I have a new Carrier heat pump/air conditioner and oil furnace as auxilary. My aux. heat is supposed to be set at 32, however it is not automatically switching over. However if I manually set the thermostat to Emergency heat the oil takes over and works as it should. I am looking for instructions to set the lockout temp on my thermostat. My installation instructions manual states the thermostat is locked so only the installer can make this change. Also I'm not sure what option to use between option 8(aux.heat lockout temp) or option 9 (heat pump lockout temp. balance point).

My thermostat manual is labeled as TP-PRH-A, NRH-A Performance Series Edge. And it is the programmable model A07049.

http://www.residential.carrier.com/products/controls/edgeprogram.shtml


Follow-Up Postings:

 o
RE: How to set Carrier Lock Out temp

I have an Edge Thermostat. The installers gave me both the Owners Manual and the Installation Manual. You should ask them for the missing Installation Manual.

Goto page 26 of the linked manual. Don't mess around with any settings you don't understand.

PS 32 degrees is not an option ... I have mine set for 30 degrees, considered 25 degrees.

Here is a link that might be useful: User Manual

This post was edited by saltidawg on Sun, Dec 2, 12 at 9:54


 o
RE: How to set Carrier Lock Out temp

I actually have the installation instructions.

http://www.favret.com/pdf_files/thermostats/tp_prh_3si_install.pdf

Page 24 shows the settings 08 and 09 that I would like to check, however it states the homeowner does not have access to make changes to the settings. I understand the risk and won't make changes until I'm clear. So if anyone knows the difference between 8 and 9 I would appreciate your help.


 o
RE: How to set Carrier Lock Out temp

I don't know how to make it clearer, in the Manual that YOU identified GOTO page 26 and it tells you to press and hold the fan button for approximately 10 seconds and that will take you to the Configuration Mode where you can change any and all of the 33 settings.

The Users manual limits the homeowner to changing only those settings marked with an asterisk.


 o
RE: How to set Carrier Lock Out temp

Option 8: Auxiliary heat lock out. When this is enabled, the auxiliary heat will not operate above the specified temperature.

Option 9: Heat pump lock out. When this is enabled, the heat pump will not operate below the specified temperature.

What is the setting for Option 1 and is it correct? Don't assume the contractor has wired the thermostat correctly.


 o
RE: How to set Carrier Lock Out temp

Thanks guys. Both 8 and 9 were set at 25. I bumped both to 35. Appreciate your help!


 o
RE: How to set Carrier Lock Out temp

There actually should be an overlap in those numbers. Say 35-40 for #8 and 30-35 for #9, depending on how efficient your HP is and how much oil costs for you.


 o
RE: How to set Carrier Lock Out temp

weedmeister,

I have both Option 8 and also Option 9 set for 30 degrees and that combination does exactly what I want.

I determined 30 degrees based on COP of Heat Pump, efficiency of oil furnace, and price of electricity and price of oil.


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Heating & Air Conditioning Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here