC REQUIRES A 2" DRAIN BEYOND THE TRAP??? |
|
| We have established that lazypup can make a mistake, and he has admitted it himself, so now let us make more progress. I am extremely disappointed that a supposedly practicing plumber doesn't know that a sink is only 2 DFU's I am extremely disappointed that lazypup has gone web searching to only one of the referenced documents, the IAPMO one. Forget it. Move on to the real Code. There is nothing to gain by parsing my words or theirs, if you have the pertinent Code in front of your eyes. I think the big question here is to know that trap "arms" can be 1.5" in diameter under the UPC-based California code. Duh. Comment on that one. Be aware that other Master Plumbers have said what I wrote above is correct. He went and defined the beginnings of DWV as the point where the "tubular" stuff stops. I'm almost willing to call this a dead horse now. |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Plumbing Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.