hot water runs cold after 5 min. Help please!

sumnerhousesf_com
13 years ago

We have a mystery on our hands so the following is details of our situation. We are having an issue with the hot water in our building. After about five minutes using the shower or any faucet, the hot water turns lukewarm and then cold. At first we thought it was the water heater as the culprit, but it seems to be more complicated than that. I have the best plumbers in San Francisco, but we are all baffled as to what is causing the problem.

The unit is a two bedroom two bath, 1200 ft.� apartment with a high-efficiency State 50 gallon water heater, powering the hot water. During normal use, there should be more than enough hot water for a long shower. In fact, everything worked fine up until recently. The water heater seems to be running fine. The pilot is lit correctly, and it turns on when it needs to. In fact, we recently installed a temperature gauge to measure the water temperature. When the water is off it reads 130�, but when turned on the water goes down to about 100�. In troubleshooting the problem, my plumbers thought it may be a check valve that has gone bad or the thermostatic valve to regulate the water temperature that is attached to the system.

The plumbers replaced the check valve and the thermostatic valve, but the same problem exists. After about five minutes the water temperature will go down to about 100� or less. There is a recirculating pump attached to the system that is also working correctly. The plumbers don't think that has anything to do with the problem since the pump should not affect the water temperature. At any rate, my plumbers believe that there is cold water somehow getting into the system. The water that comes back into the return comes back cooler than it goes out.

In addition to all of this, we have an automatic washing machine shutoff valve installed in the laundry room. My plumbers now suspect that this is actually the culprit. Somehow this unit has gone bad as is allowing cold water back into the system. You can see details of the Watts unit we have installed here:

http://www.watts.com/pages/learnAbout/intelliflow.asp

To make things more complicated, the 50 gallon water heater also powers a radiant heat floor system to heat the house. This is a closed looped system and should not necessarily affect the water temperature of the fixtures.

Here is where the mystery becomes more interesting. The building is a two unit building, and each unit has a separate but identical plumbing system each using a 50 gallon state water heater. I recently realized that we are having the same issue in both units! Is it possible that in both units the automatic washing machine shut off is causing the problem? Or is there something else causing this issue? If anyone has any ideas or experience with something similar we would love your help on this. If anything, this could serve to help someone in the future with the same problem. Thanks!

Here is a link that might be useful: http://www.watts.com/pages/learnAbout/intelliflow.asp

Comments (8)

  • justalurker
    13 years ago
    last modified: 9 years ago

    Diagnostic rule #2... eliminate one thing at a time until the problem is found.

    It should be easy enough to remove the washer valve from the system and know if that is the problem.

    I remember reading of a similar problem somewhere and it was an automatic washer shut-off valve that caused the problem.

  • zl700
    13 years ago
    last modified: 9 years ago

    If the radiant heat switches on depending on it's size, it will suck the heat out of the tank quickly. Being probably only 40,000 Btus, most likely it can't keep up. Poor mans combined radiant heat with domestic hot water off one tank is a lousy and potentially unsafe system.

  • tim45z10
    13 years ago
    last modified: 9 years ago

    How old is the heater? Could sediments and very cold outside temps be a contributing factor?

  • weedmeister
    13 years ago
    last modified: 9 years ago

    Could the dip tube have fallen down?

    In a tank, there is a tube that connectes to the cold water inlet and directs the cold to the bottom of the tank. The hot comes from the top of the tank. If this tube comes off, then the fresh cold that comes into the tank goes immediately out through the hot.

  • brickeyee
    13 years ago
    last modified: 9 years ago

    Disconnect the fill line to the water heater and check if the dip tube is broken.

  • sumnerhousesf_com
    Original Author
    13 years ago
    last modified: 9 years ago

    Thanks everyone for the responses. Our water heaters are only 6 years old so its hard to believe they would be busted already. State brand high efficiency 50 gal, 65000btu heaters.

    We turned off the radiant heat and isolated the system bypassing the floor heat. Same problem. I agree with some of you that it could actually be the dip tube. A funny thing though, the water return seems to come back cold. We may also have a broken check valve somewhere.

    Seems the only way to fix this is to break down the parts and see whats busted. It may be a costly repair. Thanks to everyone. I post once we solve the mystery.

  • sumnerhousesf_com
    Original Author
    13 years ago
    last modified: 9 years ago

    Success!

    After a long battle, we finally figured out the problem. It turns out, there was a bad check valve, near the recirculating pump that allowed the cold water to get into the system. the same check valve failed on both systems. We opened it up, and both of them were encrusted with calcium deposits and hard water debris not letting the valve close.

    Just for future reference to anybody with a similar problem here is how we tackled it:

    -We checked the dip tubes on both hot water heaters , and both of them were fine.

    -next, my plumbers isolated the hot water heater to make sure the heater was running properly. all checked out fine.

    -We turned off the radiant heat systems and bypassed them with the built-in valves.

    -My plumbers opened up each shower fixture and closed off the water valves to take those out of the equation. the hot water still ran cold.

    - Next, the plumbers removed the recirculating pump and checked the system. the water still ran cold. at this point it had to be the check valves, since nothing else would cause the cold water to come back into the system.

    - The plumbers then starting removing the check valves beginning with the one near the recirculating pump and discovered the broken valve. If this still didn't work, they would've kept going to check every check valve in the system(three total).

    the plumbers installed a temperature gauge to be able to see the change in water temperature. now the temperature holds solid and 120� when the hot water is turned on. I can't wait to take a piping hot long shower.

    Below is a picture of the plumbing system if you were curious. Two water heaters, one for each unit with the radiant heat manifolds.

    Radiant heat system by Warmfloors, Napa Ca
    Installation by AG Quality Plumbing San Francisco, CA(the best plumbers in San Francisco by far)

    Thanks all!

    Here is a link that might be useful: {{gwi:2013484}}

  • justalurker
    13 years ago
    last modified: 9 years ago

    They weren't BAD check valves and they didn't FAIL. The fact that the check valves died in both system shouts out that it is the environment and not the check valves failing. Hard water does that and will continue to do that to fixtures, valves, appliances, and plumbing.

    Ever had your water tested cause radiant heat doesn't like hard water.