Will all of this run on one 3/4" natural gas line?

Posted by wynswrld98 (My Page) on
Fri, Apr 5, 13 at 22:02

I'm getting different opinions from plumbing contractors I'm getting quotes on to replace my old electric water heater with a gas tankless re: if a new line needs to be run from the gas meter to the new tankless (85' run) or if the whole house can run off the 3/4" line which is already running right next to the electric water heater.

Here's what I have:
Gas Furnace: 154,000 BTU
Gas Fireplace Insert: 40,000 BTU
Existing Gas Tankless Water Heater: 199,900 BTU
Additional Gas Tankless Water Heater to replace electic water heater: 199,900 BTU
Gas Clothes Dryer - ? BTU
Gas Cooking Stove/Oven - ? BTU

I already have e-mailed my gas company the same specs above for them to verify the meter is sized appropriately to handle the load but my question remains re: how do I figure out which contractor is correct re: if the one 3/4" line can handle all of this?

Thanks!


Follow-Up Postings:

 o
RE: Will all of this run on one 3/4" natural gas line?

P.S. the 3/4" gas line is all iron, not the yellow flex line.


 o
RE: Will all of this run on one 3/4" natural gas line?

592,900 BTUs identified, with more to be added?

I do not have a gas table handy but that sounds like way to much for a single 3/4 inch line.


 o
RE: Will all of this run on one 3/4" natural gas line?

No more being added, that was the complete list. Ofcourse not all of that would be running simultaneous. I don't know the BTUs for the gas dryer and stove/oven as they are older but was able to find out the exact BTUs for the rest.


 o
RE: Will all of this run on one 3/4" natural gas line?

The nameplate for the appliances should have their BTU marked.


 o
RE: Will all of this run on one 3/4" natural gas line?

Gas Dryer: 22,000 BTU
Stove/Oven: 67,000 BTU

I just looked at the gas piping and the existing tankless water heater is piped such that the line that goes to it splits right at the meter into it (which is on other side of wall from meter) so essentially of the list above everything would be on the one 3/4" gas line running in the house except for the existing tankless water heater.


 o
RE: Will all of this run on one 3/4" natural gas line?

A short length right after the meter should not be as much of an issue as a long run of only 3/4 inch.


 o
RE: Will all of this run on one 3/4" natural gas line?

Right, that is why I brought it up since it should be considered


 o
RE: Will all of this run on one 3/4" natural gas line?

bump. Any experts out there? If so, thanks in advance!


 o
RE: Will all of this run on one 3/4" natural gas line?

I've been talking to the natural gas company to find out if my existing gas meter is large enough to deal with everything I have planned for it and the response was that it needs to be upgraded. However, they want to charge me $1325 to upgrade the meter. Major OUCH!

I asked what the BTUs are for the existing meter so I could gauge how much of what I have it supports and the response I got was 300,000 CFH. I did some Googling of converting CFH to BTUs and didn't understand the responses.

Anyone know how to convert the 300,000 CFH figure the gas company gave me to see how many BTUs it will cover (from my list of BTUs above)?

If I have to shell out $1325 to the gas company I'd guess switching the electric water heater to tankless is a "no go" based on way too expensive with tacking on the meter upgrade, just would make more sense to keep an electric water heater, I don't like it but it's hard to justify massive amounts of $$ to go tankless. But if my meter is close enough (the reality is only two people live in the house, all of the above things would not be running simultaneous) then perhaps it is a go and I skip the gas meter upgrade.0

Thanks!


 o
RE: Will all of this run on one 3/4" natural gas line?

1 cubic ft of natural gas is approximately 1000 BTU


 o
RE: Will all of this run on one 3/4" natural gas line?

So when I total up all of my BTUs it's 682,800. So how do I relate that to 300,000 CFH my current meter is able of providing? I'm guessing the 'H" in CFH is 'hour' meaning 300,000 cubic feet per hour but BTUs are stated per an instant in time so do I need to do some conversion of time here too to figure this out since CFH is apparently per hour but BTUs are per second or some such?

I'm completely new to all of this so I appreciate your patience but we're talking $1325 just to upgrade the meter and I'm trying to figure out how much of the BTUs the current meter is capable of handling.

Thanks again!


 o
RE: Will all of this run on one 3/4" natural gas line?

This is a quote from the gas company when I asked how CFH and BTU relate to each other, is what she saying correct?:

CFH is cubic feet p/hour & BTU's are british thermal units, same difference. The capacity of the 630 meter that would replace your meter is good to 1.2 million cubic ft p/hr.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here