Hello!

I am in HVAC Sales. I have a service customer whose system, installed by another company, cools fine until 5 or 6 pm. 2000 sf house, spray-foamed. The system is 4 ton and 2-stage cooling. It's a Comfortmaker. My Techs have been to the house several times but usually in the morning. One Tech spoke with Tech Support and filled out a report for Comfortmaker but said everything looked fine.
We suspected the 2nd stage wasn't coming on but the last Tech says it is. He didn't measure cfm but it heats fine all winter.
Has anyone out there had similar troubles with a Comfortmaker? This is the second system of that brand we haven't been able to diagnose but the neighborhood has 30 others that work well.

Any suggestions? Experience? It's a gas system, 16 SEER. About 3 years old.

I have the report in front of me if you need the readings.

Comments (4)

  • weedmeister
    11 years ago

    Where is this located and what are the ambient temperatures?

  • nechesgirl
    Original Author
    11 years ago

    I missed that important detail, didn't I? East Texas. 99-104 degrees most of summer.

    Brick house, horizontal system in attic, hard-pipe, no shade trees. Faces south with most windows on the east side or under covered patio on the north side.

  • mike_home
    11 years ago

    Does the condenser sit in the sun all day? If it is 104 degrees in the shade, then it must be 130+ in the direct sun. The unit may not be able to operate under these severe conditions.

    Try giving the condenser some shade and see if it performs well at 5pm.

  • energy_rater_la
    11 years ago

    unreal that you have to come to
    online hvac forum to solve the problem.

    there isn't enough info for anyone
    to do more than your company has..
    take a guess.

    has your company any experience with foam sealed
    attics? is the gas furnace self condensing or
    does it have 80% furnace with combustion air
    added to unit?

    to me...the starting point for a/c performance
    would be to see if air provided is being delivered
    into the living space of the house. not leaking
    into attic.
    then using data loggers, set up to take hourly readings
    to track how often unit is comming on
    and how much humidity it removes during the
    run cycle..and how much RH increases between cycles.

    send tech...in the afternoon...probably next summer
    unless we get some hot December afternoons.
    sending tech before 2 pm to troubleshoot these
    problems is just pissing away homeowners time & money.

    in high summer the unit should run continuously
    from mid afternoon into evening. with that 500 sq
    ft per tons sizing the unit probably runs 5-15 minutes
    and doesn't remove enough RH for comfort.

    if equipment is correctly installed, then you
    work from there to eliminate problems.

    if you can't solve the problem..recommend some
    one who can. call someone who can test house
    & ducts and do a house diagnostic service.
    keep their contact info for future use.

    comfort institute, RESNET, BPI have trained
    people who solve these issues if it is
    beyond the abilities of your company.

    best of luck