| Hello, I'm in the planning process of removing my Tub's Drum Trap and replacing it with a proper P-Trap and an Air Admittance Valve.
The tub is plumbed as follows in PVC: 1-1/2" Trap Adapter, Drum Trap with Cleanout, 4 feet of 1-1/2" PVC (slope = 1/2" per ft), 90 degree elbow to go vertical, 1' of 1-1/2" pipe, tee from lavitory drain, 5' 1-1/2" pipe into a 3" sanitary tee at the main drain. The closest place to put the vent line would be right after the P-trap, with a wye, going backwards at an angle, and up into the wall cavity behind the tub, which is accessable from a closet. I could also put the vent at the top of the vertical drain from the tub, but I don't have much space to get me the 4" distance from the trap to the AAV. I'd have to drop the P-trap a few inches, or increase the slope of the 4' trap arm. I made a little picture to explain my current setup and options. Which way can I go? Thanks,
|
Follow-Up Postings:
|
| How far away is the tub from the main drain? If you're within 6' you don't need a AAV unless you have 2 fixtures behind a vent. The best way to explain that to you is...if you fill up the tub and drain it, does the sink or toilet in that room make a sucking sound? By code, AAV's or back vents are supposed to terminate 6" above the highest fixtures flood rim on that line. |
|
- Posted by lazypup (lazypup@yahoo.com) on Tue, Apr 17, 12 at 7:46
| Under the IPC & IRC the maximum length of a fixture arm can be computed by dividing the diameter of the drain by the pitch. If an 1-1/2" line is installed with the code standard 1/4" per foot pitch the maximum lenght would be 1.5 / .25 = 6ft but in this instance the line has a 1/2" pitch so the maximum allowable length would be 1.5 / .5 = 3'. (The bottom of the drain line at the trap weir may not be higher than the top of the line at the vent opening). Both the configurations illustrated above would not pass code for a number of reasons. The simple solution would be to remove the drum trap & extend the length of the tub drain tailpiece. Code will allow up to 24" vertical drop from the tub drain opening to the water level in the trap. Attach a P-trap and run the line with a 1/4" per foot pitch. A wye can be installed on the drain line with the side input angling downstream. You can then put a street 1/8bend on the wye side opening input, which would turn the side opening vertical and attach an AAV where the base of the AAV is 4" above the drain line. REF-IPC |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Plumbing Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.