Shower drain - reduce 2 inch to 1 1/2 inch and venting

Posted by turnerover32 (My Page) on
Sat, Jun 20, 09 at 15:28

Hi

I have a few questions about replacing an existing bathtub with a shower as we remodel our bathroom,

The existing tub on our upper floor was plumbed with a 1.5 inch p-trap and then a horizontal run of about 9 feet before it heads vertically downwards towards the basement between all the walls. My understanding is that code calls for 2 inch drain pipe for a shower. My question is somewhere along the line (I can rip up the subfloor) I need to transition form the new 2 inch drain to the 1.5 inch line and what would be the best place to place this reducer to minimize the speed at which water can flow. It could be right at point the drain meets the the p-trap where I could reduce to 1.5 inch p-trap or I could put in a 2 inch p-trap and 2 inch line and then transition at the point the horizontal drain line connects to the 1.5 inch vertical drain line between the walls headed to the basement. I am thinking the second option would be better?

My second question I son venting- the existing tub never drained very fast. The current vent is about 52 inches form the existing p-trap. I have looked at code on the web and it varies by jurisdiction with it being with 5 feet in some and within 3.5 feet. My question is if I move the vent closer than the existing 52 inches could I increase the rate at which the water drains. If I actually left the first vent in place and added a second vent that was closer could this cause a problem?

Any advice would be appreciated


Follow-Up Postings:

 o
RE: Shower drain - reduce 2 inch to 1 1/2 inch and venting

Code prohibits decreasing the size of a line in the direction of flow. (Common sense should explain why).

If you pull the tub and replace it with a shower you will be required to make the entire run of the drain line with 2" until it connects to a larger line.

Under the IRC a 1-1/2" line requires a vent within 6' of the trap, while under the UPC they only allow 3'6" from trap weir to vent opening.

For a 2" line the IRC allows 8' while the UPC only allows 5', however according to your profile you are in Canada and I do not have the Canadian Plumbing code so you will have to find out what your local code requires. Generally you can call the code inspection office, any local plumber or perhaps the reference desk at your local library to find out what your requirements are.

All vents must rise vertically until they reach an elevation at least 6" higher than the flood level rim of the highest fixture served by that vent.


 o
RE: Shower drain - reduce 2 inch to 1 1/2 inch and venting

afaik. each province has its own code, and they all allow 1.5" drains. Everyone says so, but I've never seen it in writing. Check with a Master Plumber. Any Master Plumber. They are professionals who do not lie. They know 100% for certain what is required and they tell you the truth, when it concerns their expertise; also you do not have to hire them first before they answer questions about their area of expertise. Each Master Plumber will give you the same answer as the previous one and the next one.

Ditto, do not decrease any "drain line in the direction of flow." The trap size has to be the same as the drain size. Many people conclude that a 2" trap can be reduced to a 1.5." pipe after the trap. Use a 1.5" trap if the drain line is to going to be 1.5" diameter. This is very serious, not to be disregarded. Ask a Master Plumber if you need to hear it again.

You may wonder why you see on the internet that showers need 2" ...
I feel that this forum is the right place for this discussion.

It find the 2" diameter requirement for showers to be overkill.

I'm surprised that after many years of searching, I've never seen an internet comment from an experienced Master Plumber telling me how Code changed over the years.

I'm 100% certain that a 1.5" drain line used to be Code everywhere, for showers. I'd like to know what discussion went into voting for the new size, 2" diameter.

(?)
Here is a link showing 1.5" is OK in NY.
http://publicecodes.citation.com/st/ny/st/b900v07/st_ny_st_b900v07_7_sec009.htm

Code has changed over the years and will continue to change in the future.
I'd like to think I'm helping to air out the issues which leads later to clearing up confusion about 2" shower drains.

Imagine all the people who have been forced to do a lot of extra work for no reason !! When a 1.5" drain already plumbed could have been used, they ripped it all out and put a 2" drain in.

I'm not a plumber. Since this is a discussion forum, I'm posting this here as part of a *discussion*; everything I have written here concurs with the previous post from an expert who knows, and who shares, precisely what is code today. Code has changed over the years and will continue to change in the future.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here