Recommended Vent pipe slope

Posted by sunroomguy (My Page) on
Sun, Apr 10, 11 at 21:01

i have 3- 2" PVC lines stubbed up in the attic that i need to tie together for the plumbing vent. i know i have to increase to 3" when pentrating the roof. what is the minimum reguires slope? is there a maximun distance? i have one 40' from the other 2 with plenty of truss height.i prefer to have one stack instead of two. thanx


Follow-Up Postings:

 o
RE: Recommended Vent pipe slope

What is vented by those two (assumed to be new) 2" vents?


 o
RE: Recommended Vent pipe slope

The vent must be sloped at a minimum of 1/4" per foot down from the roof vent to the vertical riser in the house.

Under the IRC you have to increase the entire vent one nominal trade size if the total developed length of the vent exceeds 40'

Under the UPC you have to increase the entire vent one nominal pipe size if the horizontal offset exceeds 3'.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here