| Since there is quite a bit of continued discussion on LED UCL, continuation of jem199's LED UCL DIY
http://ths.gardenweb.com/forums/load/lighting/msg0600194417283.html |
Here is a link that might be useful: LED UCL DIY
Follow-Up Postings:
|
| The 2 main options 1. Direct wire 120V AC 2. Low voltage (24V or 12V DC). Low Voltage UCL characteristics Direct wire UCL characteristics Common to both options c. There could be interesting shadow zones depending on the relative position of the bars. This typically happens in corners where the light bars should be placed perpendicular to one another rather than on the hypothenuse. There could be a shadow zone between bars that have a significant spacing between the ends. Hope there's enough food for thought. |
|
| Thank you Davidtay for such great information. |
|
| All I can say is WOW! Thanks so much Davidtay - you just made my whole night with this information. I have been scouring lighting sites & a few stores all day today trying to decide on UCL. Any thoughts on above cabinet lighting? Am I right in assuming the same product will work equally well above as below? |
|
| Probably the same products would work. I would consider using higher output lighting for above cabinet lighting since it is the equivalent of cove lighting. The answer depends on the distance to the ceiling/ closest main reflecting surface and the amount of space to hold the light bar. If the distance is too close, the output should be lower. If the above cabinet lighting is just for accenting some architectural features, the output from low voltage strips would suffice. |
|
| The most important task to prepare for a continuous LED UCL install is to figure out how to fit the longest run of lights end to end under the cabinets. If the cabinets have intervening fences/ stiles, it may be difficult (or impossible) to form a continuous led section. Notching the cabinets is difficult once they are installed. Corners should have the bars fitted perpendicular to each other to avoid interesting shadow zones. The next is to decide whether to use direct wire or low voltage. This is more a logistical/ financial than technical issue as it requires selecting possible candidates and pricing out all the components involved in setting up the system. Low voltage A thicker gauge wire may also be necessary. Many sites have a calculator for figuring out the wire gauge for a given power draw. The cost of the transformer could be a significant component of the system which could result in the low voltage system costing more than equivalent direct wire systems Direct Wire Some reasons to use direct wire Reasons to use low voltage |
|
| The thread that just won't die ;) I've been here for a few years, and am feeling pressure to get undercabinet lighting into my kitchen before it's time to tear it out and do it over again! The good news is that LED prices continue a downward trend thanks to my procrastination! Anyways - I'm a DIY'er. Needs/Constraints are: Options: (b) PCB Flexible Strips: This option gets me very low profile, could get waterproof to help protect, diffuse the light slightly, options on how many LED's. In some ways, this is an inexpensive option that could easily be updated in the future if other low profile aluminum housing options appear and/or drop in price. My wires are in place, PCB installed with 3M tape. This option has me considering putting a run on top of my cabinets - would make very nice mood lighting - but I don't really want to put another dimmable power supply in just for this - could look to use the "cheap power" options maybe for this secondary run - i.e. cheap 12/24 power supplies - but maybe reaching too far, after all I don't need to make this more complicated. (c) Flush Mount Aluminum Housing w/PCB Strips and diffuser: This one really interests me, as it presents a rather finished look. Of course it may require me to remove some cabinet and/or run the router upside down (Ikea cabines, so they can come down if needed). It does require a 0.2" depth in the 3/4" cabinet bottom (which I'll make sure is doable before I destroy my cabinets!). My minor concern here is how the PCB mounted in the channel with diffuser will light my countertops (which BTW are a dark granite, so I'm expecting reflections). This would be a rather slick and finished looking design - of course more cost for the aluminum channels. Superbright LED's sells them for $25/100cm for the channel plus diffuser (clear or frosted?), nevermind, these are actually quite cheap! Guess I'm just looking for David's (or other's) quick comments or thoughts on my options. My biggest quick decision is to put some wires in the wall in preparation. The open issue is gauge from the dimmable power supply to the start of my 300cm main run/circuit. Basically 2 areas separated by the stove, with two cabinet interiors mixed in. All to run off the single switch/dimmer. As I mentioned, I know it's a 45W requirement for the aluminum strips - haven't calculated for the PCB option (but will do that next). thanks... |
Here is a link that might be useful: B3775: Flush Mount Aluminum LED Profile Housing
|
| Oh, I should have mentioned potentially using aluminum "L" channel/bracket to create a small valance on the front of my cabinets for use with the PCB LED option. It actually is a very attractive option as shown in the linked post on Ikeafans. It does hold a little more appeal than taking my cabinets back off the wall to route a channel into the cabinet bottoms.... I think. |
Here is a link that might be useful: IkeaFans forums - aluminum valance on cabinets
|
| WAC has nice stick on LED lighting, which to me is more appropriate for accent or mood rather than task lighting. Measure off the wire needed - use string to estimate the lengths of each run. The environmental lights web site has a nice calculator to help figure out the gauge needed. The power draw and wire gauge will be affected by the lights you install, length and distance from the power supply. More power supplies could be used if necessary. Some folks managed to buy the Magnitude branded power supplies. All of the power supplies need to be accessible. There will be stuff on the counter top to detract from the line of light/ beads of light reflected off the countertop. Alternatively, mount the light bars so that they shine onto the backsplash (assuming a highly non-reflective backsplash). That will be an implementation of indirect lighting, so the lighting output would have to increase. Using a router on the underside of an installed cabinet could be difficult and challenging. Uninstalling the cabinets and routing them on a bench would be more practical. |
|
| 120V direct wire solutions can be easily changed from one type of direct wire lights to another (e.g. - T5/ T4 fluorescent, halogen, xenon to LED) . Low voltage lights are somewhat tricker. |
|
| davidtay, your posts on UCL and on LED recessed lights are extremely helpful as I plan for a kitchen remodel. Thank you. |
|
| Sorry to be late to the party but here's a simple questions but has me quite perplexed. My contractor who remodeled my kitchen 11 years ago insisted on fluorescent lights--I hate them and refuse to turn them on. I want something warmer, don't care about low voltage--is there an easy solution to change them? They are direct wire on a switch. |
|
| Direct wire solutions such as MaxLite or the Philips eW Profile bars come to mind. If given a choice, I'd pick the Philips eW Profile. |
|
| Thanks for the reply. Is this a DIY or would I likely need an electrician? All the direct wiring is there, can I just change the fixture? |
|
| Yes, it could be a DIY job if you're comfortable changing out the fixture. |
|
| Should I get the 2700 if I want it warm, close to incandescent? Is it just a matter of changing the fixture? Any suggestions of where to purchase? |
|
| Yes. 2700k would be the optimal. You may want to shop on-line. eg environmentallights.com ledneonlight.com |
|
- Posted by renovating (My Page) on Thu, Mar 1, 12 at 15:40
| I do not understand electricity, wiring, or lighting. It's the one thing in my house renovation that I just cannot wrap my head around. The language barrier with my electrician is not helping. I've been reading this forum and only becoming more confused. I'd like to ask what I think is just a simple question. Kitchen was gutted for the renovation. Told electrician I wanted UCL, but at the time, had no idea what kind I wanted, other than direct-wired and dimmable. He could offer no advice or suggestions. He did the wiring for 5 lights on 2 walls, all controlled by 3 switches on different sides of the room. I purchased the Ancona LED lights from Costco (link below). He installed these for me with the basic Lutron Maestro dimmers that he used for other lights in my house. These dimmers do not work with these lights. Do we just have the wrong dimmer? Do we also need a transformer? If so, am I looking at a lot more expense and opening up walls? The alternative is to just use regular switches and have the ability to individually control each light bar with the on-low-high switch on the bar. Now that I have them installed, dimming might not be as important to me as I thought it would be -- especially if it would require 3 more expensive dimmers and a transformer. |
Here is a link that might be useful: Ancona LED UCL
|
| No, according to the description, the lights do not require a separate transformer as they are intended to be directly wired to a 120V AC line. The fixture is probably not dimmable given that it has a hi/lo/off switch. |
|
- Posted by renovating (My Page) on Thu, Mar 1, 12 at 20:15
| Ahh... that's what I wondered. Wasn't sure how to determine whether a fixture was dimmable, and what you say makes a lot of sense. Thanks so much. |
|
| There is a game changer from tech lighting. Some characteristics 1. Direct wire, 2. Implements remote phosphor. 3. Very high output. 4. Custom lengths? |
Here is a link that might be useful: UniLume LED UCL
|
| At almost $10 per inch it better be worth it. It will never pay back the cost on energy. |
|
- Posted by musky-hunter (My Page) on Sun, Apr 29, 12 at 21:12
| I need three different runs for ribbon light. Two are under 30" and one is 72". I want to use a single magnetic transformer with a AC wall switch dimmer. Is this possible? How do I split the two DC leads out of the transformer for the three runs to the ribbon runs? Thanks. |
|
| You could tie the 2 shorter ones to one lead and the long run to the other. |
|
| Assuming that you have 2 sets of leads (4 wires) |
|
- Posted by WildWomanSkins (My Page) on Wed, May 2, 12 at 17:26
| Anyone know if Lutron's CL dimmers (eg. Diva DVCL-153P) work with both magnetic and electronic led drivers? They call the technology of the dimmer "HED" high efficacy dimming. Sounds nebulous, but the Lutron tech with whom we spoke could tell us nothing more. He just did not know anything more. My husband, who really is a professor of electrical engineering - nanotechnology, thought it's probably some solid state circuitry. Wouldn't that mean electronic? If so, why don't they just say electronic???? I'm thinking to go with the direct wire product, so maybe it's irrelevant for me. Davidtay seems to really like the phillips eW. Maybe go with that. Thanks for the reference to the UniLume product, David. Looks like the same technology as in the 60W replacement bulb from Phillips. |
|
- Posted by WildWomanSkins (My Page) on Wed, May 2, 12 at 17:33
| Argh... UniLume requires a splice box. I just want to stuff my romex directly into the fixture. |
|
| The DVCL-153P does not work with magnetic power supplies. Get the ELV dimmer for the Philips eW profile. Both the eW profile and UniLume require splice boxes. |
|
- Posted by WildWomanSkins (My Page) on Wed, May 2, 12 at 18:31
| Thank you for the info, David. Why do you like the eW Profile better than the MaxLite direct wire solution? Do you know any more about "HED" dimming technology from Lutron? I see that the MaxLite actually recommends the Lutron DVCL-153P. What does that say about the integral power supply type they use? Is it electronic, magnetic, or something else? I deduce from your comment that Philips eW Profile uses magnetic power supply? Hmm... but Philips recommends the ELV dimmer. Are ELV dimmers compatible to both electronic and magnetic power supplies? What about MLV dimmers? Or is it just NOT that simple? These compatibility questions have dogged me for months. What type of dimmer technology is compatible to what type of drivers and why. Can anyone point me to a good online technical explanation? Kind Regards- |
|
| The max lite has a lower output than the Philips. The eW Profile is a nicely designed solution. The eW profile requires an elv dimmer. Most low voltage Ucl use magnetic power supplies and require magnetic low voltage dimmers. Electronic power supplies need elv dimmers. You cannot mix and match Lutron has a nice write up |
Here is a link that might be useful: Dimmer Ed
|
| davidtay: After reading about your thoughts on the Philips eW Profile LED UCL, I was looking into it, but now I've seen your entry for the UniLume UCL. I have a few questions, if you don't mind. Does the Philips eW suffer from some of the drawbacks that the UniLume says it addresses? Have you seen the UniLume in person to compare it with the Philips eW? I'd be interested in your thoughts not only about performance differences but also sense of "build quality." Lastly, what's the cost comparison between the Philips eW and the UniLume? Thank you. |
|
| Starting from the cost perspective, the UniLume should cost ~ $170 for a 19" strip while a 21" eW profile is ~ $110+. The eW profile might require the use of install tracks to ensure that everything lines up in a straight line which will add some cost. No, I've not seen the UniLume in person. The drawbacks that UniLume addresses are primarily The first problem is very noticeable when high output LEDs are run at/ near max output over a very reflective surface. The last issue UniLume claims to solve is the limited light spread of LEDs which might be true for some LED strips, but not so for the Talea-HP, eW profile or the phonier LED bars. |
|
| Thanks so much, davidtay. |
|
| I see some very cheap ($1-$2 / foot) LED strips on Amazon. Anyone have experience with those? |
|
| Specifically, has anyone used the led strips from ledwholesalers.com with the "Dimmable LED DC Magnetic Transformer"? I suspect that this transformer is pretty much (exactly) like the Magnitude, Inc "dc" LED transformer, which seems to be full wave rectified AC, not a steady 12V DC regulator. Since it is a transformer, the dimming can be done on the 120V side, which will be more convenient for my installation (I think). I'll be using multiple transformers from the same 120V regulator, to handle total power requirements. |
Here is a link that might be useful: Supply for strip LED
|
| Some have used the 24V DC version of the Magnitude "transformer" which is really a power supply. Quite a number of low voltage installs using the environmental lights/ superbrightleds/ nora lighting/ Photonier strips (24V DC) use similar power supplies and a MLV dimmer. Others have used 12V DC. It might be more convenient to source all the parts from 1 supplier. The original thread (of which this is a continuation) was started with those strips in mind (even though a number of principles are universal). |
|
- Posted by cottonpenny (My Page) on Tue, May 8, 12 at 19:30
| I've read this thread several times and still a little confused - I am doing a new build. I have (2) 36" uppers on one well separated by the range/hood. I have a 27" cabinet and an 18" cabinet on the other wall separated by the sink which will have a recessed light. I looked at the Philips ew lights but they only come in 9", 19", and 39" so I wouldn't have a good fit for my 36" cabinets. I saw these from Costco mentioned earlier. I guess I could do (2) 14" bars per 36" space. I don't really care if they are dimmable or not. But I'm completely unable to really tell if this will work or not...??? |
|
- Posted by cottonpenny (My Page) on Tue, May 8, 12 at 19:31
|
| The eW profile bars can be mixed e.g. - 9 + 19 or bars with spaces in between - 9 + 9 + 9. The main point is whether the bars will produce enough light. Using a measure such as lumens (for example) instead of measuring the light output by watts would be a better means of determining whether the lights would be usable. Environmentallights and other websites do have charts that help illustrate the light output with distance and illumination angle. If you expect to use the UCL alone without any other light sources, the bars should be capable of producing > 200 lumens per ft (very rough guess without bothering about distances). With the UniLume (~ 600 lumens per ft), you'd most likely have them dimmed. |
|
| bumping to top |
|
| Davidtay or anyone else, I'm redoing my kitchen and we want to do some dimmable UCLs.. We picked up "5 Meter Reel Warm White 2700k Flexible LED Ribbon 300 Leds 16 Ft by LEDwholesalers, 2026ww-27k" from Amazon (link below).. we also bought a "LED Driver", it's the BG-30W-12V as pictured on http://www.alibaba.com/product-gs/567794631/12V_2_5A_Led_driver_30W.ht ml. I'd like to know what we need (in addition to or instead of) in order to make these LEDs dimmable with a normal Lutron or Leviton dimmable wall switch (like the Leviton TGI06-1LB Dimmer Incandescent Single-Pole/3-Way 600W 120 Volt).. I've read on gardenweb about needing a REAL transformer and then you can wire the power to the wall switch/dimmer, then to the transformer, and then to the LED tape.. that would be ideal; but I don't know what to get as the transformer. I suspect we have the wrong stuff.. that's okay.. there's still time to get the right stuff... My contractor is going down the path of getting a low voltage dimming interface (ELV-1000 from http://www.lutron.com/TechnicalDocumentLibrary/031202b.pdf) and a dimmer switch (TGCL-153PH-WH - http://www.amazon.com/Lutron-TGCL-153PH-WH-Toggler-Single-Pole-Toggle/ dp/B0052EC160). Is this the right path? Is there a better way that doesn't involve the "interface", etc? Thanks so much! |
Here is a link that might be useful: 5 Meter Reel Warm White 2700k Flexible LED Ribbon 300 Leds 16 Ft by LEDwholesalers, 2026ww-27k
|
| Get the power supply from your led reseller. If you get a magnetic power supply, you need to use a MLV dimmer. The original thread has more info. |
|
| There's a new driverless LED strip on the market (see link below), and it looks like a game changer -- especially for retrofitting hardwired UCL installations. No transformer is required; it has a small inline rectifier that converts the AC to high voltage DC, then drives the LED strip through what I assume is a voltage divider built into the strip itself. Currently only available in lengths that are a multiple of 20", but they are apparently working on offering more length options. I bought one as a test/sample, and was really impressed. I got the "warm white" which they claim is 3100K. It matched extremely well with other incandescent lighting in my kitchen. Using a standard dimmer, it would only go down to about 50% brightness, but after switching to a Lutron CL dimmer, I was able to take it much lower (I'd guess in the 15% range). The lip below my upper cabinets is only 3/4", and these are completely invisible at any typical eye level. The only thing that might be a problem is that the LED strip comes encased in a silicone shield, obviously for safety since higher voltages are involved. This also makes it suitable for wet locations. The downside however is that this makes it too big to fit in standard strip channels, so if you have highly polished countertops and need a diffuser strip you'll have to get a bit creative. All in all an impressive product though. I'm looking forward to seeing more products like this come out. |
Here is a link that might be useful: Driverless LED Strips
|
| This is over my head no matter how many times I read it, but I think you are all saying direct wired seems to be the longest lasting product. I need led accent lights in my highest cabinets that have glass doors. The cabinets are separate pieces. How do I start on the left with the led lights, go through side walls of cabinets (x3 cabinets) then hop over to the sink (no upper cabinets at all) and continue led lights for 3 more upper cabinets? So there is a 48" gap where there are no uppers. Will this have to be 2 separate lights? I just want them as accent lights. We are putting antique dishes up there to show them off. Could also be used as a night light, but we do not want hot lights like xenon or halogen. Then we also need bright undercabinet lights. About 24" on left side of sink then 48" sink/window then continues with 20" of lights, then 42"vent hood, then another 20" of lights. So will I need separate lights for each undercabinet area? 3 switches? Don't want low voltage or puck lights. Any suggestions? Am I stuck with fluorescent? Thanks, Peke |
|
| Peke, is this a remodel? Can you wire in the walls? If not, your options are limited. I will be posting my final design in mid to late March once I've got mine installed and working! David Tay was a big help. I think low voltage tape LEDs are the best for both situations. But you do need in wall power for best setup. |
|
| Direct wire lights may be the best route for most people installing UCL as 1. It is easier to deal with as there is no need to calculate the wire gauge, etc 2. The light output is usually greater. 3. There is no separate transformer/ power supply that has to be located in an accessible place. 4. Lighting is usually the last item people tackle in kitchens and they have little energy left. Measure out the clearances you have first. Fluorescent (t4 or t5) may turn out to be too bulky. You may need to use a solution like that sold by Phantom Lighting. Yes, the lights will have to be separate. They may be joined in parallel to a 3 (or more) way controlling switch setup. |
|
| hi all, we have two upper cabinets - 47" and 34" long, where the UCL will be installed. Currently cabinets have Romex wires coming from the wall right underneath and connected to the switch. This was done when walls were open. Our cabinets also don't have any dividers underneath. We are now trying to decide which UCL lights to go with - davidtay's input on Phillpis eW profile was very valuable and we liked the lights. It is also expensive! Question is - for 47" long space, can (or even should) we get one 41" long fixture or three 11" fitures connected. Will leaving 3-4 inches on the side of the cabinet create weird shadow zones or is it ok? The same applies to the other cabinet - we can't have one straight run and need to assemble from 11"-21" pieces. With the dimensions we have we can't have 100 coverage but do we need it? is there a rule on that? Also, jumpers that are 6" long - can we introduce spaces between 11" fixtures to space them out? The driverless LED Strips post by spacedog looks very intriguing since there is no bulky junction box to deal with and it is dimmable, and also more affordable than eW profile. Do you guys have opinions on this new product yet? thanks |
|
| You don't need to have the light bars arranged in a straight line (for example W or V may be used). 100% coverage is nice, but there are installs which only light up specific portions Get some ideas from your local lighting show rooms. A splice box will be required to connect the romex coming out of your walls to the wiring connected to the light bars/ strips. |
|
| thanks, davidtay. there is a lighting wholesale distributor near where i work, i will check them out. |
|
- Posted by SparklingWater (My Page) on Sun, Feb 17, 13 at 22:15
| Re: Driverless LED Strips As stated, a new and less complicated alternative for kitchen direct wire LED integration in under cabinet lighting. Certificates CE, RoHS European import Wonder about safety issues of product as so new. No Underwriters Laboratories seal since new and imported. Thoughts? |
|
| Yes, it is a remodel. The old cabinets and sheetrock is gone so we can run a direct wire which is what I prefer. I looked at Emeralight but it said something about needing a driver. Now I am totally lost. Are these direct wired? Thanks David...so would I have 4 separate switches to control the lights? One for upper left cabinet inside glass and one for right side. Then one for under left cabinet and one for right side. Is there any way to have all inside cabinet lights (behind glass doors and separated by a sink with no uppers) on one switch? What about the undercabinet lights on one switch? (separated by 48" sink area) (Sorry...you lost me on 3-way and parallel.) LOL I looked at Phantom Lighting website, but couldn't figure out which one I needed. Thanks, |
|
| Peke, The light you looked at are low voltage bars. The lighting can be controlled with one or two switches (3 way setup) Wireless switches utilizing enOcean technology can be used to create multi-way switching setups. I will post a diagram for the 3way and parallel setup later |
|
| I guess I just don't know what to buy for direct wired LED. Do I buy the same light for the upper glass cabinets as for the undercabinet lights? If I buy the right lights my electrician will figure out the wiring I guess. I just don't want to buy the wrong ones. Sheetrock is going up soon so I need to get something ordered. Who knew lights could halt my kitchen remodel! Thanks, Peke |
|
| Peke, Questions to answer 1. What look would you be aiming for for the upper cabinets? - Concealed lights or a puck on the top? If you prefer concealed lighting, you'd need to figure out if you can hide strips like the MaxLite or eW Profile (for direct wire). Otherwise, you'd have to work with low voltage lighting like the PhantomLighting setup or some other low profile led tape/ bar setup. If centrally located string of pucks in each cabinet is acceptable, you need to use low voltage lighting. Assuming that low voltage is necessary for the uppers, you need to figure out where the driver will reside (it has to be accessible) and a separate switch location to control the cabinet lighting. 2. Would controlling the lights in the upper cabinets independently of the rest of the lighting be desirable. If the upper cabinet lighting uses a separate circuit from the UCL, having a separate switch becomes necessary. Recommendations 1. Find out from your cabinet maker/ installer where each of the boxes for the upper cabinets will end up and the best locations for a hole. The location will need to be transferred to the wall, wiring run and the necessary holes made. 2. Plan on having 2 separate circuits anyway (min 2 switches). I've added a link to a description of a 3 way switch diagram with multiple lights (the lights are in parallel so that even if one goes out, the remaining light(s) still function. The nice things about enOcean type switches are that Leviton enOcean example |
Here is a link that might be useful: 3 way switch diagram with multiple lights
|
| I found these direct wire undercabinet lights. Would they work well? Do I need anything else for them to work under my cabinets? Would I get the same for the upper glass doors or some other direct wire lights? Only the top cabinet shelf will have the glass fronts. Thanks, Peke |
|
| Well I guess it helps to put a link. http://www.pegasuslighting.com/led-thin-under-cabinet-task-lights.html or these http://www.elementalled.com/shop-by-item/dimmable-led-lights/dimmable- items-light-bars.html Peke |
|
| The pegasuslighting bar is almost an inch tall (15/16") while the elementalled bar is 1". The style is the same as the traditional t5 UCL lights. Probably not really suitable for in cabinet use - too much room taken up. |
|
| My cabinets were just installed and now I need UC lights. I have 4 separate sections of uppers with Romex coming out of the wall just under the cabinets in the 4 locations. The 4 sections of lighting are to be controlled together, with dimmers at 2 locations (3-way). The available width under 2 of the cabinets is 28” and 18.5” under the other 2 cabinets. My designer recommended the Lithonia Rayzer LED bars in 18” (353 lumens) and 24” (441 lumens) lengths. It looks like the Rayzer requires a separate transformer and step dimmer -- I’m not sure if I can use 1 transformer and dimmer for all 4 cabinets, since the lights will not be physically connected (except by the in-wall wiring). The more expensive Tech Lighting Unilume bars have an integrated driver, but the available lengths do not work as well for me. I would have to use 13” bars (432 lumens) under the 18.5” cabinets and 19” bars (645 lumens) under the 28” cabinets. The UC lights are an important light source in my kitchen, as our wood ceiling prevents us from using recessed cans, so the UC lights are intended to provide both task and ambient lighting. For good light dispersion, would it be better to use longer, lower lumen bars or shorter, higher lumen bars? Are there different products you would recommend to better fit my needs? |
|
| Your description tells me that you cannot use the Rayzer LED bars. The romex wiring and dimmers indicate that your electrician pre-wired for 120V AC. Longer bars would be better. You could stagger the bars to fit 2 13" under the 18.5" cabinet runs. Alternatives - eW profile, maxlite direct wire lights that have been discussed above. I would suggest adding pendants / suspended light bars for better ambient lighting. |
|
| Something like the following would be interesting as an alternative to recessed pot lights |
Here is a link that might be useful: selux linear led
|
| Thanks, David. I guess I want the upper glass cabinets to have a light in the front that projects toward the back of the cabinet. I am not sure if that is the best or not. I just want to spotlight some antique dishes. I am not sure about puck lights. Don't they get really hot? I think I need LED. My electrician has never done any of the tapes with transformers so I don't want him to learn on my house. LOL I think direct wire would be best for us since he knows how to do that. I just need to find the lights. Maybe I will wait until all cabinets are in, then choose the lights. Peke |
|
| Peke, Waiting until the cabinets go in is a bad decision as putting in wiring then without damaging the cabinets is nearly impossible. Options In either case, you still need to consult with your cabinet maker and installer. |
|
| We live in the middle of nowhere so my cabinet guy does not create a plan with dimensions. We can't seem to pin him down right now. He is working on another project. So I cannot do anything direct wired....only low voltage? Peke |
|
| Romex wire is much thicker and stiffer than the typical low voltage wire. Direct wire devices will require larger holes in the cabinets and the bars are typically larger than the equivalent low volrage devices. For in cabinet applications, low voltage devices are typically deployed as size is more important. It is possible to estimate the dimensions of the cabinets, height above the countertops and mark out the approximate locations for the necessary holes in the dry wall first even with minimal input from the cabinet maker. You might want to contact Phantom Lighting directly and discuss things. |
|
| David, I am very annoyed to hear my electrician wired the kitchen in a manner that is not compatible with the Rayzer LED bars, since they were specified by name on the electrical sheets of the building plans. The eW Profile was my first choice, based on reviews here, but the available sizes don't work with my cabinets. Maxlight has good sizes, but not the 3000K color specified for all of my kitchen lighting. In addition to UCL, we will have above cabinet cove lighting, 2 aimable LED spots in a soffit over the bay window behind the sink, an 8' long fluorescent up-down sconce (Artemide Talo) above recessed cabinetry on one wall, and a track with 3 pendants above the island. So, the UCL are not the primary lights, but they are probably more important for ambient lighting in our kitchen than in kitchens with lots of pot lights, so I want to make sure they provide enough light (lumens and width of light). |
|
| The other signs for direct wire would be 1. The voltage readings at the exposed ends of the romex wires give 115 - 125v. 2. There is no romex wire leading to an obscure but accessible location(s) where a power supply would be stored. Assuming that the best solution now is to use the installed wiring, you could have the bars staggered so that there is some overlap or arranged in a W or \ \ fashion. |
|
| It is possible he planned to put the transformer and step dimmer in the attic. There is no attic over the half of the house with vaulted wood ceilings (including the kitchen), but the hallway next to the kitchen has attic above it, so I think a lot of the wiring goes through there. My GC asked what lights I want so he can install them, since the electrician doesn't seem inclined to come back and finish the job anytime soon, so I guess the GC has to figure out how it is wired. I was worried the light might look strange (not in a straight line) if the fixtures are staggered, but maybe that is not a concern? The electrician wanted me to just use the field cutable LED tape he usually uses, but I thought the light quality would be better using a bar with a lens to diffuse the light (to avoid dots on the counter). |
|
| Ask your GC to check if it is direct wire or configured for low voltage. The staggering of fixtures does not matter as much as the illumination result as the underside of the cabinets are not directly visible. For example, if the expected result are uniformly lit counter tops without shadow regions (near the top), the bars may have to be placed in a staggered pattern (especially in right angle corners). The tiny dots of light can be avoided if the lights are installed like cove lighting. In reality, when the kitchen is used, there will be things on the countertops to obscure the reflection. |
|
- Posted by akbarnjeff (My Page) on Fri, Mar 8, 13 at 16:05
| I just called the company that sells the driverless led strips posted by spacedog above, to ask them if they can be direct wired (their website shows them to plug into an outlet). I was told they could be, but that you have to leave the "box" in the middle of the cord in place. So I asked if you simply cut the plug off and connect the plug wires to my 120v wires inside of a junction box and the sales rep said, "Yes." Does that sound correct to those of you with more knowledge of the electrical code than I have? Is it OK to wire the cord to your romex cable? |
Here is a link that might be useful: driverless led strip
|
| You need to connect the romex to the wiring in a small junction box under the cabinet. |
|
- Posted by akbarnjeff (My Page) on Fri, Mar 8, 13 at 17:40
| Thanks David, but my question was more about wiring the "cord" to the romex, than about the junction box (which I mentioned in my post). Just seems odd that you can wire a cord to romex, but very handy if it is legal. |
|
| The cord cannot go inside a junction box embedded inside a wall. However, it can be connected to romex inside an exposed junction box using wire nuts. |
|
- Posted by akbarnjeff (My Page) on Fri, Mar 8, 13 at 18:18
| Thanks again David. I assume this means that a cord can be wired to romex in any junction box that is a true junction box (as in accessible). When you say "embedded" in the wall I assume you are talking about an illegal junction box that is hidden in the wall. |
This post was edited by akbarnjeff on Fri, Mar 8, 13 at 18:22
|
| The romex wire has to exit the wall. The eW profile bars utilize a small under mount junction box to be code compliant. |
|
| David, why does the Phillips eW have to have a transformer? Somehow I missed this part. I am sure you have said why multiple times....sorry. Thanks, Peke |
|
| There is no transformer with the eW Philips. You may be confusing the "small under mount junction box" with transformer. The 2 items are not the same. The small under mount junction box is used to connect the romex wiring exiting the wall to the lamp cord attached to the LED strip. |
|
- Posted by SparklingWater (My Page) on Fri, Apr 5, 13 at 23:00
| Just bumping this informative thread up after reading it again. Thanks davidtay! |
|
- Posted by sparkier73 (My Page) on Wed, Apr 10, 13 at 11:46
| Was sold on Philips eW for our UCL, but having trouble finding a source. Seeing as how it's been available for a few years, has it now been replaced with something newer... better? If so, what? Also - davidtay (or anyone) - the longest jumper available for the eW seems to be a 5'. That is not long enough to connect the cabs across the window/sink area. Can two 5'footers be connected, if so - with what? Or will our UCL need to be operated on two separate switches? |
|
| You can get it from http://ledneonlight.com/index.php?main_page=index&cPath=11_60_64 It would be better to put a direct wire (inside the wall, on the same circuit) into the other cabinet section than to use jumper cables. |
|
| David, I looked at the link on your last post. It looks like they are taller than the ones I posted. The Philips lighting 11 inch 3000k white eW profile powercore is 120 volt and has a small profile of 1.7 inches high by .88 inches wide by 9.25 inches long. |
|
| The height of the bar is 0.88 inch not 1.7. |
|
- Posted by niteshadepromises (My Page) on Mon, Apr 15, 13 at 23:05
| Quick question on the driverless LED linked previously. It appeals in that its super easy for an utter electrical noob to just plugin in. I'm thinking of ease of replacement when the time comes. However if you want to have dimmable functionality, is there any easy way to do that without cutting off plugs? Can you get a receptacle attached to a wall dimmer that you then plug these into? If so can anyone provide the info on that? |
|
| The short answer is no. The general expectation is for switched receptacles to be controlled by on/ off switches, not dimmers. Direct wire lighting should be relatively easy to replace compared to low voltage in that you could conceivably change out one vendor's light bars for another (eg - unilume for maxlite). Having said that, the likelihood of replacing a LED bar is low, barring any major mishaps such as a roof leak /fire. |
|
- Posted by niteshadepromises (My Page) on Tue, Apr 16, 13 at 4:49
| I'm looking for low cost solutions for cove lighting but some decent task lighting if I want to crank it up. I'll probably go ahead and use bars for ucl but much....much too expensive from what I'm seeing for accent or ambient lighting above cabinets or in coves. The driverless Solid Apollo LED's seems to have some awesome lumens per foot at 220, at a comparable price to other conventional tape LED's (by the time you buy the driver) that offer less. Also the long run flexibility. So I guess heres my real question. If I want to use these and have them dimmable as the product description suggests they are, how is the best way to do it then? Is it going to pass code if I tell the electrician to just cut the plug, its a new construction home? Sorry, really am a noob with electrical, I'm sure the electrician would know but I find if you sorta know what you are talking about going into the conversation, it commands more respect. Hopefully Apollo expands their product description to be more precise, its somewhat counter-intuitive to have a plug and play LED strip and advertise it as fully dimmable but not explain how its accomplished (and in fact can't be accomplished by the plug provided). |
Here is a link that might be useful: Ling to Apollo driverless (if needed)
|
| The cord has to be connected to the romex wire outside the wall in a small junction box like that used by the eW profile. As stated earlier Posted by davidtay (My Page) on Fri, Mar 8, 13 at 17:58 |
|
- Posted by niteshadepromises (My Page) on Tue, Apr 16, 13 at 16:37
| Thanks david, after reading the posts 3-4 times I figured that was the jist. Threw me having the EW profile referred back to so I wasn't sure if it was applicable in this case.and whether or not it would pass inspection. The folks at Solid Apollo weren't sure of that either. |
This post was edited by niteshadepromises on Tue, Apr 16, 13 at 16:57
|
- Posted by SparklingWater (My Page) on Tue, Apr 16, 13 at 17:34
| I need to do direct wire UCL for various reasons, but have a 3/4" light rail!. I don't want to use Xenon due to their heat unless they can be dimmed down to less heat. I'm really stuck in that my light rail is 3/4" and very few direct wire manufacturers have lower or equal height profiles. I've called Lunilume distributors near me but they all say they don't carry it. Strangely a lot don't know about Lightolier either (part of EPhillips?). Any low profile direct wire LED light suggestions out there, or ways to lower xenon's produced heat? In many ways I'd prefer xenon (like the light), but I have a few glass cabinets and am concerned with the bottom shelf. I don't even know if xenon direct wire comes in 3/4" low profile. Thinking maybe I"ll skip UCL until something new breaks on the market. Wonder how I'd deal with the romex capped in a junction box if that's even possible to buy some time. I guess I'm going on a little, sorry. This lighting and venting MUA are tough to figure out to the point of an actual purchase. |
|
- Posted by EATREALFOOD (My Page) on Wed, Apr 17, 13 at 22:58
| Sparklingwater:Phillips eW powercore direct wire LED light bars with a 3/4 light rail should work fine.(how deep are other light rails ? deeper than 3/4"?) They have a low profile. I have them with no light rail and cannot see them straight on but can see them in the adjoining room which does not bother me personally..These lights are very simple for you if you are handy or have an electrician to install. |
|
| The local lighting store, our contractor and our electrician all suggest we use the Seagull Ambiance LED lights for our UCL. Is there a reason we should push to use something else? So many other things to deal with, I would rather just go with what they are recommending unless there is a good reason not to. Frogster |
|
| As stated earlier in the thread, the 2 main choices are direct wire or low voltage. The Seagull ambience LED options appear to be mostly low voltage. To reiterate Reasons to use low voltage Please read through the discussions on this thread (& the predecessor) You need to price out the entire system and at least one other alternative. It will be a substantial investment. Since you're going to have to live with the UCL, make sure that it will be something that works well for you. |
|
- Posted by SparklingWater (My Page) on Wed, Apr 24, 13 at 22:06
| An International Light Fair is currently being held in Philadelphia PA, USA. I spent a good hour looking around at the awards section, particularly looking for new concepts in under-counter lighting (ucl) but nothing stood out on ucl. I am noticing that Europeans tend to use an ucl LED puck light design in the kitchen. While I can't recall the manufacturer, I recently viewed an ucl puck of 43 or so diodes per round puck (designed in response to consumer requests), and is dim-able (very bright). Any thoughts on LED ucl puck lights, which casts a sort of triangular light rather than rectangular light for UCL? Here's a link to some new LED lighting concepts, commercial and residential at the fair. |
Here is a link that might be useful: link
|
- Posted by SparklingWater (My Page) on Thu, Apr 25, 13 at 22:39
| I'm going to investigate the Phillips 0.88 inch PowerCore, ERF. It would be 0.13" over the .75" light bar in height. Today I meet with a lighting designer about Lunilume which is less than 3/4" height profile and hard wired (splice box required). Lastly, Lowes Kichler Utilitech LED can be hard wire spliced I believe but major draw back of not dimmed. Not the best reviews however. Their newer Utilitech Pro is dimmable, but over 1 inch. I keep viewing low voltage tape, strips and bars DIY on youtube: with a little electrician's help due to my 120 AC fear, I think that is a very viable option, especially aided by davidtay's wiring notes and the first ucl diy thread.
|
|
| I have read and reread these threads about UCL. I hope someone can help me make sure I have what I need. We currently have hard wired flourescent lights. I want to switch them out for LEDs. I bought Juno upled pro series in various sizes to fit the cabinet lengths we have. they are listed as 3000k and dimmable. I saw them in a local lighting store and I liked the light, bright but not blue. A few questions: 2. The specs state that they are compatible with several magnetic low voltage dimmers and electronic low voltage dimmers. Is there one dimmer that is better than the other? 3. My GC says that lights are usually installed closer to the wall, which is how the current ones are installed. After reading the posts here and looking at the spec sheet, it looks like the recommended location is to install them as close to the front of the cabinet as possible. When I told him, he said, "lets just do it in the middle instead." So, front or middle? I have the lights. I need to buy the dimmers and if we mount them closer to the front, I will need a cable to allow for that. Does that sound right? Thanks so much for any help you can give me! |
Here is a link that might be useful: Juno upled lights
|
| A small junction box may be necessary to splice the romex wire if the original is too short. You might have to use the old position if finding the appropriate box is too difficult. Using an ELV dimmer would be more sensible. |
|
| Davidtay: thanks for the help!!! Is this what I need to move the boxes closer to the front of the cabinet? The link below us for a direct wire module. Just to clarify, if this is what I need, would you recommend mounting them closer to the front of the cabinet? Our uppers are 12" deep and bottoms are 24". Thanks so much for your help!! |
Here is a link that might be useful: Direct wire module
|
| Probably. Most of the installs on this and the previous threads used the 3 pin low voltage LED bars. 12" is not that much room, and the lights you're intending to use aren't that thin, so the variation in the placement wouldn't be that significant. I would suggest considering using the existing location as that would be more cost effective. |
|
| Oh, no...now I'm worried. Are these lights not recommended? When I went to the lighting store, I liked the color/brightness of the LED light, the fact that they are dimmable and that they are the hard wire kind. Should I look for a different kind/brand of light? The uppers are standard depth, which I thought was 12inches, is that not correct? So, then when does placement become an issue? Sorry for all of the questions. I thought I was on the right track with the lighting... Thanks again for all of your help!!! |
|
| sorry, duplicate! |
This post was edited by rkb21 on Sat, Apr 27, 13 at 20:02
|
| Use what you're comfortable with. There are many choices ranging from the exorbitant to the traditional look. If you use a sleeker bar like either the MaxLite or eW profile, there is more room to play with. Some place the light at the front and angle the light towards the backsplash. A traditional UCL is usually placed at the rear to middle as the lamp faces forward and the housing offsets the lamp towards the front. Placing the UCL at the rear ensures that the romex wire is largely obscured by the housing body. I think you should price out the entire system you looked at as well as another alternative such as the eW profile or Maxlite bars. The lower the profile, the higher the price. |
|
- Posted by SparklingWater (My Page) on Sun, Apr 28, 13 at 17:14
| Not much discussion of cost of LED ucl on this thread so I thought I'd summarize a quote I got on AC direct wire/step down to 24v. also, the power switches and hardware supply(s) are 1 inch, so exceed the light rail profile of 3/4". 12 three-prong led fixtures of various sizes for 8 uppers $2032.00 not including tax Is there a less expensive way to still use LED for under-cabinet lighting? Can you pull the 120v romex through and connect to a halogen or other puck light for now? Then later, change out to LED when costs drop? Or can you forget AC romex pull and just do entirely low voltage for savings (led 3M tape-does that wreck painted cabinets when removed)? Thank you very much for any advice. While I've read and re-read these threads, I'm just not grasping how to do these under-cabinet lights without spending a small fortune. |
|
| The nice thing about direct wire is that you have more options - halogen, fluorescent, xenon, led and can swap out the fixture more readily in the future. With low voltage, you might be constrained to either 12V or 24V depending on what you're replacing. Converting from low voltage to line voltage will require pulling the necessary wiring and potentially making additional holes in the cabinets. Removing stick on lights may pull off some paint. Why do you need so many switches? |
|
- Posted by SparklingWater (My Page) on Sun, Apr 28, 13 at 23:06
| Yes, I'm not sure, but I wonder if it could be a new local 2013 electrical code? Vaguely remember hearing about bad news that each light needed it's own box but when I spoke with the electrical code office directly about this, he said nothing. I have to ask the Rexel dealer to review how he came up with this. I do agree having direct wire placed while down to back walls (who knows what shape they are in) is prudent. That's why I've been searching vigorously and rather unsuccessfully for a low profile LED direct wire. This isn't even the Unilume quote. I may have to consider other lighting format for now. One nice aspect of my frameless cabinet is it's 3/4" thick on the bottom of the uppers, so xenon-produced heat will have farther to travel before impacting items in the lower shelf. Doesn't dimming of xenon lower the voltage and thus resistance induced heat? davidtay, have you looked at Halo led ucl, by Cooper Lighting? I briefly looked at it and bookmarked to research this week. Imported but priced reasonably. Thanks very much. |
|
| "If the cabinets have intervening fences/ stiles, it may be difficult (or impossible) to form a continuous led section. Notching the cabinets is difficult once they are installed." Just notch out the wood. "Using a router on the underside of an installed cabinet could be difficult and challenging." Try a "Gent's saw' and a little handwork. It will easily cut the small section of case side below the bottom of the cabinet floor, and then you just pop it out with a chisel. Has had work died so badly everything must be powered? Even a tiny notch on the bottom of a cabinet edge? If you are worried about the wood not breaking off cleanly enough, make repeated adjacent cuts and use a smaller chisel to clear them (maybe even bevel down and at an angle to start). Even in the age of 'power everything' some handwork if often needed. You could even use a very narrow blade on one of the oscillating tool cutters to clear the waste between the two vertical cuts. You can take an oscillating tool saw blade and cut it down even narrower. |
|
- Posted by SparklingWater (My Page) on Fri, May 3, 13 at 17:47
| Oops, xenon lighting results in a gaseous state , so no dimming with them. My Unilume quote came in at around $2600 for 9 lines etc of various sizes. Surprisingly not much different from the first quote. davidtay or anyone, have you ever used tresco LED lighting products? similar to unilume in quality as far as I can see from spending some hours on their videos and site. Huge selection of LED products. Not feeling the cost here...but more manufacturers should weigh in soon on my lighting plan for ucl and in cabinet light. |
Here is a link that might be useful: tresco led
|
- Posted by SparklingWater (My Page) on Fri, May 3, 13 at 19:05
| davidtay-I'm not sure I understand your LED diagram with one transformer downside from an AC switch and parallel led light sides across room space. For example, I can see one switch and one accessible transformer on EACH side of my kitchen, for total of 2 switches and two transformers. I can place each of the power supplies in an accessible place with separate AC switches (dimmer switches) close enough to each transformer to be wired, then the DC wires/jumpers connect to the led bar lights. I don't get how you can jump clear across the room to the other side using just one switch and power supply without low voltage wires going into ceilings or floors to get to the other side, which my remodel isn't doing. What am I missing here? ps: Peke, if you're still here, how did you lighting turn out? Did you figure out your install. thanks. |
|
| The diagram is just an illustration showing how 3 separate runs could be made in parallel. People do have low voltage wiring in the walls, floors and ceilings - lighting, sound systems, networking ,... If you don't want to use in wall wiring, there is the flat wire option which is embedded in the wall texture. |
|
| "Oops, xenon lighting results in a gaseous state , so no dimming with them. " Say what? Dimming Xenon charged light will result in more darkening of the envelope by the firmament (with a decrease in life) but it still depends on how often and what level you dim them. If they send most of their life on full they will be just fine. |
|
- Posted by SparklingWater (My Page) on Sat, May 4, 13 at 15:26
| Ooops,oops, not xenon sorry. It's electrified fluorescent light tubes that are filled with noble gases such as argon, krypton or neon to eliminate chemical reactions resulting from the electrical discharges in the tube. Thanks brickeyee. Btw, what's your opinion on LED under-cabinet lighting? Our local lighting designer who works at the lighting supply and is very knowledgeable, told me LED pricing will never come done due to its requirement of trace elements. Not sure about that. To follow our local code of 18" to combustible surface lateral to my range, I raised the cabinets 3/4" and bought a 3/4" light rail. Given that step and frameless flat cabinets, one of the lowest profile lights is needed which happen to be LED. Not a bad choice, just that my GC wants direct wire. It's all going to work out though, and LED it will be. |
|
| What trace elements? LEDs are now poised to displace CFLs and other cold cathode lighting. LED has already displaced cold cathode (fluorescent) backlighting in LCD TVs. LED UCL will only see a gradual decrease in pricing because UCL is only a small portion of the lighting market. The easiest option is to use direct wire. |
|
| "Rare earths" are used in some semiconductor fabrication steps, many that manufacturers will not disclose or discuss. Semiconductor fabrication is often protected as proprietary until no longer economically useful. Patents require you to reveal more information than the manufacturers are willing to give up. The actual manufacturing procedures and steps are the 'tricks' that make it work. |
|
- Posted by SparklingWater (My Page) on Wed, May 8, 13 at 21:02
| I continue to research Unilume undercabinet LED due to it's excellence in many ways and at 0.74" inclusive of built in tranformer, a true low profile for my 0.75" light rail. To keep the cost more in my budget, I wish to ask if I could consider centering a 19" bar on each of three 30" cabinets and later consider adding another 7" bar to each via a jumper cable. As I understand it, Unilume lumens are 600 lumens per foot at 90 CRI/3000 K. That is a lot of bright light and as my cabinets are long, a lot of light over a long distance. For this reason, I wonder if I might compromise in the above manner initially. Three of the 30" cabinets will have in-cabinet lighting, as well as LED recessed cans above pointed to counter top edge above. Thank you for your thoughts on this matter. Time to demo is approaching and soon I must make my decision. |
This post was edited by SparklingWater on Wed, May 8, 13 at 22:08
|
| It would be just like using traditional ucl- the important areas are brighter than others |
|
| Hi all. I was just on Lowe's website, and they are supposed to get Utilitech led direct wired dimmable ucl in 2-4 weeks. I am in Oklahoma which means your state may already have them. We get things about 6 months after every other state. Reasonable prices. 12", 18", 24", and 30" David have you heard anything yet? |
Here is a link that might be useful: lowes utilitech ucl
|
| This is a direct replacement for the typical t5/ t4 fluorescent Ucl box. Each is expected to be wired directly to a romex wire coming out of the wall which would be the case when previously configured for fluorescent Ucl. The height is > 1" which is taller than either the maxlite, eW profile or newer lights from Philips. |
|
- Posted by SparklingWater (My Page) on Mon, May 13, 13 at 7:24
| "or newer lights from Philips" davidtay, I'll look on their site, but is there a newer Phillips direct hardwire, low profile I missed? My profile is 3/4" and it's pretty slim pickings in mid-upper mid price range. Thank you very much. |
|
| There is the fortimo led strip, which could be deployed as Ucl with significant assembly required. The eW profile is not going away as it is a complete system. Either the maxlite or the eW profile (for direct wire) should work fine even with a style of 3/4". If you must have a slimmer profile, low voltage could yield some savings vs UniLume. |
Here is a link that might be useful: Fortimo led strip
Please Note: Only registered members are able to post messages to this forum. If you are a member, please log in. If you aren't yet a member, join now!
Return to the Lighting Forum
Instructions
- You must be a registered member and logged in to post messages on our forums.
- Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review the contents and make changes.
- After posting your message, you may need to refresh the forum page in order to see it.
- It is illegal to post copyrighted material without the owner's consent.
- HTML codes are allowed in the message field only.
- No advertising is allowed in any of the forums.
- If you would like to practice posting or uploading photos, please visit our Test forum.
- If you need assistance, please Contact Us and we will be happy to help.