verifying correct gas flow to range?

Posted by stuarbc (My Page) on
Wed, Jan 15, 14 at 14:01

Builder had the plumber install the gas lines for my house. The line enters my house as 3/4" galvanized pipe, goes into the attic and then branches off. One branch reduces down to 1/4" copper tubing and then run across the house (in the attic) about 40' before dropping down to the gas range. The other line stays 3/4" piping to a stub out on the side of the house. I have to run piping from the stub out to a fire pit. After researching the size pipe needed for the fire pit, I am concerned that the 1/4" tubing he ran to the range is not enough. I confronted the builder and said that per what I saw on the internet listing code requirements, the pipe appeared to be undersized. He would not change it....stating that that is the size they have always used and have had no problems.
I purchased one of the NXR 30" ranges that have 4 x 15000 btu burners and a gas oven.....so pretty high capacity. I was trying to find a way to verify that the range is getting the proper flow.....but do not know of a way to measure BTUs.

The only way I could think of would be to run one burner on high and see what the flame looks like.....then turn everything on and see if the flame looks the same or smaller. If it is smaller, that should show that the flow is restricted.

Is there a better way?


Follow-Up Postings:

 o
RE: verifying correct gas flow to range?

Call your gas company tech support and ask what size line is required for your range.


 o
RE: verifying correct gas flow to range?

It is customary to use 1/2" black pipe (iron pipe) for a gas range. For my detatched heated garage I used 1/2" id copper tubing - about a 60' run.

Are you sure it's 1/4"?


 o
RE: verifying correct gas flow to range?

it is 3/8" OD.....which I understand is 1/4" tubing


 o
RE: verifying correct gas flow to range?

3/8" tubing 40 ft in length will get you about 45 cubic ft of gas per hour at residential pressure, a bit over 45000 btu.


 o
RE: verifying correct gas flow to range?

Is residential 2 psi? Per my review of the sizing charts and the attached diagram.....I show that I would need 1" in the main line and the line to the range would need to be increased from 1/4" copper to 1" if it were to remain copper.


 o
RE: verifying correct gas flow to range?

Stuarbc - call your City Code Enforcement Office and ask them.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Plumbing Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here