Follow-Up Postings:
|
| woops....on the future vent, I meant to say it goes from the basement to the attic vertically @ 10' and then horizontally roughly 9ft (not inches) then stubs up to a 3" through the roof. |
|
| here is my proposed vent and draining drawing: Does this work? Can the toilet drain turn in drain to the front or does the drain have to turn and go behind the tank? I can not get a vent into the left wall by the shower from underneath due to a floor joist being directly under the wall cavity. I was planning on going into the the shower wall, which does not go to the ceiling, turning horizontal to vertical then proceed up to the attic through the wall between bedroom2 and shower. I will then abandon the future vent in the first drawing. I would like the drains for the WC & Shower to be in the same floor joist cavity to eliminate drilling floor joists. I believe I have a total of 9 DFU's for the bathroom group. Can I use a 1 1/2 vent for the tub/vanity and then tie to the 2" from the shower/WC? I can't find a lot of info on critical distances for the drains to the vents. Any info will be greatly appreciated. I am completely behind the 8ball on this job as I told my wife she would be able to take a bath in her new tub by the time she Graduates from college. Which is in a month. Yikes! Thanks, Steve |
|
| Anyone able to help me on this or confirm that my plan will work before I sheet-rock? Anyone? |
|
- Posted by lazypup (lazypup@yahoo.com) on Wed, Apr 27, 11 at 7:54
| Before we begin, to answer one of your questions, you can find the UPC vent size DFU table on the Vent page in your code check. It is listed as table 11 on the right hand side of the page. I can see a number of small problems on your proposed layout. 1. On the branch drain which is serving the W.C. & shower you show a cleanout on the end of the line with a wye & 1/8bend and a fixture arm to the shower, then another wye & 1/8 bend with a short horizontal offset to the vent riser. In that configuration you have a horizontal offset on the vent below the floor, but code prohibits any horizontal offsets on a vent until the vent reaches an elevation at least 6" higher than the flood level rim of the highest fixture served by that vent, which in this case you be 6" higher than the W.C. bowl rim. You could place the shower arm wye between your proposed location for the cleanout and the vent. In this manner the vent would be on the downstream side of the shower arm and assuming the vent rises vertically you would be ok. For the branch serving the W.C. and the shower the combined fixture load is 4dfu's and an 1-1/2" vent is rated for up to 8dfu's, but note the subscript 2 beside the dfu number. If you look at the second exception on the chart it says NO W.C. A wc requires a 2" vent. On that branch you only need a 3" drain until you reach the wye at the WC. From the WC wye to the shower and vent it can be 2" but be careful here as well. On the top of the drawing it shows the 2" vent has a horizontal offset to the vent through the roof. If any horizontal offset on a vent line exceeds 3' the entire vent line must be increased one nominal trade size. That means the entire vent would then be 3" and the drain line downstream from that vent opening would also need to be 3". If you have enough vertical clearance in the attic space you could make that offset rise at a 45degree angle because in plumbing any line that rises at an angle of 45degree or greater is said to be a vertical line. The lavatories are rated at 1dfu which would be an 1-1/2" drain line, but code will allow us to increase the drain line by one nominal trade size, which would then be 2". A 2" fixture arm is allowed to go 5' from trap weir to vent opening. I roughly scaled your drawing and you should be able to run a 2" line from the tub and tie the vent in at 5'. The vent should then rise between the two lavatories very close to the left hand lav as facing the lavs from the front. You could then run a 2" over to the other lav and still be under the 5' maximum, thus you would not need two vent risers on this wall. The total dfu load for the tub and two lavs is 4dfu's which could be vented with an 1-1/2" line, but since you have a horizontal offest greater than 3' the vent must be increase one nominal trade size, which would be 2" which you have already specified. |
|
| Lazypup, Thank you very much for replying. I was hoping you would chime in here. This drawing is definitely not to scale, and all the lines shown for drains are not to scale. This was just a real rough drawing to get my plan started. Now with the knowledge in your reply I can move forward and adjust as necessary. One question on the vents running horizontally in the attic. These runs are both longer than 3'. If I run the vent straight up through the roof on the shower/WC vent and serve that with a 2" I can then tie the vanity/tub vent into that. I do not have enough clearance to go @ 45 degrees in the attic with that vent so this will have to be horizontal( pitched of course). If I sized the vent for the Tub/Vanity to 2" to accommodate a trap arm distance of 5', would the entire vent need to be up-sized to 3" both horizontal and vertical, or only the section in the attic which goes horizontal? If I do then I think I could run 1 1/2" vents from the tub, into the vanity (as shown in drawing) and then only have to up size to 2" due to the horizontal length and do away with wet venting. Does this make sense? I am going to adjust my drawing and re-post. Would it be OK to email you my updated drawing for further critiquing from you. I am hoping on doing this job this weekend. Thank you very much again, Steve |
|
- Posted by lazypup (lazypup@yahoo.com) on Thu, Apr 28, 11 at 11:43
| The tub & vanity drain has a combined load of 4dfu's and no WC so if that vent were to go straight up and through the roof it would only need to be 1-1/2". Since you are proposing the long horizontal section in the attic space you need to increase that one nominal trade size which means you need a 2" vent from the drain line all the way to where it ties into the other vent line. |
|
|
|
| Lazypup, So I started digging into my walls today. I have some restrictions/limitations in the shower walls where I proposed my vent for the WC/Shower. I am now going to turn the toilet so the back faces the Bedroom2 as in drawing #1. The Master Bedroom mate wall houses a pocket door so I am building a false wall in front of it. I plan to run the vent up this wall into the attic. I believe this will make things a lot easier. I will also be putting some shelving for the toilet in this wall. So my question is this, can I extend the 3" past the WC and stub my 2" trap for the shower into it with a 3"x3"x2" Wye with a clean-out on the end, or do I reduce it to a 2" drain past the WC to the shower? I read a 2" horizontal wet vent can handle 4 DFU's and a 3" 8 DFU's. Would this be considered wet venting, or is it just a trap arm length critical distance? The new 2" vent location would end up 56" downstream from the trap weir of the shower, and 20" downstream of the WC. If I am correct, the toilet needs to be within 6' of the vent and the 2" Shower drain within 5'. I will then proceed vertical to the attic and 45* to a point where I can stub through the roof. I think this will work right? Thanks, Steve |
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Plumbing Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.