leak problem with threaded connections

Posted by homebound (My Page) on
Tue, Jun 5, 12 at 9:03

In a shower rough-in, I'm testing and getting drips at some threaded connections that I can't seem to solve.

I'm using 3/4 CPVC male adaptors into the volume control valves (Rohl), along with Rectorseal T plus 2 (I also tried 4 or 5 wraps of teflon tape). I've tried both the fully CPVC ones, and the ones that are brass/cpvc combo. I am cranking them in there nice and tight with two wrenches, then gluing it all together...and wham...another @$#% drip. Any idea what I'm doing wrong here? Thanks much.


Follow-Up Postings:

 o
RE: leak problem with threaded connections

Your putting the thread adapters in "Nice & tight" but not nice & tight enough...LOL.

Crank them ondown a bit more....when MIP thread fitting is made up correctly there should be no more than 1 thread still visible.


 o
RE: leak problem with threaded connections

Thanks for the advice.

BTW, this last time I really cranked them...almost to the point I was afraid I might crack the valve. I'm going over to water test today - hopefully finally got it.

Also, there are a total of 8 of these connections in this bathroom. First, 3 were leaking, then 1, so maybe I'm ok. But should I disassemble the other 5 and crank them down just in case? The others were holding, but I don't want a bad surprise two weeks later.


 o
RE: leak problem with threaded connections

Wow, didn't realize threaded connections were that difficult.


 o
RE: leak problem with threaded connections

"Wow, didn't realize threaded connections were that difficult."

They are not with the correct pipe dope and decent size wrenches.


 o
RE: leak problem with threaded connections

Brickeye,,,you are absolutely correct,,"They are not with the correct pipe dope and decent size wrenches."

The problem is, most homeowners & DIY'ers have never seen descent size pipe wrenches. Most of them are struggling along with 14", 16" & maybe 18" el cheapo wrenches made in China when in fact, for working 3/4" pipe they should be using an 18" to steady the pipe and another 18" or 24" to turn the fitting or vice versa.

I love to see ppls reaction when we are tearing out old 4" and we resort to the 48" or 60" pipe wrenches. Most ppl have never seen a pipe wrench that is 5ft long and they surely would not want to see the price tag... 60"iron frame is $315 and a 48" aluminum frame is $347.


 o
RE: leak problem with threaded connections

I have used my pair of 60 inch Stillson brand just enough times over the years in renovation work to be glad I inherited them from my Grandfather.

They are steel and are indeed a real handful.

I even have spare jaws.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here