Water boiler temperature for best efficiency

Posted by jsherk (My Page) on
Wed, Dec 9, 09 at 23:09

I have a weil-mclain cg-5 series 12 water boiler in my basement, and am trying to maximize the efficiency.

The way it is currently wired, when there is a demand for heat from thermostat, the boiler kicks on and once the water temp reaches about 145 degrees, the circulator will turn on. When the circulator starts running, the temp slowly drops over about 30 seconds back down to about 120 degrees and then circulator will shut off. The water temp will rise back up to about 145 again, circulator will turn on, temp will drop to 120 and the cycle continues.

The gizmo that adjusts these settings is some kind of Honeywell thing, and there are two settings I can adjust:
#1 - The temp that circulator shuts off at (currently 120), and
#2 - The difference (how much hotter) above the shut off temp before it turns back on (currently set to max of 25 degrees).

I have read that boilers are more efficient at hotter temperatures. Should I adjust any of these settings to improve the efficiency?

Thanks


Follow-Up Postings:

 o
RE: Water boiler temperature for best efficiency

Can you even heat (baseboard?) with such low water temps? Baseboard is designed for 600 BTU per foot at 180 degrees.

You can increase the differential 10-25 degrees if you want hotter water for longer runs, but most people keep it at 10 degrees. A setting of 10 means that your circulator will stop at 10 degrees below the low limit setting and restart at the low limit setting. A setting of 25 will restart the circ at 15 degrees above the low limit setting (for longer runs).

The differential setting is used to preserve hot water for the hot water coil.

Most boilers are set at 160/180 with a differential of 10 for baseboard and 15 for cast iron rads.

In the summer, you can turn the low limit down to 130-140 for domestic water use. Or turn it down all the way if you use a hot water heater.

Boilers are most efficient when they are in steady state operation. On the coldest day of the year, your boiler should run 24/7 and maintain the desired temps, if it is sized properly. Most are oversized. You can reduce the nozzle size for longer runs and more efficiency, but any changes have to be verified and tuned with a Bacarac kit.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here